User: kkyyllee, Location: california
Asked on: Wednesday, September 25, 2024 at 10:27 am EDT
Answered on: Thursday, March 6, 2025 at 2:55 am EST
Question: Good morning, my AHJ has received a request if this "common disconnect accessory kit" would be accepted to meet the requirements of the 2020 NEC 230.71B. Would you consider this to be a2. Panelboards with a main service disconnecting means in each panelboard enclosureYou could operate each disconnect independently once the dead front is removed. This doesn't appear to meet the intent to me.
Good morning! Based on your description and the NEC 2020 230.71(B) requirements, I agree with your assessment. This "common disconnect accessory kit," where multiple disconnects can only be operated independently once the dead front is removed, likely does not meet the intent of NEC 230.71(B).Here's why: NEC 230.71(B) (Maximum Number of Disconnects)
This section allows up to six service disconnects for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception No. 1, 3, 4, or 5.
Intent of 230.71(B)
The intent of this rule, and particularly the "six disconnects" rule, is to provide a reasonably accessible and straightforward means for the fire department or other emergency personnel to quickly de-energize the entire service. This is a critical safety feature.
Issue with the Common Accessory Kit
If the disconnects require removing the dead front to operate independently, it defeats the purpose of a quick, emergency shut-off. Removing the dead front:
Introduces a Delay
Precious seconds can be lost in an emergency situation fumbling with screws or fasteners to remove the dead front.
Creates an Additional Hazard
Exposing live parts while trying to remove the dead front is a significant safety risk for emergency responders, and even qualified personnel.
Does not provide for quick shut-off of the service.Here's how it likely FAILS to meet the NEC intent
Accessibility for Emergency Personnel
In an emergency, firefighters or other first responders will not have the time or tools to remove a dead front to operate multiple disconnects. The disconnecting means needs to be rapidly accessible without exposing live parts.
Practicality
The "common disconnect accessory kit" appears to be a workaround to get multiple disconnects within a single panelboard, but it sacrifices the critical safety factor of quick and easy disconnection.
Not truly independent: To be considered a properly rated disconnect in compliance with 230.71b, each disconnect needs to be able to be shutoff independently and rapidly without requiring any tools or the removal of panel sections.
Therefore, my recommendation is to REJECT this "common disconnect accessory kit" as NOT meeting the requirements of NEC 2020 230.71(B).Alternatives that are likely to comply with 230.71(B)
Multiple Panelboards
Use separate panelboards, each with a main service disconnect (up to six total).
Properly Listed/Labeled Equipment
Ensure any panelboard or service equipment used is listed and labeled for use as service equipment and is designed with multiple independent disconnects accessible without* removing the dead front.It's always best to consult with a qualified electrical engineer or the manufacturer of the equipment for specific code compliance interpretations.
Key takeaway: The spirit of 230.71(B) is about rapid, safe disconnection in an emergency. This accessory kit appears to compromise that safety.Good luck with your review! Flag for review