Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Gounding a detached structure

User: pv Installs, Location: Rhode island

Asked on: Wednesday, September 25, 2024 at 12:45 pm EDT
Answered on: Thursday, March 6, 2025 at 2:55 am EST

Question: Recently we installed a solar system to a detached barn. This barn has no electricity ran to it. We ran the solar lines off the roof through a trench to the house. Inspector failed us because he said the barn now has feeders and needs to be grounded with 2 ground rods.. what are we supposed to tie the ground into? I'm assuming the disconnect for the solar system? But then wouldn't that make a parallel ground?

Okay, let's break this down. Your inspector's requirement is likely based on the National Electrical Code (NEC), which requires grounding for buildings with electrical service, even if that service comes from a renewable energy source like solar. The intent is safety, protecting people and equipment in case of a fault.Here's a breakdown of the issues and how to approach a solution

Understanding the Issues
Building as a Separately Derived System

The key point here is whether the inspector is treating the barn as a separately derived system. If the inverter at the house is sending AC power to the barn, even through a DC-linked system, the barn now effectively has a separate electrical service. The NEC section 250.32 (Grounding and Bonding Requirements for Separate Buildings or Structures) would likely apply.


Ground Rods

Ground rods provide a path for fault current to flow to the earth, helping trip a breaker or fuse in the event of a ground fault.

Parallel Grounds

You are right to be concerned about parallel grounds. Under normal conditions, current shouldn't flow through the grounding system. However, if multiple grounding paths exist between buildings, during a fault, current
can flow through the earth and the grounding conductors simultaneously. This can create circulating currents, potentially energizing metallic parts and creating a safety hazard. The NEC often addresses this with specific bonding requirements.

NEC 250.32(B): Equipment Grounding Conductor Requirement

This NEC section states that you must run an Equipment Grounding Conductor with the feeder between the house and the barn.

What the Inspector is Likely Looking For (and How to Address It)
1. Equipment Grounding Conductor (EGC)

Run an equipment grounding conductor along with the AC feeders to the barn. It must be sized according to NEC Table 250.122, based on the size of the overcurrent protection device protecting the AC feeder.
2.


Grounding Electrode System (GES) at the Barn

A grounding electrode system is required at the barn. The inspector is asking for ground rods, but NEC Section 250.50 describes all electrodes that must be bonded together to form the GES. These might include:

Ground Rods

Two ground rods, spaced at least 6 feet apart.


Concrete-Encased Electrode (Ufer Ground)

If present, a metal reinforcing bar or rod encased in at least 2 inches of concrete that is in direct contact with the earth.

Ground Ring

A bare copper conductor buried in direct contact with the earth that encircles the building.


Metal Water Pipe

If it's in direct contact with the earth for at least 10 feet.3.

Bonding at the Barn

Bond the Equipment Grounding Conductor that is ran with the AC Feeder to the barn to the grounding electrode system. Bond any exposed non-current-carrying metal parts in the barn (metal boxes, enclosures, etc.) to the equipment grounding conductor.

Where to Connect the Grounding System at the Barn
Main Disconnect at the Barn

The primary connection point for the ground rods and EGC should be at the main disconnect switch or panel at the barn. If the inspector is calling the DC disconnect the "main disconnect", then connect the ground there.


Bonding Jumper

Use a bonding jumper of the appropriate size (again, according to the NEC tables) to connect the grounding electrode conductor (the wire running to the ground rods) to the metal enclosure of the disconnect.

Why This Approach Matters
Safety

Provides a low-impedance path for fault current to return to the source (inverter/house panel), tripping a breaker and preventing dangerous voltage on metal parts.


Code Compliance

Meets the requirements of the NEC, avoiding future inspection issues.

Steps to Take Now
1. Clarify with the Inspector

Politely ask the inspector for the specific NEC articles and sections they are citing for the grounding requirements. This will give you a clear understanding of what they expect. It is always best to have good communication with the inspector!2.

Review the NEC

Read NEC Article 250 thoroughly, paying close attention to sections on grounding and bonding of separately derived systems and separate buildings.3.

Consult a Qualified Electrician

Given the complexity and safety implications, it is highly recommended that you consult with a licensed electrician experienced in solar installations and NEC grounding requirements. They can assess your specific situation, ensure proper sizing of conductors and equipment, and perform the work safely and correctly. The cost of an electrician is less than the potential liabilities.

Important Considerations
Inverter Grounding

Some inverters have specific grounding requirements. Check the inverter manufacturer's instructions carefully.


Overcurrent Protection

Make sure the overcurrent protection devices (breakers/fuses) are correctly sized for the conductors and equipment.

Wire Sizing

All grounding and bonding conductors must be sized according to NEC tables, based on the size of the overcurrent protection.


Local Amendments:
Be aware of any local amendments to the NEC in your jurisdiction.By following these steps, you can ensure your solar installation is safe, compliant with the NEC, and meets the inspector's requirements. Remember, electrical safety is paramount! Flag for review

Previous Question Next Question