Topic: Disconnect Switch Sizing

User: faresos, Location: Illinois

Asked on: Wednesday, September 25, 2024 at 3:51 pm EDT
Answered on: Thursday, March 6, 2025 at 2:56 am EST

Question: Hello Everyone,What size of disconnect can be used for 300HP air compressor (NP FLA= 325A, with S.F.: 1.15)? My understanding the 400A HD disconnect is only rated for 250HP. The disconnect is not used for controls (On/Off) as it has it's own controller. The NEC tables indicate the FLA for 300HP is 361A. Questions:1. Can I size the disconnect switch based the name plat of the motor X S.F. (325A X 1.15 = 374A- which means I can use 400A HD Disc sw) or it needs to be rated for the motor HP, whch means I have to use 600A since the 400A disc is only rated at 250 HP?2. Can I use the FLA name plate (325A) for sizing or I must use the NEC FLA (361A)Thank you,

Let's break down the disconnect sizing requirements for your 300 HP air compressor. This involves a combination of nameplate data, NEC tables, and disconnect switch horsepower ratings.

Understanding the Relevant NEC Sections 430.110(C) Ampere Rating and Interrupting Capacity

This section is key for motor disconnect sizing. It states that the disconnect "shall have an ampere rating not less than 115 percent of the full-load current rating of the motor." This means you need a disconnect rated for
at least 1.15 times the motor's FLA.

430.109(A)(1) Horsepower Rating

"For a motor rated more than 2 hp, the disconnecting means shall be listed in accordance with the horsepower rating of the motor and shall be rated in accordance with the locked-rotor current of the motor." This means the disconnect switch must have a HP rating equal to or greater than the motor HP, and must have an adequate withstand rating for motor starting inrush.

Answering Your Questions
1. Disconnect Sizing: Nameplate FLA with SF vs. Horsepower Rating This is where it gets a bit nuanced, and code interpretation can vary. While some would argue you can use the nameplate FLA x SF (325 x 1.15 = 373.75), the NEC mandates a HP rated disconnect. Therefore, due to the 300HP motor, you CANNOT use a 400A HD Disconnect Switch that is rated for 250HP. You will need to use a 600A HD Disconnect Switch that is rated for 300HP. Justification: The horsepower rating is a minimum. While the amperage rating of the 400A switch might seem adequate based on FLA x SF, it is still rated for a 250HP motor.2. Nameplate FLA vs. NEC Table FLA Use the Nameplate FLA. Section 430.6(A)(1) states that full-load current ratings shall be used as specified in 430.6(A)(1)a or 430.6(A)(1)b. 430.6(A)(1)a states that when the motor current is required to be used, the full load current values shown in Table 430.247, 430.248, 430.249, or 430.250, shall be used instead of the actual current rating marked on the motor nameplate plate. Exception No. 1 states that the full-load current shall be permitted to be obtained from the motor nameplate where the motor is part of an approved assembly that does not have overload protection. In your case, the overload protection is separate (controller), you must use the motor's FLA.

In summary

Use the nameplate FLA of 325A. You

must
use a disconnect switch rated for at least 300 HP. This will likely mean using a 600A HD disconnect switch. Ensure the disconnect switch is rated for the voltage and short-circuit current available at the location.

Important Considerations



Local Codes and AHJ (Authority Having Jurisdiction)

Always check with your local electrical inspector or AHJ. Their interpretation of the code is what matters most.


Manufacturer's Specifications

Consult the disconnect switch manufacturer's data sheets for specific ratings, suitability, and installation instructions.

Short-Circuit Current Rating (SCCR)

The disconnect switch must have a short-circuit current rating (SCCR) high enough to withstand the available fault current at the installation point. This is critical for safety.


Voltage Rating

Verify the disconnect's voltage rating is compatible with the system voltage.

Disclaimer:
I am an AI Chatbot. This information is for general guidance only. Always consult with a qualified and licensed electrical engineer or electrician for specific design and installation advice. They can assess your specific situation, local codes, and safety requirements to ensure a compliant and safe installation. Flag for review