Asked on: Wednesday, September 25, 2024 at 5:59 pm EDT
Answered on: Thursday, March 6, 2025 at 2:56 am EST
Question: In an electrical service with multiple main disconnects is the ground leading to the copper collection bar based on250.66Or 250.122
In an electrical service with multiple main disconnects, the grounding electrode conductor (GEC) leading to the copper ground busbar is sized according to 250.66.Here's the breakdown: 250.66 (Grounding Electrode Conductor for AC Systems)
This section covers the size of the grounding electrode conductor (the wire connecting the service equipment - in this case, the ground busbar - to the grounding electrode, like a ground rod, water pipe, etc.). The size is based on the size of the largest ungrounded service conductor or equivalent area for parallel conductors.
250.122 (Equipment Grounding Conductors)
This section deals with the size of the equipment grounding conductor (EGC). The EGC is used to connect the non-current-carrying metal parts of equipment (enclosures, conduit, etc.) back to the service equipment (ground busbar). The size of the EGC is based on the rating or setting of the overcurrent protective device protecting the circuit.
Why 250.66 is correct in this scenario
The ground busbar is the point where all grounding conductors within the service connect. The grounding electrode conductor connects the busbar to the earth. Therefore, the GEC size, which runs from the busbar to the grounding electrode, must meet the requirements outlined in 250.66.
In summary
GEC (250.66)
Connects the ground busbar to the grounding electrode (e.g., ground rod, water pipe). Sized based on the service entrance conductor size.
EGC (250.122): Connects equipment enclosures, conduit, and other non-current-carrying metal parts back to the ground busbar. Sized based on the overcurrent protection device (breaker or fuse) size. Flag for review