Topic: Reading Siemens Series Rating Chart

User: Tainted, Location: New York

Asked on: Wednesday, September 25, 2024 at 7:03 pm EDT
Answered on: Thursday, March 6, 2025 at 2:57 am EST

Question: How do I read this Siemens series rating chart? I need to find series rating for HQP breaker fed by a fuse. Is the chart below saying that the HQP breaker is series rated with class J fuse? Or is it only saying that it's series rated with a Class T fuse (300V)? Or is it series rated with both?

Let's break down how to read the Siemens series rating chart (or, more accurately, a snippet of one) and interpret it for your HQP breaker and fuse combination.

Understanding the Chart Components



Manufacturer

(Siemens, in this case) - Specifies the manufacturer of the circuit breakers being considered for the series rating.


Breaker Type

(Likely refers to the type of circuit breaker) - This is the downstream breaker that you're trying to protect and determine its series rating. In your case, it's the "HQP" breaker.

Upstream OCPD (Overcurrent Protective Device) - Type/Class

This column indicates the type of overcurrent protection device (OCPD) used upstream of the breaker. This is often a fuse or another circuit breaker. In your case, it would be the fuse used upstream of the HQP breaker.


Upstream OCPD - Minimum Ampere Rating

Specifies the minimum ampere rating of the upstream OCPD required for the series rating to be valid. The ampere rating will differ depending on the fuse class.

Series Rating

This column indicates the short-circuit current (in kA) that the combination of the upstream OCPD and the downstream breaker can withstand. This is the value you're ultimately looking for.


Voltage Rating

Specifies the voltage rating.

Analyzing Your Snippet

Based on the image you provided, here's the interpretation, but keep in mind this is only a

SECTION
of a possibly much larger chart: HQP Breaker with Class T Fuse (300V)

The chart likely
is indicating a series rating when an HQP breaker is fed by a Class T fuse rated at 300V. You will need to determine the minimum fuse rating. The series rating for a 300V Class T fuse is listed as 100kA.

HQP Breaker with Class J Fuse

You mentioned a Class J fuse but the image you provided does not include a Class J fuse series rating. Check to see if the Class J fuse is a listed series rating on a different section of the chart. If it is, you can read the series rating as before with Class T fuse. If there is no series rating for Class J fuse on the chart, then you

CANNOT
use it as series rated.

Important Considerations and Next Steps


Complete Chart is Essential

The small snippet you provided is not enough for a definitive answer.

You MUST consult the complete Siemens series rating chart document.
These charts can be extensive, covering many combinations.2. Specific HQP Model

Series ratings can vary depending on the exact model of your HQP breaker. Ensure you're looking at the correct series rating for your specific breaker model number.3.

Fuse Manufacturer and Specific Fuse

Series ratings are often dependent on the specific fuse model/brand. For example, a Bussmann Class J fuse might have a different series rating than a Littelfuse Class J fuse, even if they are both Class J and have the same ampere rating.4.

Voltage Rating

Always verify that the voltage rating of the fuse matches or exceeds the voltage of the circuit you are protecting. The Class T fuses in the image you provided are only 300V.5.

Upstream Device Rating

The minimum ampere rating of the upstream OCPD is crucial. Using a fuse with a lower ampere rating than specified in the chart will invalidate the series rating.6.

Proper Installation

Series ratings are only valid if the installation is done according to the manufacturer's instructions and applicable electrical codes.7.

Verification with a Qualified Electrician/Engineer



The most important step is to have a qualified electrician or electrical engineer review the entire situation and verify the series rating.
Incorrectly applying series ratings can be dangerous.

In summary, read the entire Siemens series rating chart document. Find the section that corresponds to your specific HQP breaker model. Then, check if Class J or Class T fuses are listed for series rating. If so, verify that the voltage rating, ampere rating of the fuse, and the fuse manufacturer meet the conditions specified in the chart. Finally, have a qualified electrician/engineer verify your interpretation and the proper installation. Flag for review