User: mannyb, Location: Florida
Asked on: Wednesday, September 25, 2024 at 8:25 pm EDT
Answered on: Thursday, March 6, 2025 at 2:57 am EST
Question: 320 meter with parallel service feeds . We are installing ATS for new generator and limited space. I can only fit 1-3" conduit at bottom of meter can over to new ATS. Is it wise to install 1 conduit or 2 for parallel conductors to ATS
Okay, let's break down the situation and determine the best and safest approach for your conduit installation.
Understanding the Problem Parallel Service Feeds
You have a 320A service, and it's paralleled. This means each phase (and likely the neutral) has two conductors in parallel to carry the current.
ATS and Generator
You're adding an Automatic Transfer Switch (ATS) for a generator, which is good for backup power.
Limited Space
The biggest constraint is the very limited space, restricting you to a maximum of 1 or 2 3" conduits between the meter can and the ATS.
NEC Compliance and Safety are Paramount
This installation must comply with the National Electrical Code (NEC) and be safe for both the installer and end user.
Key Considerations1. Ampacity
The first question is can you physically fit enough conductors in one 3" conduit to handle 320A of power, while derating for conductor fill in the conduit? The answer is likely no, since you will have parallel runs of the same conductor in the same conduit.2.
NEC Article 310: Conductors for General Wiring
This article covers conductor ampacity and adjustment factors. Crucially, section 310.15 details ampacity requirements for conductors in raceways. Since you will have a high percentage of conductors in the raceway, ampacity derating is critical.
3.
NEC Article 300: Wiring Methods and Materials
Pay attention to sections dealing with parallel conductors, conduit fill, and derating factors. Specifically, parallel conductors must meet the requirements of 310.10(H). In parallel installations the conductors in each parallel set must: Be the same length Be of the same conductor material Be the same size in circular mil area Have the same insulation type Be terminated in the same manner4.
Conduit Fill
NEC Chapter 9, Table 1 (and notes) specifies the maximum allowable fill for conduits. Typically, for more than two conductors, it's 40% fill.5.
Inductance/Impedance
When paralleling conductors, it's critical that the conductors of each phase/neutral set are routed together in the same conduit. This minimizes inductive reactance and ensures balanced current sharing. You CAN NOT run all the 'A' phase conductors in one conduit and all the 'B' phase conductors in another.
Analysis and Recommendation
Given these constraints, the safest and most code-compliant approach is: Two 3" Conduits are likely REQUIRED
Because of ampacity derating caused by conductor fill, two conduits will be required.
Steps to Take (Critical!)1. Calculate Ampacity Derating
Determine the actual ampacity required after accounting for temperature correction and the number of current-carrying conductors in the conduit.2.
Conduit Fill Calculation
Calculate how many of your conductors (with insulation) will fit within a 3" conduit, adhering to the 40% fill rule. This requires knowing the physical dimensions of the conductors you plan to use (including insulation).3.
Pull Boxes (If Needed)
If it's impossible to make the bends required for the conduit run without exceeding the allowed number of bends, include appropriately sized pull boxes in the run.4.
Inspection
This must be inspected by a qualified electrical inspector. They have the final authority on code compliance.
Example Scenario (Illustrative - You MUST Perform Calculations)
Let's assume you're using THHN/THWN-2 conductors for your 320A service. (These are common). To carry 320A, you would need (at a minimum, before derating) two sets of 1/0 AWG copper conductors per phase/neutral. Even with 1/0 AWG copper conductors, the 40% fill limitation with THHN/THWN-2 insulated conductors in a 3" conduit will likely prevent you from placing enough sets of parallel conductors in a single conduit, which is why two conduits are necessary.
Important Safety Note
Working with service entrance conductors is extremely dangerous. If you are not a qualified electrician,
DO NOT attempt this work yourself. Engage a licensed and experienced electrical contractor. Flag for review