Topic: 310.12 - Sizing conductors downstream of ATS

User: marmathsen, Location: Seattle, Washington ...ish

Asked on: Thursday, September 26, 2024 at 1:02 am EDT
Answered on: Thursday, March 6, 2025 at 2:58 am EST

Question: Do the downstream conductors of an ATS serving the entire load of the house qualify for 83% sizing per 310.12?In particular I'm thinking about the sense, control, and battery charge conductors that would not be included in the feeder supplied by the ATS. In a Generac transfer switch I'm looking at, the T1, N1, and N2 conductors are protected by (3) 240VAC 6.3A fuses which makes me think I CAN'T USE THE 83% ALLOWANCE.Rob G - Seattle

You've hit on a very important point about 310.12 and its applicability. Let's break it down

Understanding 310.12 and the 83% Rule:
Purpose

310.12 aims to reduce conductor sizes for dwelling unit service and feeder conductors where the
entire load is calculated per Article 220, Parts III and IV. It recognizes the diversity of residential loads and allows for a reduced ampacity based on the calculated load.

Requirement: Serving the Entire Load

A critical requirement is that the reduced conductor size must serve the entire calculated load of the dwelling unit. This means everything connected to the service or feeder must be included in the calculation and served by the reduced conductors.

Applicability

It applies
only to the main service conductors or a feeder supplying the entire load of a dwelling unit.

Your Specific Scenario with the ATS (Automatic Transfer Switch)

You are correct to question the application of 310.12 in your scenario for these critical reasons:1.

The ATS does
NOT serve the entire load during a power outage

Your observation about the sense, control, and battery charge conductors that are
not included in the feeder supplied by the ATS is the key. The Generac ATS, in its normal operation, is not carrying these loads, which are part of the total house load calculation. These loads are powered directly from the utility supply, outside the ATS's jurisdiction, until there is a generator start and transfer. When the generator runs, a whole new set of rules come into play. Therefore the ATS does not handle the entire load and 310.12 is no longer applicable.
2.


Fuse Size as an Indicator

The presence of the 6.3A fuses protecting the T1, N1, and N2 conductors is
strongly suggestive that those conductors are not intended to carry a significantly large load. Their purpose is primarily for control, sensing, and signal functions.3.

Generator sizing

If the generator can only supply the house for some of the loads you have, such as air conditioning or electric heat, 310.12 isn't applicable because the generator and the associated ATS aren't capable of supplying the entire load.

Why 310.12 Doesn't Apply (and Why It's Important)



Code Intent

The NEC's intent with 310.12 is to save on conductor costs without compromising safety. When the entire load is served, the diversity calculations are reliable. If you exclude portions of the load and still reduce the conductor size based on 310.12, you're essentially under-sizing the conductors for those excluded loads when they are energized. This is a safety hazard.

Example

Let's say your house has a calculated load of 150A, but the ATS only supplies 100A when on generator power. You can't use 310.12 to size the conductors
before the ATS to 83% of the 150A. You need conductors capable of handling the full 150A. After the ATS, the generator-fed conductors also can't be sized with 310.12.

Safety

Conductors must be sized to safely carry the load. By not including all loads, it's possible to overload the conductors and create a fire hazard.

In Summary

You are correct to conclude that you cannot apply 310.12 sizing to the conductors associated with the Generac transfer switch, specifically the sense, control, and battery charge conductors. Those conductors are not part of the "feeder" as described in 310.12.

For clarity:
You can apply 310.12 to the service conductors if you've correctly calculated the entire load, according to Article 220, Parts III and IV. Flag for review