Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 348.60 (D)

User: jes25, Location: Midwest

Asked on: Thursday, September 26, 2024 at 12:19 pm EDT
Answered on: Thursday, March 6, 2025 at 3:00 am EST

Question: I'm working on some content for our apprentices with Mike Holt's material and I'm not clear on something. 348.60(D) talks about bonding jumpers for FMC and points us to 250.102. Specifically, 250.102 (D) (2) where, it says we can run a bonding jumper on the OUTSIDE of a raceway up to 6 feet. The NEC handbook even shows a graphic with a bond wire on the outside of a piece of flex going to a motor next to this section. Mike Holt also has similar graphics.What I don't understand is how this wire on the outside of the flex is being classified as a bonding jumper instead of an EGC. 348.60 (B) says an EGC is required for flexible installations and right below in 348.60 (C) says a to install the EGC per 250.134 which doesn't allow any EGC on the outside of a raceway.What I'm saying is, the way I read this a bonding wire on the outside of a piece of flex doesn't meet the requirement for a EGC. Agree?Which begs the question, why install that wire on the outside of the flex.Can anyone clear this up?

You've hit on a really important point that often causes confusion. Let's break it down to understand the nuances

Key Difference: Equipment Bonding Jumper vs. Equipment Grounding Conductor (EGC)
Equipment Grounding Conductor (EGC)

Its primary function is to carry fault current back to the source, facilitating the operation of the overcurrent protective device (OCPD) like a breaker or fuse. It's part of the normal grounding path for equipment. EGCs are defined in 250.118


Equipment Bonding Jumper

Its primary function is to ensure the electrical continuity of metal raceways and enclosures. It connects metal parts together to create a low-impedance path for fault current. Think of it as making sure all the metal pieces are at the same electrical potential relative to each other. This is crucial for safety, even if a dedicated EGC is also present.

Understanding the Code Sections



348.60(B)

This
requires an EGC to be installed with the flexible metal conduit (FMC).

348.60(C)

This specifies that the EGC must be installed according to 250.134. As you correctly point out, 250.134 generally mandates that the EGC be inside the raceway or cable. There is no mention of any EGC on the outside of the raceway.

348.60(D)

This addresses the
need for bonding jumpers in certain situations. It doesn't eliminate the requirement for the EGC. It just adds a secondary requirement in some cases.

250.102(D)(2)

This allows for an equipment bonding jumper to be installed outside of a raceway, up to 6 feet long, under certain conditions. These conditions typically involve mitigating potential issues with impedance or ensuring a low-impedance path across a section of raceway.

The "Why" of the External Bonding Jumper

The external bonding jumper, as shown in the Mike Holt graphics and the NEC Handbook, is not intended to replace the required EGC that runs inside the FMC. It's in addition to the EGC.Here's why it's used:1.

Ensuring Low Impedance

FMC, particularly when it is very long or made of thinner metal, can have a relatively high impedance for fault current. The spiral construction of FMC means that fault current has to travel a longer, spiraling path. This impedance can impede the tripping of the OCPD in a fault situation. The external bonding jumper (which is often a short, heavy gauge wire or braided conductor) provides a parallel, lower impedance path. This helps ensure that a fault current can quickly and reliably trip the breaker.2.

Overcoming Concentric Knockouts

When FMC is connected to enclosures using concentric knockouts, there can be a questionable electrical connection between the enclosure and the fitting on the FMC. The equipment bonding jumper (which may be the grounding locknut) helps maintain electrical continuity.3.

Motor Vibration

When a motor vibrates, the FMC connections can loosen over time. The supplemental bonding jumper provides a more secure and reliable bonding connection that is less susceptible to loosening.4.

Harmonics

Sometimes, the EGC on the inside is not able to handle the harmonics on the line. The supplemental bonding jumper is used to assist with the additional harmonics and noise on the line.

Therefore, the external wire is an equipment bonding jumper installed to supplement the internal EGC, not a replacement for it.
Your Core Question Answered

You are correct:

a bonding wire on the outside of a piece of flex, by itself, does not meet the requirement for an EGC as per 348.60(B) and (C).
It serves a different, supplementary purpose related to bonding.

How it All Works Together


Install the EGC

You must run an EGC (sized per 250.122) inside the FMC, as required by 348.60(B) and (C). This fulfills the primary grounding requirement.
2.


Assess the Need for a Bonding Jumper

Determine if a bonding jumper is necessary based on the installation conditions (length of FMC, potential impedance issues, motor vibration, etc.).3.

Install the Bonding Jumper (if required)

If needed, install the equipment bonding jumper externally, adhering to the length limitations in 250.102(D)(2). Connect it securely to the metal enclosures or equipment at both ends.

In summary

Don't think of the external wire as an EGC substitute. Think of it as a bonding jumper that enhances the bonding of the raceway system and improves the overall safety and performance of the grounding path in specific situations. You need both the EGC inside the FMC and potentially a bonding jumper outside depending on the installation.

Recommendation:


When teaching this concept to apprentices, emphasize the distinction between EGCs and bonding jumpers. Use clear diagrams and examples to illustrate how each conductor contributes to the overall grounding and bonding system. Walk them through the code sections and explain the reasoning behind each requirement. Practical exercises, where they have to identify and install both EGCs and bonding jumpers, will solidify their understanding. Flag for review

Previous Question Next Question