Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: HVAC and Residential load Calculation

User: ING23, Location: Las Vegas

Asked on: Thursday, September 26, 2024 at 1:47 pm EDT
Answered on: Thursday, March 6, 2025 at 3:00 am EST

Question: Any one could help clarifying how determine the load for HVAC with Gas Heater . I understand we have 3 motor , (Compressor , Condenser Fan and Blower )Which one (motors ) should I must consider?Which Parameters of the motor I must use?What chapter the code support your answer?Every example online always mention the AC load , but not how to get it or just analyze the HVAC with the electric heater (usually with higher demand and they just use that value on load calc because the load is the higher than the load of the AC. )here is the Specification:Thanks for your help

Okay, let's break down how to determine the load for an HVAC system with a gas heater, focusing on the electrical components and how to apply the NEC.

Understanding the Electrical Load in a Gas Heating System

While the primary heating source is gas, these units still have electrical components that contribute to the overall electrical load calculation. The key components you need to consider are: Compressor

(Refrigerant cycle if the unit is also an air conditioner)


Condenser Fan Motor

(Cools the refrigerant in the outdoor unit if the unit is also an air conditioner)

Blower Motor

Circulates air throughout the ductwork, regardless of whether heating or cooling.


Ignition System

(Typically a small load, but should be considered)

Controls

(Thermostat, control board – typically a very small load, but present)

Which Motors to Consider and Why


You
must consider all of the motors in the system. Here's why: Compressor & Condenser Fan Motor (if applicable)

These represent the main power draw when the unit is in cooling mode (if it's a combination gas furnace/AC unit).

Blower Motor

This motor is
always running (or cycling on/off) whether you are heating or cooling. It's essential for air circulation.

Other electrical components

While these are not motors, the ignition system and controls need to be considered.

Motor Parameters to Use


You'll primarily use the following information from the unit's nameplate for each motor: Full Load Amps (FLA)

This is the most critical value. FLA represents the current the motor draws when operating at its rated horsepower and voltage under full load.


Voltage

You need to know the voltage the motor is designed to operate at (e.g., 120V, 240V). This is critical for voltage drop calculations and proper circuit sizing.

Horsepower (HP)

While FLA is more directly used in calculations, HP is useful for understanding the motor's capacity.


Locked Rotor Amps (LRA)

LRA is the current drawn by the motor when it's initially starting. This is a very high current that lasts for a short period. It's important for overcurrent protection sizing (fuses or circuit breakers). Often, LRA will only be listed for the compressor motor.

Minimum Circuit Ampacity (MCA)

This value (often found on the outdoor unit nameplate for AC systems) is the
minimum ampacity of the branch circuit conductors required to supply the unit. It's calculated based on the compressor and fan motor loads. MCA is a crucial value to use.

Maximum Overcurrent Protection (MOCP)

This value (also often on the outdoor unit nameplate) is the maximum size of the overcurrent protection device (fuse or circuit breaker) allowed to protect the circuit.

How to Determine the HVAC Load (Step-by-Step)
1. Gather Nameplate Data

Locate the nameplates on all components of the HVAC system (indoor unit, outdoor unit if it's an AC). Record the FLA, voltage, HP, LRA (if available), MCA, and MOCP for each motor and electrical component.2.

Cooling Load Calculation (If Applicable)

If the unit includes air conditioning, determine the total cooling load: Use the MCA value from the outdoor unit nameplate. This is often the easiest and most accurate way to determine the cooling load.

Alternatively, if MCA is not available, calculate it

Start by calculating 125% of the largest motor load (usually the compressor). `Largest Motor Load = Compressor FLA x 1.25`
Add the FLA of all other motors (condenser fan motor). Add any other continuous loads (controls). The result is the Minimum Circuit Ampacity (MCA).3.

Heating Load Calculation

The heating load is primarily determined by the blower motor and any auxiliary electric heat (if present, which is rare with gas furnaces). Determine the FLA of the blower motor. Add the amperage of any other electrical components (ignition system, controls). If there is auxiliary electric heat, add its amperage to the blower motor and other components.4.

Compare Cooling and Heating Loads

Compare the total amperage calculated for the cooling load (if applicable) with the total amperage calculated for the heating load.5.

Use the Larger Load

The
larger of the cooling load or heating load is the value you use for your overall load calculation for the HVAC system. This ensures you're accounting for the worst-case scenario.6.

Overcurrent Protection

Select an overcurrent protection device (circuit breaker or fuse) that is sized appropriately for the
largest motor's LRA (if known) or the MOCP value on the nameplate, while also complying with the NEC requirements for motor protection. The MOCP is usually the easiest way to select the correct overcurrent protection.7.

Conductor Sizing

Size the branch circuit conductors according to the
larger of the cooling or heating load calculation. The conductors must have an ampacity equal to or greater than the MCA value.

NEC Code References


The following NEC articles are particularly relevant:
Article 430: Motors, Motor Circuits, and Controllers

This is the primary article for all motor-related installations. It covers motor circuit conductors, overcurrent protection, motor overload protection, and motor control circuits.

Article 440: Air-Conditioning and Refrigerating Equipment

This article supplements or modifies the general requirements of Article 430 for air-conditioning and refrigeration equipment. It has specific rules for calculating branch-circuit loads, conductor sizing, and overcurrent protection.


Article 220: Branch-Circuit, Feeder, and Service Calculations

This article provides the general requirements for calculating branch-circuit, feeder, and service loads. You'll use this to combine the HVAC load with other loads in the building.

210.24: Branch-Circuit Requirements

(Summary of common branch circuit ratings)


110.3(B): Examination, Identification, Installation, and Use of Equipment

This section mandates that you follow the manufacturer's instructions and listing requirements for the equipment. This is why the nameplate data is so important.

Specific Considerations for Gas Heaters
Auxiliary Electric Heat

As you mentioned, some gas furnaces might have auxiliary electric heat strips. If present,
this will significantly increase the electrical load of the heating system. Make sure to account for the amperage of these heat strips in your calculations. If present, the electric heat load will likely be the dominant load in the heating calculation.

Combination Units

If you're dealing with a combination gas furnace/AC unit, the AC load (compressor, condenser fan) will usually be higher than the gas heating load (blower motor, ignition). However, always calculate both and use the larger value.

Example (Simplified)


Let's say you have a gas furnace/AC unit with the following nameplate information: Outdoor Unit (AC)

MCA: 20 Amps MOCP: 30 Amps

Indoor Unit (Furnace)

Blower Motor: 120V, 5 Amps Ignition System: 1 AmpIn this case:1.

Cooling Load

MCA = 20 Amps2.

Heating Load

Blower (5A) + Ignition (1A) = 6 Amps3.

Overall HVAC Load

20 Amps (because the cooling load is larger)4.

Conductor Sizing

Use wire rated for at least 20 Amps (e.g., 12 AWG copper for typical installations).5.

Overcurrent Protection

Use a 30 Amp circuit breaker (following MOCP).

Important Notes



Local Codes

Always check with your local building codes and electrical inspectors for any specific requirements or interpretations.


Qualified Electrician

HVAC wiring should be performed by a qualified and licensed electrician.

Voltage Drop

After determining the amperage and wire size, perform a voltage drop calculation to ensure the voltage at the unit is within acceptable limits, especially for longer wire runs.


Service Factor:
Some motors have a service factor listed on the nameplate. If so, you can multiply the FLA by the service factor to get a higher allowable continuous load. However, this is usually only used for motor overload protection, not for branch-circuit sizing.By following these steps and consulting the relevant NEC articles, you can accurately determine the electrical load for an HVAC system with a gas heater and ensure a safe and compliant installation. Remember to always prioritize safety and consult with qualified professionals when in doubt. Flag for review

Previous Question Next Question