Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 620.25 - split units for elevator machine rooms

User: GWillmott, Location: Denver

Asked on: Thursday, September 26, 2024 at 2:54 pm EDT
Answered on: Thursday, March 6, 2025 at 3:00 am EST

Question: Hey guys,I have an elevator inspector who's insisting that we installed a fused disconnect in the machine room of an elevator between the indoor air handler and the outdoor condensing unit.We obviously have a fused disco outside by the outdoor unit, but installing one inside the machine room would surely mess with the communication cables, no? Is he interpreting the code correctly? Thanks

Okay, let's break this down. Your question revolves around the NEC (National Electrical Code) requirements for disconnects in elevator machine rooms, specifically in relation to HVAC equipment for the elevator machine room.

Understanding the Inspector's Perspective

The inspector is likely referencing a section of the NEC (I need to know what year NEC you are using in order to give the precise code) that requires disconnecting means for equipment in the elevator machine room. The primary goal of these disconnects is safety: Emergency Shutdown

To allow maintenance personnel or first responders to quickly and safely de-energize equipment within the machine room in an emergency.


Lockout/Tagout

To provide a means for isolating equipment during maintenance and repair.

Why He Might Think You Need a Disconnect Inside
Dedicated Equipment

If the indoor air handler in the elevator machine room is
exclusively serving the machine room, it might be argued that it needs its own disconnecting means within the machine room. The code emphasizes that this disconnecting means needs to be readily accessible.

Clarity and Simplicity

The inspector might be aiming for a situation where anyone entering the machine room knows exactly where to shut off power to any equipment within that room, regardless of where the primary supply originates.

Why Your Concerns About Communication Cables Are Valid


You're right to be concerned about the communication lines between the indoor and outdoor units. Here's why: Low-Voltage Control Signals

HVAC systems often use low-voltage communication cables (e.g., 24VAC) to control functions like compressor operation, fan speed, and defrost cycles. These are often run alongside the power conductors.


Interruption Issues

Placing a disconnect on the power feed to the indoor unit would de-energize the control board, breaking the communication link. This could cause error codes, system malfunctions, and potentially damage the equipment. The outdoor unit would be running without any direction from the indoor unit, which is extremely problematic.

Key Arguments for Not Needing an Additional Disconnect Inside


Here's where you can build your case:1. The Existing Outdoor Disconnect

You already have a fused disconnect located at the outdoor condensing unit. A strong argument is that this disconnect serves as the primary disconnecting means for the entire HVAC system (both indoor and outdoor units). It breaks the power to the whole system.2.

Accessibility

The NEC requires the disconnecting means to be "readily accessible." Argue that the outdoor disconnect meets this requirement. While it's outside the machine room, it's a permanent, clearly labeled, and accessible disconnecting means for the HVAC system. It should be labeled in a way that makes its function clear.3.

Maintenance Procedure

A proper maintenance procedure for the HVAC system would already require shutting off power at the outdoor disconnect before working on any part of the system (indoor or outdoor). This is standard practice for safety.4.

Machine Room Disconnect Exception

Review the specific NEC code your area uses. There might be exceptions for HVAC equipment that is clearly associated with, and directly powered by, an outdoor unit that already has a readily accessible disconnect.5.

Clarify the Scope of the Machine Room Disconnects

The elevator machine room disconnect requirements are primarily intended for the elevator equipment itself (hoist motor, controller, etc.). Ensure the inspector understands that you are not trying to circumvent those requirements.

How to Respond to the Inspector
1. Be Respectful and Collaborative

Start by acknowledging the inspector's concerns and demonstrating that you understand the intent of the code (safety).2.

Reference the Specific Code

Ask the inspector to point you to the exact section of the NEC he believes requires the additional disconnect. This will help you understand his reasoning and allow you to research the relevant clauses.3.

Present Your Arguments Clearly and Concisely

"We believe the outdoor disconnect at the condensing unit serves as the primary disconnecting means for the entire HVAC system, including the indoor air handler." "Shutting off power at the indoor unit's location would disrupt the communication link between the indoor and outdoor units, potentially causing malfunctions and damage." "Our standard maintenance procedure requires de-energizing the HVAC system at the outdoor disconnect before performing any work." "The outdoor disco is readily accessible and is clearly marked for the HVAC unit that it controls."4.

Document Everything

Keep a record of your conversation with the inspector, including the code sections discussed and the arguments you presented.5.

Escalate If Necessary

If you cannot reach an agreement with the inspector, you may need to escalate the issue to a supervisor or another authority.

Important Considerations
Local Amendments

Be aware that local jurisdictions may have amended the NEC to include stricter requirements.


AHJ (Authority Having Jurisdiction)

Ultimately, the AHJ has the final say in interpreting the code.

In summary, while the inspector's concern about safety is valid, you have a strong argument that an additional disconnect inside the elevator machine room is unnecessary (given the existing outdoor disconnect), and potentially detrimental to the HVAC system's operation.


Good luck navigating this situation! Flag for review

Previous Question Next Question