Question: From 404.7 I was under impression main breaker on shall be up and off down. Am I missing an exception attached is an online picture. I feel as though I’m wrong

You're right to question what you saw. You are generally correct: the preferred orientation for a vertically mounted circuit breaker in the "on" position is UP. This is described in NEC 404.7.Here's a breakdown of 404.7 and why the image might be misleading or violate code

NEC 404.7 (indicating)
General Rule

All switches and circuit breakers used as switches shall be installed so that the "up" position of the handle is the "on" position.


Vertical Position

Where handles operate vertically rather than rotationally or horizontally, the "up" position of the handle shall be the "on" position.

Horizontal Position

Where handles operate horizontally, the "left" position of the handle shall be the "on" position.

Why the Image Might Be Problematic/Incorrect
1. Violation of Code

If the circuit breaker in the picture is indeed a standard vertically operating breaker and the panel is installed in the US, and the "ON" position is truly down, it
likely violates NEC 404.7.
2.


Misinterpretation

The breaker might be a type where "up/down" doesn't clearly indicate "on/off". These are less common. It's possible, though unlikely, that the panel and breaker are from a region with different standards (though the labeling appears to be in English).

Exceptions and Nuances
Handle Ties

If multiple single-pole breakers are "handle-tied" together to serve as a multi-pole switch, the orientation rule still applies to the tied unit as a whole.

Accessibility

While the rule is for safety and usability, the AHJ (Authority Having Jurisdiction) might consider the practical impact on accessibility during inspection. If the standard orientation creates an undue hazard due to the installation, the AHJ may allow an orientation that reduces that hazard

Key Takeaways
Standard Practice

In the US, the standard is "up for on, down for off" for vertical breakers.

Safety and Clarity

This standardization is vital for quick identification of breaker status, especially in emergency situations.


Verify the Label

The image might be misleading. Is there a clear "ON" and "OFF" indicator?*

Consult the AHJ

If you find a situation like this, the best course of action is to discuss it with the local electrical inspector (AHJ) for clarification.

In conclusion, unless there's a very unusual reason or the image is misleading, the picture likely shows a violation of NEC 404.7 if it shows that "ON" is DOWN.
You are right to question it. Flag for review