Topic: Service calculations

User: Jeffb30, Location: Minnesota

Asked on: Thursday, September 26, 2024 at 3:46 pm EDT
Answered on: Thursday, March 6, 2025 at 3:01 am EST

Question: Can you apply a demand factor to a multi family dwelling of 28 units that has fixed electrical space heating?

Yes, you can apply a demand factor to a multi-family dwelling of 28 units with fixed electrical space heating, but it's crucial to understand how to do it correctly and what code(s) govern the application. The applicable code is typically the NEC (National Electrical Code) in the US.Here's a breakdown of the process and considerations

1. NEC Article 220 is Key:
Article 220 of the NEC deals with branch-circuit, feeder, and service calculations. This is where you'll find the guidance and tables for applying demand factors. Specific sections within Article 220 are relevant



220.82 (Optional Calculation – Dwelling Units)
: This section offers a simplified calculation method and applies demand factors based on the total connected load. It's often used for dwellings. However, there are important stipulations about the use of optional calculations. 220.84 (Optional Method – Multifamily Dwelling): This section is specifically for multi-family dwellings and provides demand factors based on the number of dwelling units and the connected load. This is the section you'll want to use for your 28 unit dwelling. 220.12 (Show Window and Track Lighting) 220.14 (Outlets) 220.18 (Dwelling Unit Receptacle Loads)2. Steps for Applying Demand Factors (Using NEC 220.84)



Calculate the Connected Load

This is the sum of the wattage of all electrical loads within the 28 units. This includes:

General Lighting

Use the NEC's Volt-Amps per square foot requirements for dwelling units (refer to NEC 220.12).


Small Appliance Branch Circuits

Each kitchen counter receptacle circuit is typically calculated at 1500 VA.

Laundry Branch Circuits

Typically calculated at 1500 VA per circuit.


Fixed Appliances (Heating, Water Heaters, Ranges/Ovens, etc.)

Use the nameplate rating of each appliance.

This is crucial for your fixed electrical space heating.
Other Outlets

Receptacles not covered above, calculated per NEC requirements.


Apply the Demand Factors from NEC 220.84
This section provides a table based on the number of dwelling units. Here is the table from the 2023 NEC:| Number of Dwelling Units | Demand Factor (%)

---------------------------|--------------------
3–5 | 45
6–7 | 44
8–10 | 43
11–13 | 42
14–16 | 41
17–19 | 40
20–22 | 39
23–25 | 38
26–28 | 37
29–31 | 36
32–34 | 35
35–37 | 34
38–40 | 33
41–43 | 32
44–46 | 31
47–49 | 30
50–52 | 29
53–55 | 28
56–58 | 27
59–61 | 26
62 Units and Over | 25 | For 28 units, the demand factor is 37%. Multiply your total connected load (including the electric space heating) by 0.37 to get the calculated load. Consider Other Loads

Don't forget to factor in other loads not directly related to the dwelling units, such as:

Common Area Lighting

Hallways, stairwells, exterior lighting.


Elevators (if applicable)
Laundry Facilities (if common) Water Heating for common areas HVAC for common areas Fire Pumps or other special loads

Calculate these separately, and then add them to the calculated load from the dwelling units. Demand factors may also apply to some of these common area loads.

Example

Let's say the total connected load for the 28 dwelling units (including all lighting, receptacles, appliances, and electric space heating) is 1,000,000 VA. The common area loads are calculated at 50,000 VA.1.

Dwelling Unit Demand

1,000,000 VA 0.37 = 370,000 VA2.

Total Calculated Load

370,000 VA + 50,000 VA = 420,000 VAThis 420,000 VA is what you'd use to determine the required service size (ampacity of conductors and rating of the overcurrent protection).

Important Considerations & Cautions



Local Codes and Amendments

Always check with your local building department or electrical inspector. They may have amendments or interpretations of the NEC that affect how you apply demand factors.

Continuous Loads

Electric space heating is often considered a
continuous load. NEC defines a continuous load as a load where the maximum current is expected to continue for 3 hours or more. Continuous loads require special consideration. The branch circuits and feeders that supply continuous loads need to be rated for 125% of the continuous load. This is in 210.19(A)(1) and 215.2(A)(1).

Diversity is Key

Demand factors work because not all loads are operating at their maximum simultaneously. The more units you have, the more likely it is that this "diversity" exists.

Professional Calculations

It's strongly recommended that you consult with a qualified electrical engineer or licensed electrician to perform these calculations. Incorrect calculations can lead to undersized service equipment, which can be a serious safety hazard.


Feeder Size

This calculation provides the minimum service and feeder sizing. Oversizing is an option. Also, this calculation does not determine the panel size needed for the 28 units.

Future Expansion

Consider potential future increases in electrical load (e.g., residents adding more appliances, electric vehicle chargers). It might be wise to add some capacity beyond the minimum calculated load.


Documentation

Keep detailed documentation of your calculations, including all connected loads and demand factors applied. This will be helpful for inspections and future reference.

Article 220 part III (Optional Calculation for schools) and Article 220 Part V (Optional Calculation for New Restaurants) may apply.
210.23 Permissible loads on branch circuits. 220.3* Conductors shall be sized to carry not less than the larger of 220.3(A) or (B) loads supplied.In summary, while you can apply demand factors to a 28-unit multi-family dwelling with electric space heating, it's a process that requires careful consideration of the NEC, local codes, and the specific electrical characteristics of the building and its loads. Always consult with qualified professionals to ensure a safe and code-compliant installation. Flag for review