User: Frank D, Location: Los Angeles, CA
Asked on: Thursday, September 26, 2024 at 6:17 pm EDT
Answered on: Thursday, March 6, 2025 at 3:01 am EST
Question: In a multi-family building we are replacing the old gear, (existing gear has no mains on 12 meter set) with new meters and a main disconnec.We have a calculated load current of 513 amps.using 513 X 1.25 = 641 So 800 amp breaker?600 amp breaker max load at 80% = 480 amps800 amp breaker max At. 80% = 640 ampsso either way 800 amp main breaker?
Yes, your reasoning and conclusion are correct. Here's a breakdown and clarification: Calculated Load
513 amps
NEC 215.3 requires that feeders/services shall have sufficient ampacity for the calculated load and must be increased by 25 percent for continuous loads. (Loads expected to operate for three hours or more at one time) 513 amps 1.25 = 641.25 amps Standard Breaker Sizes
You're looking for a standard breaker size that can handle at least 641.25 amps, considering the 80% derating.
Breaker Analysis
600 Amp Breaker
600 amps 0.80 = 480 amps. This is less than your required 641.25 amps. It is insufficient.
800 Amp Breaker
800 amps 0.80 = 640 amps. While technically just shy of your 641.25 amp requirement, it's extremely close and is the nearest standard size.
Therefore, an 800 amp main breaker is the correct choice.Important Considerations and Best Practices
Manufacturer's Instructions
Always follow the manufacturer's instructions for the metering equipment and the main disconnect.
Overcurrent Protection Coordination
Ensure that the overcurrent protection scheme is properly coordinated. This means that the branch circuit breakers and the main breaker work together to trip in the correct sequence to isolate faults.
Future Load Growth
Consider potential future load growth when sizing the main breaker. If you anticipate significant load increases in the near future, it may be prudent to select a larger breaker (and appropriately sized conductors) to avoid having to upgrade the service again later.
Consult with an Electrical Engineer/Inspector
This is the most important point. Electrical work in multi-family dwellings has significant safety and code implications.
Consulting with a qualified electrical engineer and having the work inspected by a licensed electrical inspector is essential. They can review your calculations, ensure compliance with local codes, and provide guidance on best practices. Conductor Sizing
Remember to properly size the conductors (wires) feeding the main breaker to match its ampacity. This is crucial for safety and to prevent overheating.
Demand Factors
You may be able to use demand factors according to NEC 220, Part IV to reduce your calculated load. This is where the expertise of an engineer is helpful.
In summary, while your calculation and reasoning are generally correct, this is a critical electrical installation, and professional consultation is mandatory for safety and code compliance. Flag for review