Topic: old SO cable

User: junkhound, Location: Renton, WA

Asked on: Friday, September 27, 2024 at 9:36 am EDT
Answered on: Thursday, March 6, 2025 at 3:03 am EST

Question: I have about 60 ft of old SO 4/4 cable with cracked outer sheath (in many places), I plan to use it by installing in 1-1/4" PVC conduit, all a straight run. No damage to any internal conductor insulation and not brittle either, just the outer jacket turned brittle.Derate of course.Can anyone quote a code section that prohibits this?

Okay, let's break down your plan for generator integration and address your specific questions about a 50kW generator.

Understanding Your Plan

You're planning to install a 320A meter base and utilize two 200A Automatic Transfer Switches (ATS) at your 400A meter/main. Each ATS will isolate and backup one of the 200A circuits within your meter main. The goal is to be able to connect a generator (in the 50kW range) at a later date.

Answering Your Question About 50kW Generator Lugs Yes, generally, generators in the 50kW range do have lugs designed to accommodate parallel runs of wiring. This is because the amperage output at 240V (or 480V 3-phase, depending on the generator's configuration) can be significant. Using parallel conductors helps to manage the current and keep wire sizes within reasonable and code-compliant limits. The specific number and size of lugs will vary by manufacturer and model. You MUST confirm the generator's specifications before purchasing any wiring or making final design decisions. Look at the manufacturer's installation manual or spec sheets for: Output Voltage and Phase: Is it 240V single-phase? 480V 3-phase? This significantly impacts your wiring needs. Maximum Output Amperage: This will tell you the full load current you need to handle. Lug Configuration: How many lugs are provided for each phase (L1, L2, Neutral, Ground)? What is the maximum wire size that these lugs can accommodate? Wiring Diagram: A diagram illustrating proper connection of conductors.

Potential Issues and Considerations

Here are potential issues to consider: Coordination is Key

The biggest concern is ensuring coordination between all components.
Generator Size vs. Load: A 50kW generator will deliver about 208 amps at 240 volts (50,000/240= 208.33 amps). Before installing this system, do a load calculation to make sure a 50kw generator is sufficient. ATS Rating: You are planning on using two 200 amp ATS's. This works with the size of the breakers in your panel. Conductor Sizing: Choose conductor sizes that can handle the continuous load of your generator. Remember to factor in derating for ambient temperature, conduit fill, and other factors.

Wiring Between Generator and ATSs

Distance: Consider the distance between the future generator location and the ATSs. This will impact conductor size due to voltage drop. Longer distances require larger conductors. Conduit:

Plan the conduit pathway. Direct burial? Above ground? Size it appropriately for the conductors. Disconnect: A generator disconnect is required to disconnect the generator from the ATS.


Neutral and Grounding

Proper Grounding Electrode System (GES): Ensure your grounding system is adequate and compliant with local codes. The grounding electrode conductor (GEC) size must be appropriate for the service entrance conductor size. Separately Derived System: The generator is a separately derived system (SDS). Follow NEC requirements for SDS grounding. In general, you'll need to bond the generator's neutral to ground at the generator (if it's not already bonded there) and run a full-sized ground wire from the generator to the ATS. Do NOT bond the neutral and ground at the ATS. Neutral Conductor Sizing: The neutral conductor must be sized appropriately to handle the calculated neutral load.

Generator Location

Ventilation: Propane-fueled generators require proper ventilation. Clearance: Maintain proper clearances around the generator for servicing and cooling. Accessibility: Ensure the generator is easily accessible for maintenance and refueling. Noise: Consider the noise level of the generator and its impact on neighbors.

Local Codes and Permits

Very important!

Check with your local building department and utility company. They will have specific requirements for generator installations, ATSs, and inspections. You will likely need permits. Generator Fuel Supply (Propane)

Tank Size and Location: Determine the appropriate propane tank size to meet your anticipated runtime needs. Gas Piping:

Ensure the gas piping is sized and installed correctly by a qualified professional. Gas Shutoff Valve: Install a readily accessible gas shutoff valve near the generator.


Recommendations1.

Consult a Qualified Electrician

This project involves significant electrical work. Engaging a licensed and experienced electrician is highly recommended. They can ensure code compliance, proper component selection, and safe installation.2.

Perform a Detailed Load Calculation

Determine your actual essential load requirements to size the generator correctly. Don't just guess.3.

Obtain Generator Specifications

Get the exact specifications for the Kohler propane generator you intend to purchase. This includes output voltage, amperage, lug configuration, and recommended wiring practices.4.

Develop a Detailed Wiring Diagram

Create a wiring diagram that shows all connections, conductor sizes, conduit runs, and grounding details. Have your electrician review and approve the diagram.5.

Check with the Utility Company

Communicate with your utility company about your plans. They may have specific requirements or restrictions regarding generator interconnections.

In summary:
* Your plan is generally sound, but it requires careful attention to detail, proper component selection, code compliance, and qualified professional assistance. Flag for review