Question: Can you have a 208/120V service into a building and also have a 480/277V feeder from a separate building? My instincts say no, but I don't see the words that say no in either article.
You're right to question this. While the NEC doesn't explicitly forbid having both a 208/120V service and a 480/277V feeder in the same building, it creates significant safety and logistical problems, and should generally be avoided. Here's why
Problems and Code Concerns (Implied Limitations):
1. Identification & Coordination (NEC 215.5, 225.32)
This is the biggest practical issue. You would need to clearly and permanently identify which loads are supplied by which voltage system. Consider the following:
Panelboards and Circuits
Every panelboard and every circuit would need to be unambiguously labeled to indicate whether it's fed from the 208/120V service or the 480/277V feeder. Think about the long-term maintenance and potential for mistakes. An electrician might assume a 120V receptacle is available when it might be 277V.
Equipment
Any piece of equipment (e.g., HVAC, water heater) must be clearly marked with its voltage rating and the source of supply.
Personnel Safety
This is the biggest concern. Someone working on the electrical system must know which voltage they're dealing with. Accidental contact with 277V or 480V when expecting 120V can be fatal.2.
Mixing Voltages in Raceways (NEC 300.3(C))
While not a direct prohibition, it's relevant. It states conductors of different systems (e.g., 208/120V and 480/277V) shall not be installed in the same raceway, cable, or enclosure unless specifically permitted elsewhere in the NEC. Exceptions are very limited (e.g., control circuits). This is a significant practical constraint.3.
Neutral (Grounded Conductor) Issues
You cannot combine the neutrals of the 208/120V service and the 480/277V feeder. Each system must have its own separately derived neutral. Bonding and grounding become more complex.4.
Disconnects (NEC 225.31, 225.32)
The feeder to the building would require a readily accessible disconnecting means, either inside or outside the building. Coordination with the main service disconnect is important. The number of disconnects for a premises is also limited in the NEC.5.
Engineering Complexity
Designing, installing, and maintaining a system with two voltage levels is inherently more complex and expensive.
Why Your Instincts are Correct
Your instinct to avoid this situation is excellent. While technically possible to design a system that meets code with both voltage levels, the added complexity, cost, and potential safety hazards outweigh the benefits in almost all cases.
Alternatives
The far more common and recommended approach is to use a transformer to derive 120/208V from the 480/277V feeder. This way, you have a single point of supply to the building.
In Summary:
It's possible* but strongly discouraged to have a 208/120V service and a 480/277V feeder in the same building due to safety and logistical concerns. Use a transformer to step down the voltage instead. Consult with a qualified electrical engineer or inspector before considering such a design. Flag for review