Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Adding Grounds...

User: Coachmike, Location: Morris County, NJ

Asked on: Friday, September 27, 2024 at 3:54 pm EDT
Answered on: Thursday, March 6, 2025 at 3:04 am EST

Question: Have 4- 4" PVC feeders with 4- 750 MCM CU in each. Need to put a 250 MCM CU ground in each. Any ideas? TIA!

Okay, let's break down this situation and explore some practical solutions for adding that 250 MCM copper ground to your existing 4" PVC conduits, each already packed with four 750 MCM copper conductors. It's going to be tight, but there are options.

Understanding the Challenge



Conduit Fill

You're already likely near the maximum allowable conduit fill. Adding a 250 MCM copper conductor will significantly exceed that limit if you try to pull it
inside the existing conduit.

Code Compliance

Violating conduit fill requirements is a violation of the National Electrical Code (NEC). Overfilled conduits can lead to conductor damage, overheating, and potential fire hazards.

Practicality

Physically getting another large conductor into an already full conduit can be extremely difficult, even with copious amounts of lubricant.

Potential Solutions (in order of most preferred to least preferred, based on code compliance and practicality)


External Bonding/Grounding Conductor (Preferred & Likely Necessary)



Explanation

Instead of trying to cram the 250 MCM ground inside the conduit, run it outside and bond it to the metallic components at each end of the PVC conduit run (e.g., the enclosures where the conductors terminate).

How to Implement

Run a bare 250 MCM copper conductor alongside the PVC conduits. Secure it properly to the conduit using appropriate straps or clamps specifically rated for grounding conductors. Use listed grounding lugs (suitable for 250 MCM copper) to connect the grounding conductor to the metal enclosures at each end of the conduit run. Make sure the enclosures are properly grounded themselves (e.g., connected to the building's grounding electrode system). Consider exothermic welds (Cadwelds) at the termination points for ultimate reliability, especially in harsh environments.

Code Justification

NEC Article 250 (Grounding and Bonding) permits external bonding conductors. Section 250.130(C) speaks directly to using equipment grounding conductors outside of the raceway in certain circumstances. While not a complete parallel, this reinforces the concept.


Advantages



Code Compliant

Keeps you within conduit fill limits.


Practical

Much easier to install. You don't have to disturb the existing conductors.

Effective Grounding

Provides a solid, low-impedance ground path.


Inspectable

The grounding conductor is visible for inspection and maintenance.2.

Parallel Grounding Conductors (Less Desirable, Code Requires Careful Sizing)



Explanation

If adding
one 250 MCM conductor is impossible, consider running multiple smaller grounding conductors in parallel. The combined ampacity of the parallel conductors must equal or exceed the ampacity of a single 250 MCM copper conductor.

Code Considerations

NEC 310.10(H) Conductors in Parallel has very specific requirements: All parallel conductors must be the same length, conductor material, circular mil area, insulation type, and be terminated in the same manner. You must ensure that the overcurrent protection device is sized correctly to protect the smallest conductor in the parallel set.

How to Implement (Example)

Instead of one 250 MCM copper, you might be able to use two or three smaller conductors (e.g., two 4/0 AWG copper conductors – calculate their combined ampacity to ensure it equals or exceeds 250 MCM). Run these parallel conductors inside the conduit (but still carefully checking conduit fill). Terminate them identically at both ends with appropriately sized lugs.

Disadvantages

Complicates installation. Difficult to ensure equal current sharing between parallel conductors. Requires careful calculations and documentation for code compliance. Still might violate conduit fill.3.

Replace the Conduit (Expensive, but Best for Long Term)



Explanation

The cleanest solution (but most expensive and disruptive) is to replace the existing 4" PVC conduit with a larger size that can accommodate the existing conductors and the 250 MCM ground wire without exceeding fill limits.

Advantages

Full Code Compliance: Allows you to follow all conduit fill requirements. Future Proofing: Provides extra capacity for future expansion or changes.

Disadvantages

Significant cost (materials and labor). Requires a complete shutdown of the circuit. Disruptive to existing installation.4.

Using the Metal Conduit Body as EGC(NOT RECOMMENDED but used in some older installations)



Explanation

This is NOT a viable option with PVC conduit. It's mentioned for informational purposes only and in case you are encountering an older installation.

Disadvantages

The Metal Conduit Body itself must be electrically continuous and properly grounded. This may require bonding jumpers at each joint. May not provide as robust a ground path as a dedicated grounding conductor. PVC is Non-Metallic and thus this is not a viable option.

Important Considerations



Conduit Fill Calculations

Always perform accurate conduit fill calculations according to NEC Chapter 9, Table 1 and Annex C. Use the conductor dimensions in Chapter 9, Table 5. Overfilling a conduit is a code violation and a safety hazard. There are online conduit fill calculators available.

Local Codes and AHJ

Always consult with your local electrical inspector (the Authority Having Jurisdiction - AHJ) before starting any work. They may have specific requirements or preferences. They are the ultimate authority on code compliance in your area.

Qualified Electrician

This work should be performed by a qualified and licensed electrician who is familiar with the NEC and local codes.


Lubricant

If you attempt to pull any additional conductors, use a high-quality wire pulling lubricant specifically designed for the type of insulation on your conductors.

Recommendation

Based on the information provided,

Solution #1 (External Bonding/Grounding Conductor)
is the most practical, code-compliant, and cost-effective approach. It avoids the difficulty and potential code violations associated with trying to cram more conductors into already full conduits. Make sure to use appropriate hardware and installation methods for a secure and reliable grounding connection. Consult your local electrical inspector to confirm that this approach is acceptable in your specific situation. Flag for review

Previous Question Next Question