Topic: Conduits in quazite boxes (underground pull box)

User: Dsg319, Location: West Virginia

Asked on: Friday, September 27, 2024 at 4:45 pm EDT
Answered on: Thursday, March 6, 2025 at 3:04 am EST

Question: Example: pulling power conductors underground with wire type EGC and using rigid metal conduit. In the middle of the run there is an underground pull box where the raceways stub up though the open buttom.Would a bonding bushing be required for the continuity of the race way? Or could that be satisfied as long as each end of the 2 conduits tie into a metal enclosure bonded to the EGC on both sides of the run.In my head with theory this seems fine as there is still a fault current return path via both ends of the conduit being bonded to a metal enclosure.Was wanting to use plastic bushings. But not a big deal either way.

Okay, let's break down the requirements for bonding in this scenario, focusing on NEC (National Electrical Code) considerations.

The Scenario

Underground run of power conductors. Equipment grounding conductor (EGC) is present within the conduit. Rigid Metal Conduit (RMC) is used. Underground pull box with open bottom. Conduits stub up through the open bottom of the pull box. You're considering plastic bushings at the conduit ends in the pull box.

The Core Question: Is a Bonding Bushing Required at the Pull Box Conduit Entries?
Probably NOT, BUT with a VERY important caveat.Reasoning and Relevant NEC Sections


EGC in Conduit is Key

Because you have a dedicated EGC run with the power conductors inside the RMC, the primary fault current return path is through that EGC. This is significantly different than using the RMC itself as the sole fault current return path.2.

NEC 250.96(A): Bonding of Metal Enclosures and Raceways

This section generally requires bonding of metal enclosures and raceways that contain service or feeder conductors. However,

250.96(A) Exception

A raceway containing power conductors is permitted to enclose the equipment grounding conductor or be bonded to the metallic enclosure by connection to the equipment grounding conductor. This exception allows you to use the EGC within the conduit to satisfy the bonding requirement if the conduit is bonded to the metal enclosures at both ends.3.

NEC 250.92(B): Services
This section outlines the methods for ensuring electrical continuity of metal service raceways and equipment. While your scenario is not a service, the principles are still relevant for ensuring a reliable fault current path. It emphasizes the importance of proper connections and bonding at each end of the raceway.4. NEC 250.4(A)(5): Effective Ground-Fault Current Path

This is a fundamental requirement. The path must be:
Permanent Continuous Have sufficiently low impedance to facilitate the operation of the overcurrent protective devices. Capable of safely carrying the maximum ground-fault current likely to be imposed on it.5.

NEC 314.40(E): Bushings
The NEC only requires bushings on raceways where the conductors are #4 AWG or larger. A standard bushing should be installed as the conductor emerges from the raceway.

The Caveat (The "But VERY Important" Part)



Solid, Reliable Connections at BOTH ENDS

Your plan hinges entirely on having absolutely solid, low-impedance connections where the RMC enters the metal enclosures at both ends of the run. These connections MUST be made to points that are effectively bonded to the EGC within the enclosures. This is where things can go wrong.

Enclosure Bonding

The enclosures themselves
must be properly bonded to the EGC. The method used to bond the enclosure to the EGC will likely be the location where the RMC is also bonded.

Why Plastic Bushings CAN Be Used (with the Caveat Addressed)

Since you have the EGC within the conduit, the RMC isn't relied upon as the primary fault current return path between the enclosures. The plastic bushing simply provides physical protection for the conductors as they exit the conduit, which would be required for conductors #4 AWG and larger. The electrical continuity of the raceway is assured at the entry/exit points of the enclosures.

Why Bonding Bushings
Could Still Be a Good Idea (Even Though Technically Not Always Required)



Redundancy

A bonding bushing adds an extra layer of fault current protection. If, for some reason, the connection at one end of the conduit becomes compromised, the bonding bushing in the pull box might provide an alternate path to ground (depending on the nature of the compromise and the connection of the pull box itself to the grounding system).

Peace of Mind

Some electricians and inspectors simply prefer the added assurance that bonding bushings provide, even if the code technically allows for an exception.


Future Considerations

If the electrical installation changes in the future (e.g., the EGC is removed from the conduit), the bonding bushings would ensure that the RMC remains a reliable fault current path.

Inspection Issues

Some inspectors might be more comfortable seeing bonding bushings, even if the code compliance is technically met without them. This can avoid unnecessary delays or debates.

Best Practices and Recommendations


Prioritize Solid Connections

Ensure that the connections between the RMC and the metal enclosures at
both ends are exceptionally well-made, clean, and tight. Use appropriate bonding locknuts or grounding bushings specifically designed for this purpose.2.

Consider Bonding Bushings

While technically optional with the EGC present, consider using bonding bushings in the pull box for the reasons mentioned above (redundancy, peace of mind, potential future changes). The cost is relatively low compared to the potential benefits.3.

Verify Enclosure Bonding

Confirm that the metal enclosures are themselves properly bonded to the EGC.4.

Document Your Approach

Clearly document your grounding and bonding methods in your electrical drawings and specifications. This will help with inspections and future maintenance.5.

Consult with Local Inspectors

The most important advice is to consult with the local electrical inspector
before starting the work. They may have specific interpretations or requirements that you need to follow. They can give you the most accurate guidance for your specific jurisdiction.

In summary:
With a dedicated EGC run inside the RMC, bonding bushings may not be strictly required at the underground pull box if you have solid, low-impedance connections at both ends of the conduit run to properly bonded metal enclosures. However, consider the additional benefits and potential inspection issues associated with not* using bonding bushings, and consult with your local inspector before proceeding. Flag for review