Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Siemens Series Rating with Class T Fuses

User: Tainted, Location: New York

Asked on: Saturday, September 28, 2024 at 2:25 pm EDT
Answered on: Thursday, March 6, 2025 at 3:06 am EST

Question: Siemens series rating chart says that the HQP breaker is series rated with class T (300V) as shown below.I am wondering if this is saying I must strictly use a 300V class T fuse. What if I use a 600V class T fuse but my applied voltage is 208V? 208V is less than 300V. Would I still be able to achieve the series rating?

You're right to question this. Here's the breakdown: Series Rating Meaning

A series rating chart means that the combination of the upstream fuse (the Class T in this case) and the downstream circuit breaker (the HQP) has been tested and certified to safely interrupt a fault current higher than either device could handle alone. This is often done to save money on downstream breakers, as they don't need to be rated for the full available fault current.


Voltage Rating Considerations

While the voltage rating is important, you're on the right track with your thinking. The voltage rating of the fuse is its maximum voltage.

As long as your actual applied voltage (208V in your case) is at or below the minimum voltage rating of the fuse specified in the series rating chart, it should be acceptable.
This is because the fuse is designed to operate safely at or below that voltage. It is important to check with the fuse manufacturer to confirm what the minimum voltage rating is. Why the 300V Specification?

The 300V spec could be there for a variety of reasons (some of these can be assumed if not explicitly stated in documentation):

Testing and Certification

Siemens tested and certified
only with 300V Class T fuses for the specific series rating combination shown in the table. They haven't tested other voltage ratings, so they can't guarantee performance.

Minimum Voltage Required for Fuse Operation

It's possible the fuse needs a certain minimum voltage to properly arc and extinguish the fault current during an interruption. For example, some fuses need to see more than 120V to reliably operate.

Coordination

Perhaps, they intended to use 300V fuses so it can have coordination with other branch circuit devices.


Documentation

This information may be included in a more comprehensive document.

Therefore, here's the definitive approach


Consult the Manufacturer

The absolutely best thing to do is contact the manufacturer of both the Siemens HQP breaker and the Class T fuse you are considering. Ask them directly if a 600V Class T fuse is acceptable in this series-rated application, given your 208V system voltage. Provide them with the specific model numbers of both devices. They will provide the official answer based on their testing and certification.2.

Documentation

Look for any additional documentation from Siemens or the fuse manufacturer regarding the series rating. There might be more detail hidden away than what is in the chart itself.3.

If no documentation exists, and there's no specific testing of using a 600V fuse with the HQP breaker at 208V, it's best to adhere to the series rating chart and use the 300V Class T fuse.
In summary:

While theoretically, a 600V fuse might work safely at 208V (assuming it meets or exceeds the minimum voltage requirement). The series rating is only valid for the tested and certified combination. Deviating from that is taking a risk that the manufacturer hasn't approved and could compromise the protection of your system. Flag for review