User: Sparks4769, Location: Long Island, NY
Asked on: Saturday, September 28, 2024 at 2:34 pm EDT
Answered on: Thursday, March 6, 2025 at 3:06 am EST
Question: Hello Everyone, I’m an electrician on Long Island in NY. I am just curious on pool bonding terminations. I have a pool that was never bonded and I have gotten mixed reviews on bonding terminations throughout my career. This application happens to have the #8AWG bonding wire terminate in a Intermatic subpanel that supplies all the pool equipment. In the beginning of my career I was taught to terminate back to the main service panel and that terminating in the pool subpanel was no good. Please if anyone can shed some light on this
Okay, let's clarify the pool bonding requirements according to the NEC and best practices, especially in the context of a pool subpanel.
NEC Requirements (Generally)
Purpose of Bonding
The primary purpose of pool bonding is not for fault current clearing (though it can help in some scenarios). It's to create an equipotential plane. This means reducing voltage gradients in and around the pool area, minimizing the risk of shock to someone in or near the water.
Required Bonding Components
The following items, if metallic and within 5 feet of the inside wall of the pool, must be bonded together with a solid #8 AWG copper conductor:
All Metal Parts of the Pool Structure
(The pool shell itself if metal, reinforcing steel if it's a concrete pool, etc.)
Metal Fittings Within or Attached to the Pool Structure
(Ladders, handrails, diving board supports, etc.)
Metal Piping Systems
(Associated with the pool, such as circulation piping, fill lines, etc.)
Electrical Equipment
(Pump motors, filter housings, heaters, underwater lighting, etc.)
Metal Fences and Enclosures
If within 5 feet of the inside wall.
Pool Cover Motors The Equipment Grounding Conductor (EGC) of all circuits serving the pool. This is crucial! Bonding Connections
Must be made with listed bonding connectors suitable for direct burial, if buried. These connectors should be corrosion-resistant (e.g., bronze or stainless steel). Wire nuts or standard lugs not intended for direct burial are not acceptable.
Single Wire
The bonding conductor should be continuous, or made electrically continuous by listed means. It generally forms a loop around the pool area.
The Subpanel Question: Where to Terminate the Bonding Conductor
This is where the interpretation sometimes gets tricky, and is related to changes in the NEC over time. Older Thinking (and the source of your initial training)
In the past, it was more common to run the #8 bonding conductor all the way back to the main service panel's grounding electrode system (GES). The logic was that the GES was the ultimate reference point, and everything should tie back to it. This is still a compliant method if executed correctly.
Modern Interpretation and Code
The NEC allows (and often encourages) terminating the bonding conductor at the equipment grounding bus (the one that connects to the EGCs) of the pool's subpanel, provided that the subpanel is properly connected to the main service panel's GES.
Key Point
The pool subpanel's grounding system must be properly connected back to the main service's grounding electrode system (GES). Typically, this connection is established through the subpanel's EGC (equipment grounding conductor) which runs with the feeder conductors back to the main service.
Why this is acceptable
The equipotential bonding is primarily concerned with minimizing voltage differences within the pool area. As long as everything in the pool area is bonded together and connected to a common grounding point (the subpanel's EGC bus) that is itself reliably connected to the main service's GES, you've effectively created that equipotential zone.
Advantage
This simplifies the wiring in many cases, as you're not running a long #8 conductor all the way back to the main panel. It also often results in a lower impedance path back to the source in fault conditions.
NEC 680.26(C)
Specifically addresses the bonding conductor connection. It states that bonding conductors shall be connected to a common bonding grid, which can be, and often is, established at the pool equipment location (the subpanel).
Therefore, terminating the #8 AWG bonding conductor at the equipment grounding bus of the pool subpanel is permissible and compliant with the NEC if
The pool subpanel is properly grounded back to the main service panel's GES (through a properly sized EGC run with the feeder conductors). This is essential. The EGC must be sized according to NEC 250.122 based on the overcurrent protective device protecting the feeder to the subpanel.
2. All the other bonding requirements are met
All metallic parts listed above are properly bonded together in a continuous loop.3.
Listed bonding connectors are used suitable for the application (direct burial, if applicable).4. All bonding terminations are accessible for inspection and testing.
Important Considerations and Best Practices
Inspection
Your local electrical inspector is the ultimate authority. Consult with them before starting the work to ensure they are comfortable with your approach and interpretation of the code. Document your plan and discuss it.
Saltwater Pools
Saltwater chlorinators are highly corrosive. Use high-quality bonding connectors specifically designed for pool environments and consider using tinned copper bonding conductors. Sacrificial anodes may also be beneficial.
Corrosion
Carefully inspect all bonding connections for corrosion. Clean and re-tighten connections as needed. Use anti-oxidant compound on connections.
Grounding vs. Bonding
Don't confuse grounding with bonding. Grounding is about providing a low-impedance path for fault current to return to the source. Bonding is about creating an equipotential plane to minimize voltage differences.
GFCI Protection
All outlets and equipment serving the pool must be GFCI protected, as required by the NEC.
Voltage Drop
Ensure adequate voltage at the pool equipment by properly sizing the feeder conductors to the subpanel.
Documentation
Keep detailed records of all bonding and grounding connections, including photographs.
In summary: Terminating the bonding conductor at the pool subpanel is generally acceptable if the subpanel is properly grounded back to the main service and all other bonding requirements are met. However, always verify with your local inspector and follow best practices for corrosion prevention. Consider running a separate ground wire back to the main panel if there is any question on proper grounding. Flag for review