Question: Hello All,If the POCO available fault current is 65kAIC at POCO's 800A rated pullbox (208/120V, 3ph 4w) then what is the available fault current at the customer swbd which is 800A, 208/120V, 1ph 3w? POCO provide 3 phase service but the customer only uses 1 phase. The distance from the pullbox to the swbd is about 5ft.A formula would be appreciated.Thank you.
Okay, let's break down how to calculate the available fault current at your customer's single-phase switchboard. This is an important calculation for safety and to ensure proper equipment selection.
Understanding the Problem POCO (Power Company) Source
The POCO provides a 3-phase, 4-wire, 208/120V service with a documented available fault current of 65 kAIC at their pullbox.
Customer Load
The customer only uses one phase of the 3-phase service, fed to an 800A, single-phase, 3-wire switchboard.
Distance
The distance between the POCO pullbox and the customer's switchboard is a short 5 feet.
Goal
Determine the available fault current at the customer's single-phase switchboard.
Key Concepts1. Fault Current Reduction
The available fault current will decrease as it travels from the source (POCO pullbox) to the load (customer switchboard) due to the impedance of the conductors between the two points. Even a short run of conductors has some impedance.2.
Single-Phase vs. Three-Phase
Since the customer is only using one phase, you'll need to adjust the three-phase fault current to a single-phase equivalent.3.
Impedance
The most important factor in the calculation is the impedance of the conductors.
Formula and Calculation Steps
Here's the general approach and the formula we'll use:1. Calculate the 3-Phase Source Impedance (Zsource_3ph)
We need to convert the POCO's 3-phase fault current into an equivalent source impedance. The formula is:
Ifault_3ph)Where: `VL-L` = Line-to-Line Voltage (208V) `Ifault_3ph` = 3-Phase Available Fault Current at the POCO pullbox (65,000 Amps) `√3` = Square root of 3 (approximately 1.732)Calculation:Zsource_3ph = VL-L / (√3
65000) = 208 / 112580 = 0.00185 Ohms2. Zsource_3ph = 208 / (1.732
Calculate the Conductor Impedance (Zcable)
This is the trickiest part, as it requires knowing the conductor size, material (copper or aluminum), and type (THHN, XHHW, etc.). You'll also need to consult conductor impedance tables.
Assumptions (Example)
Let's assume you are using 500 kcmil copper conductors in parallel for each leg (A, B, and Neutral) to handle the 800A load over the short 5-foot distance. You will need two conductors for each of the phases and neutral.
Find Impedance from Table
Refer to a conductor impedance table (found in electrical engineering handbooks, the NEC Annex B, or online resources like Southwire's Voltage Drop Calculator). These tables usually provide impedance in Ohms per 1000 feet. For example, for 500 kcmil copper THHN conductor at 208V, you might find a value of approximately 0.032 ohms per 1000 feet for reactance (X) and 0.020 ohms per 1000 feet for resistance (R) at 75 degrees C.
Adjust for Length and Parallel Runs
Since you have a 5-foot run, calculate the impedance per foot: (0.032 + 0.020) / 1000 = 0.000052 Ohms/ft. Total length: 5ft 2 = 10 ft (for 2 cables in parallel) Calculate the total resistance and reactance: R = 0.020 ohms/1000 ft 10 ft = 0.00020 ohms X = 0.032 ohms/1000 ft 10 ft = 0.00032 ohms
Impedance Calculation
The total impedance of the cable is a complex number, but for fault current calculations, we can often approximate using the magnitude:Zcable = √(R² + X²)
3. Zcable = √(0.00020² + 0.00032²) = √(0.00000004 + 0.0000001024) = √0.0000001424 = 0.000377 ohms
Calculate the Total Single-Phase Source Impedance (Ztotal_1ph)
First, you need to convert the 3-phase source impedance to an equivalent single-phase impedance. Since the customer is using one phase to neutral, we can use the following:
Zsource_3phZsource_1ph = (3 / 2)
Then, add the cable impedance:Zsource_1ph = (3 / 2) 0.00185 = 0.002775 OhmsZtotal_1ph = Zsource_1ph + Zcable
4. Ztotal_1ph = 0.002775 + 0.000377 = 0.003152 Ohms
Calculate the Available Single-Phase Fault Current (Ifault_1ph)
Use Ohm's Law to calculate the fault current:
Where: `VN` = Nominal Line-to-Neutral Voltage (120V)Calculation:Ifault_1ph = VN / Ztotal_1phIfault_1ph = 120 / 0.003152 = 38,069 Amps
Result
Based on the assumptions above, the available single-phase fault current at the customer's 800A switchboard is approximately 38,069 Amps (38.1 kAIC).
Important Considerations and Caveats Conductor Size and Type are Critical
The conductor size and type significantly impact the impedance and, therefore, the fault current calculation. Use accurate conductor information from your design. Increase the conductor size to reduce voltage drop, which decreases impedance.
Temperature
The impedance of conductors increases with temperature. Consult tables for impedance values at the operating temperature (usually 75°C or 90°C for terminations).
Transformer Impedance
If there's a transformer between the POCO pullbox and the customer's switchboard (even a small one), you must include its impedance in the calculation. This will reduce fault current significantly.
Documentation
Obtain the official available fault current from the POCO. Do not guess. Ask for the documentation specifying the fault current at their connection point.
Software
For more complex systems, especially those with multiple transformers and long cable runs, use a dedicated electrical power system analysis software package (e.g., SKM PowerTools, EasyPower, ETAP). These programs automate the calculations and provide more accurate results.
Safety Factor
It's always wise to add a safety factor when selecting protective devices. Consider rounding up the calculated fault current value to the next standard interrupting rating.
Coordination Study
This is a simplified fault current calculation. For a comprehensive design, a full coordination study should be performed to ensure that all protective devices (circuit breakers, fuses) are properly coordinated to minimize the impact of a fault.
NEC Requirements
Refer to the National Electrical Code (NEC) Article 110.9 and 110.10 for requirements related to interrupting rating and fault current protection.
In summary, you must know the exact conductor size, type, length, and temperature rating to perform this calculation accurately. The assumed values in this example are for illustrative purposes only. Get the fault current information from the POCO and consult with a qualified electrical engineer to ensure your system meets all applicable codes and safety standards. Flag for review