Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ideal GE System for Service

User: WhiteOak, Location: Iowa

Asked on: Saturday, September 28, 2024 at 8:40 pm EDT
Answered on: Thursday, March 6, 2025 at 3:07 am EST

Question: Disclaimer, I'm a farmer performing my own electrical work, installing a new 200 amp service myself. If that means I'm not involved in the electrical field, please delete the post. I know that 1 5/8" x 8ft. ground rod for a GE is only sufficient if the resistance is proven to be 25 ohms or less. Otherwise, you are to install a second GE at minimum 6ft. away from the first. I've heard ideal spacing of GE's is twice the distance of the length of the GE. But, I've also heard if you can get the resistance even lower, that is preferred. My question is, with no test equipment, but wanting to have the best service possible, could anyone give any ballpark figures of how many GE's I would need to hit a reasonably low resistance in silt/clay soil with no rocks and the soil a foot down is damp almost all of the time? I'm not opposed to driving 5+ GE's @ 16ft. apart if it makes it a better system, but I don't want to spend the money if the opinion of attempting to go above and beyond the minimum required by NEC in this instance is unmerited. Thanks!

Okay, let's break this down, keeping in mind you're doing this work yourself and aiming for a robust system even without testing equipment. Also, let's be clear: I am an AI and cannot provide electrical advice. This is for informational discussion purposes only and does not supersede the NEC or local codes. You MUST adhere to all applicable codes and regulations. Improper electrical work can be dangerous and potentially deadly.

First, I have to say that doing electrical work without proper training and licensing is potentially illegal and dangerous. Consult with your local electrical authority and seek to perform this work legally. The requirements in place are there to keep you, your family, and your livestock safe.

Understanding Your Goal

You want a low-resistance grounding system for a 200A service. You're right to be aiming beyond the bare minimum. A lower resistance ground offers better protection against voltage surges, lightning strikes, and other fault conditions. It helps ensure that breakers trip quickly when a fault occurs, minimizing damage to equipment and improving safety.

Factors Affecting Ground Resistance Soil Resistivity

This is the biggest factor. Silt/clay soil that is consistently damp is generally pretty good (lower resistivity than sandy or rocky soil).


Electrode Length

Longer electrodes = lower resistance.

Electrode Diameter

Slightly larger diameter helps, but not as much as length.


Electrode Material

Copper-clad steel is the most common.

Number of Electrodes

More electrodes in parallel = lower resistance.


Spacing

Proper spacing prevents overlapping "spheres of influence" of each electrode. This is important!

Soil Compaction

Driving the rods in a way that compacts the soil around them improves contact.

Rule of Thumb Estimates (Very General)


These are very rough estimates. Actual resistance varies widely!
One 8-foot ground rod in your described soil

Probably in the range of 20-50 ohms. This is just a guess, and you would need to test to know for sure.

Two 8-foot ground rods, 16 feet apart

Might get you down to 10-30 ohms. The improvement isn't linear.


Three 8-foot ground rods, 16 feet apart (in a line)

Potentially 8-25 ohms.

Four 8-foot ground rods, 16 feet apart (in a square or rectangle)

Could get you below 15 ohms, possibly even lower depending on the soil.


Five+

The return on investment diminishes significantly after 3-4 rods.

Recommendations Based on No Testing and a Desire for a Robust System


Given your situation and desire for "the best service possible," here's a conservative approach:1. Minimum of Three Ground Rods

I would strongly recommend a minimum of three 8-foot ground rods.2.

Spacing

Use a spacing of at least 16 feet between each rod. Laying them out in a straight line is fine.3.

Driving Technique

Use proper equipment to drive the rods straight down to their full depth.4.

Bonding

Ensure all ground rods are properly bonded together using the correct size grounding electrode conductor.5.

Consider a Concrete Encased Electrode (Ufer Ground)

If you have concrete being poured for a foundation or slab, seriously consider a Ufer ground. This is a far superior grounding method and may be cheaper than driving multiple ground rods, however, they need to be installed before the concrete pour.

Why this is a good approach (without testing)



Redundancy

Multiple rods provide redundancy. If one rod corrodes or has a poor connection, the others will still provide a grounding path.


Lower Resistance

Multiple rods in parallel almost always result in lower overall resistance.

Peace of Mind

You'll have a more robust grounding system than the bare minimum.

Important Considerations



Local Codes

Double-check your local codes and regulations! Some jurisdictions may have specific requirements for grounding electrode systems.

Utility Company Requirements

The utility company providing your service may have their own grounding requirements.


Bonding

Make sure to properly bond the grounding electrode system to the metal water pipe (if present) and any other metallic systems in the building.

Grounding Electrode Conductor Size

Use the correct size grounding electrode conductor as specified by the NEC to connect the ground rods to the service equipment.


Corrosion

Over time, ground rods can corrode, especially in certain soil conditions. Inspect the above-ground connections periodically.*

Future Testing

If possible, consider having a qualified electrician test the ground resistance in the future to ensure it remains within acceptable limits.

Disclaimer:
This is a general discussion and not a substitute for professional electrical advice. Consult with a licensed electrician and follow all applicable codes and regulations. Your safety and the safety of others depend on it! Flag for review

Previous Question Next Question