Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: campground site grounding rod

User: jonathn3, Location: Tennessee

Asked on: Sunday, September 29, 2024 at 12:58 pm EDT
Answered on: Thursday, March 6, 2025 at 3:08 am EST

Question: At a campsite where trailers come and do hook ups. I find the service electrical is using a ground wire out to the electrical box and tie's it to the plumbing system, and using it as a grounding point. This happens at every site. Is this safe? Seems more like grounding rods all around rather than a bonding jumper to all sites. ( Sorry unsure how to add the picture I took.

No, this is absolutely not safe and is a dangerous and improper installation. It violates electrical code and creates a serious risk of electrocution, fire, and damage to equipment.Here's why and what needs to happen: Why it's dangerous



Improper Grounding Path

The plumbing system (especially if it's metallic) can become energized if there's a fault in any electrical appliance or wiring at any of the campsites. Instead of the fault current safely returning to the source through the proper grounding path (which should be a grounding conductor back to the service panel), it would flow through the plumbing.

Electrocution Hazard

Anyone touching the plumbing (faucets, pipes, etc.) while a fault exists could receive a dangerous electrical shock. This is especially dangerous if they are also in contact with the ground (e.g., standing in damp ground or touching a metal trailer frame).


Corrosion

Fault currents flowing through the plumbing system can cause rapid corrosion of the pipes, leading to leaks and weakening the system.

Lack of Proper Bonding

This is NOT bonding. Bonding is when all metal parts that could become energized are connected to form a path back to the source.


Code Violations

The National Electrical Code (NEC) specifically prohibits using metallic water piping systems as the sole grounding electrode. Proper grounding electrode systems are outlined in the NEC and typically involve grounding rods, ground rings, or connection to a metallic underground water pipe (under very specific conditions, and even then, supplemental electrodes are often required).

What needs to be done IMMEDIATELY


Disconnect Power

If possible, turn off the main power to the campsite's electrical system until the problem is resolved.2.

Contact a Qualified Electrician

A licensed and experienced electrician is
essential to inspect the entire electrical system and correct the grounding issues. They will be familiar with local codes and the NEC.3.

Correct Grounding System Installation

Install a proper grounding electrode system (e.g., grounding rods, ground ring). The size and number of grounding electrodes will be determined by the electrician based on the service size and local conditions. Ensure a grounding conductor (wire) runs from the service panel to the grounding electrode system. Bond the metallic water piping system to the grounding electrode system with a bonding jumper of the proper size. This creates an equipotential plane. Verify that each campsite has a proper grounding conductor in the electrical circuit that runs back to the service panel. The grounding conductor must be connected to the grounding pin on the receptacle.

Important Considerations



This is a SERIOUS SAFETY HAZARD.
Do not use the campsites until the electrical system is properly grounded and inspected. Document Everything

Take detailed pictures and notes of the improper grounding. Keep records of all inspections and repairs.


Contact the Campsite Management

Inform the campsite management immediately about the dangerous electrical situation. They are responsible for ensuring the safety of their facilities. If they are unresponsive, you may need to report the issue to your local electrical inspector.

In summary, the current setup is a dangerous and unacceptable electrical installation. It requires immediate attention from a qualified electrician to ensure the safety of everyone using the campsite.
Flag for review

Previous Question Next Question