Question: NEC 310.15(B)(3)(c) TEXT title: Raceways and Cables Exposed to Sunlight on Roof-TopsGoing over this article...AGAIN! I have went through some past threads and remain unsure that I have a complete understanding on when and what is a compliant action to take.OLD Threads..."Rooftop conductor derating.": Feb 4, 2016'don_resqcapt19'...provides a CMP write up I believe is related to the 2017 change."Derating Factor": Sept 20, 2017Seems to imply if your raceway is 7/8" or greater above the roof line then you are done...no derating regardless of what wire type you use."How do you know the ambient temperature of a roof?": Nov 17, 2021This thread seems to imply the same thing and also brings up reference to a temperature guide publication located at "https://www.copper.org/applications/electrical/building/pdf/rooftop.pdf". Tom Baker seemed to be familiar with this document.Can we come to a consensus on what is the proper approach to this design issue?Scenario 1: Raceway install at or above 7/8" on a roof. Insulation may be ANY acceptable wire for your application.a. NO adjustment for what is known to be a higher ambient than the provided ampacity tables? Simply use ampacities as provided in wire tables.b. Make adjustment for ambient, but not required to add additional 33deg C penalty from 310.15(B)(3)(c). Pull your temperature value from the(LINK) publication referenced above from the column headed "Max Temp".c. Make adjustment for exterior temperature adder per 2017 Handbook "Calculation Example" pulling your temperature value from the (LINK)publication referenced above from the column headed "2% Design Temp" and not required to add additional 33deg C penalty from 310.15(B)(3)(c).Scenario 2: Raceway install below 7/8" on a roof. Insulation may be ANY acceptable wire for your application.a. Make adjustment for ambient, and required to add additional 33deg C penalty from 310.15(B)(3)(c). Pull your temperature value from the (LINK)publication referenced above from the column headed "Max Temp".b. Make adjustment for exterior temperature adder per 2017 Handbook "Calculation Example" pulling your temperature value from the (LINK)publication referenced above from the column headed "2% Design Temp" and required to add additional 33deg C penalty from 310.15(B)(3)(c).Scenario 3: Raceway install below 7/8" on a roof. Insulation will be XHHW-2.a. NO adjustment for what is known to be a higher ambient than the provided ampacity tables? Simply use ampacities as provided in wire tables.b. Make adjustment for ambient, but not required to add additional 33deg C penalty from 310.15(B)(3)(c). Pull your temperature value from the(LINK) publication referenced abovefrom the column headed "Max Temp".c. Make adjustment for exterior temperature adder per 2017 Handbook "Calculation Example" pulling your temperature value from the (LINK)publication referenced above from the column headed "2% Design Temp" and not required to add additional 33deg C penalty from 310.15(B)(3)(c).I realize the wording in NEC 2020 was revised, I do not believe it changed the impact of 2017. I do not have a NEC 2023.
Let's break down NEC 310.15(B)(3)(c) and address your scenarios based on the 2020 NEC, as you stated. While the wording was revised, the intent and application largely remained the same. Keep in mind local jurisdictions can amend the NEC.
Understanding NEC 310.15(B)(3)(c) – The Core Concept
This section deals with the increased ambient temperature that conductors experience when installed in raceways or cables exposed to direct sunlight on rooftops. The key takeaway is that rooftop temperatures can be significantly higher than the ambient temperatures used in the standard ampacity tables.
Key Elements
Direct Sunlight
This section only applies when the raceway or cable is directly exposed to sunlight. If it's shielded from sunlight (e.g., under a solar panel, under a roof overhang), this section doesn't apply.
Rooftop
The conductors need to be on a roof.
Height Above Roof
This is critical. If the raceway is installed 7/8 inch (22 mm) or more above the roof, you do not need to apply the 33°C (59°F) adder. This is a big deal!
33°C (59°F) Adder
This is the penalty for raceways and cables closer than 7/8 inch to the roof surface. It's an addition to the ambient temperature.
Insulation Rating
The conductor's temperature rating is crucial. You must select conductors that can withstand the calculated elevated temperature. XHHW-2 is often used because of its higher temperature rating (90°C in dry and damp locations).
Ambient Temperature
You always have to start with the actual ambient temperature.
General Process for Calculations1. Determine Ambient Temperature
Find the appropriate ambient temperature for your location. You can use historical data or resources like the Copper Development Association document. This temp is "T-Ambient" in the steps that follow.2.
Determine if the 310.15(B)(3)(c) Adder Applies
Is the raceway/cable less than 7/8" above the roof? If yes, go to Step 3. If no, skip to step 4.
3.
Apply the 33°C Adder
Add 33°C (59°F) to the ambient temperature. T-Rooftop Ambient = T-Ambient + 33°C4.
Determine the Maximum Conductor Temperature
This is based on the insulation type (e.g., 90°C for XHHW-2). T-Max = 90°C for XHHW-2.5.
Calculate the Temperature Derating Factor
Use the formula in 310.15(B)(1) using the conductor's insulation temperature rating and the adjusted ambient temperature, T-Rooftop Ambient.
6.
Apply Other Derating Factors
Remember to consider other derating factors, such as the number of conductors in a raceway (310.15(C)).
7.
Determine the Adjusted Ampacity
Multiply the conductor's base ampacity (from the ampacity tables) by the temperature correction factor and any other applicable adjustment/derating factors.
Addressing Your ScenariosScenario 1: Raceway installed at or above 7/8" on a roof. Correct Answer: a. NO adjustment for what is known to be a higher ambient than the provided ampacity tables? Simply use ampacities as provided in wire tables. Explanation
Because the raceway is 7/8" or more above the roof, NEC 310.15(B)(3)(c) does not apply. You still need to consider the actual ambient temperature for your location and apply temperature correction factors from Table 310.15(B)(1), but you do not add the 33°C penalty.
Scenario 2: Raceway installed below 7/8" on a roof. Correct Answer: a. Make adjustment for ambient, and required to add additional 33deg C penalty from 310.15(B)(3)(c). Pull your temperature value from the (LINK) publication referenced above from the column headed "Max Temp". Explanation
Since the raceway is closer than 7/8" to the roof, the 33°C adder applies. You start with your ambient temperature, add 33°C, and then use that value to determine the temperature correction factor in Table 310.15(B)(1). The conductor's insulation rating then dictates if you can use it after you apply the temperature correction. Using Max Temp column value is the proper value to use.
Scenario 3: Raceway installed below 7/8" on a roof. Insulation will be XHHW-2. Correct Answer: b. Make adjustment for ambient, but required to add additional 33deg C penalty from 310.15(B)(3)(c). Pull your temperature value from the (LINK) publication referenced above from the column headed "Max Temp". Explanation
Using XHHW-2 changes nothing about the initial calculation process. You STILL need to follow 310.15(B)(3)(c) as stated above. What it DOES do is provide more allowable temperature range for the conductor to remain within rated values.
Important Considerations
Documentation
Always document your calculations clearly.
Safety First
Err on the side of caution. If there's any doubt, use a higher temperature rating for the conductors or increase the height of the raceway above the roof.
Local Amendments
Always check with your local electrical inspector for any local amendments to the NEC.
The Copper Development Association Document (copper.org link):
This document is a valuable resource for finding typical rooftop ambient temperatures. Use the "Max Temp" column for the actual* ambient temperature in your area as the starting point. Flag for review