User: engineeringthoughts, Location: Colorado
Asked on: Monday, September 30, 2024 at 11:09 am EDT
Answered on: Thursday, March 6, 2025 at 3:10 am EST
Question: Source to transformer stepped-up from 480/277V to 13.2 kV wye - delta (corner grounded). Then stepped down via delta (corner grounded) to wye (grounded) from 13.2 kV back to 480 V. The load is about 630 kVA and .9 pf. I only have line currents on the load (wye) side of A = 200, B = 16, and C=190 A, I need the neutral current on both wye sides and the line currents traced back to the source. This is a problem I have been working on (purely for myself).
Okay, let's break this down and work through the calculations. This is a good exercise in understanding transformer connections and current relationships.1. Load Side (480V Wye)
Given
kVA = 630 kVA Power Factor (PF) = 0.9 Line Currents: A = 200A, B = 16A, C = 190A
Calculate Phase Voltages
Voltage Line-to-Line = 480V Voltage Line-to-Neutral = 480V / √3 ≈ 277V
Calculate Real Power (kW)
kW = kVA PF = 630 kVA 0.9 = 567 kW
Calculate Reactive Power (kVAR)
kVAR = √(kVA² - kW²) = √(630² - 567²) ≈ 275 kVAR
Calculate Neutral Current
Since the neutral is grounded, it will carry any unbalanced current. The easy method (but not correct) is to add the currents from each phase together: 200A + 16A + 190A = 406A. This is not the way the neutral current operates. The neutral is the phasor addition of all three phases. Ia = 200 + 0i Ib = 16 cos(-120) + 16 sin (-120) i = -8 - 13.9i Ic = 190 cos(120) + 190 sin (120) i = -95 + 164.5i In = 97 + 150.6i Magnitude = √(97² + 150.6²) = 179.4 A (Neutral Current)
2. Load Side Transformer (480V Delta - 13.2kV Wye, Corner Grounded Delta)
Voltage Ratio
480V Delta : 13,200V Wye
Understanding Corner Grounded Delta
In a corner-grounded delta system, one of the phase conductors is connected to ground. This means the line-to-ground voltage on that phase is zero, and the other two phases have a line-to-ground voltage equal to the line-to-line voltage.
Current Transformation (Approximate)
We'll assume an ideal transformer for this calculation. The current on the delta side will be lower due to the higher voltage. Remember the current on the delta side will be a line current and the wye side will be line current. This means the currents will be inversely proportional to the square root of 3 times the voltage ratio. Current Ratio ≈ (480 V √3) / (13,200 V) ≈ 0.0629 Delta Side (13.2kV): A ≈ 200 A 0.0629 ≈ 12.58 A B ≈ 16 A 0.0629 ≈ 1.01 A C ≈ 190 A 0.0629 ≈ 11.95 A
Delta Current in each winding
Iab = Ia / √3 = 7.27 A Ibc = Ib / √3 = .58 A Ica = Ic / √3 = 6.9 A
3. Source Side Transformer (13.2kV Delta - 480V Wye, Corner Grounded Delta)
Voltage Ratio
13,200V Delta : 480V Wye
Current Transformation (Approximate)
Similar to above, but in reverse. Current Ratio ≈ (13,200 V) / (480 V √3) ≈ 16 Delta Side (480V): A ≈ 12.58 A / 16 ≈ 0.79 A B ≈ 1.01 A / 16 ≈ 0.06 A C ≈ 11.95 A / 16 ≈ 0.75 A
Delta Current in each winding
Iab = Ia / √3 = .46 A Ibc = Ib / √3 = .03 A Ica = Ic / √3 = .43 A
Important Considerations and Refinements
Transformer Losses
We've ignored transformer losses. In a real-world scenario, these losses (core and copper) will affect the current calculations. You'd need to factor in the transformer efficiency.
Magnetizing Current
Transformers require magnetizing current, which is primarily reactive. This adds to the primary current and is typically a few percent of the full-load current.
Phase Shifts
Delta-Wye transformers introduce a 30-degree phase shift between the primary and secondary voltages and currents. This is crucial for parallel operation but doesn't significantly affect the magnitudes of the currents in this type of hand calculation. For precise work, you'd need to account for this phase shift.
Corner Grounded Delta System
It's vital to understand that in a corner-grounded delta system, one of the phases is directly grounded. The currents in a corner-grounded system can be more complex to analyze than a standard delta system, especially during fault conditions.
Neutral Current (Source Side)
In a properly functioning, balanced wye system, the neutral current should be near zero (ideally). The more unbalanced the load, the higher the neutral current.
Disclaimer:
This analysis is based on simplified assumptions and provides approximate values. For critical applications or detailed power system analysis, use dedicated power system simulation software (e.g., ETAP, SKM PowerTools, EasyPower) and consult with a qualified electrical engineer. Corner-grounded delta systems require careful design and protection coordination. Flag for review