Question: There is no code that says the lighting inveter circuits(EM) have to be in a separate conduit from normal, correct?
You are correct. The NEC (National Electrical Code) does not explicitly require emergency lighting inverter circuits (EM) to be in separate conduits from normal lighting circuits unless specific conditions exist.Here's a more detailed explanation: General Rule
Generally, as long as the wiring methods are acceptable (e.g., conductors are properly insulated, conduit fill is within limits, etc.), you can run normal and emergency circuits together in the same raceway (conduit).
Exceptions / Situations Where Separation IS Required
Fire-Rated Cables
Where required to be installed as Fire-Rated cables (e.g. fire-rated cable assemblies or cables encased in concrete) the EM and normal conductors are required to be separated.
Fire-Rated Assemblies
If emergency lighting is required to maintain its operation during a fire, the wiring to that lighting might need to be protected by a fire-rated raceway or cable assembly. In such cases, it's common (and sometimes explicitly required by local codes or the building's fire safety plan) to keep the emergency circuits separate from normal circuits to prevent a fire in a normal circuit from taking down the emergency lighting. This separation ensures that a failure in the normal power system does not also compromise the emergency system.
Emergency System Integrity
Some jurisdictions or specific project requirements may dictate separation to ensure the highest level of reliability for the emergency lighting system. This is particularly common in critical facilities (hospitals, data centers, etc.).
Specific Equipment Instructions
The manufacturer's instructions for the emergency lighting inverter or transfer switch may have specific requirements regarding wiring and separation from other circuits.
Article 700 (Emergency Systems)
Reviewing Article 700 of the NEC is crucial. While it doesn't have a blanket "separate conduit" requirement, it does have requirements around independent wiring and protection of emergency circuits to ensure they function when needed. These requirements could lead to the practical need for separation in certain situations. For example, if the normal lighting circuit is likely to be subjected to conditions that could damage it, the emergency circuit would need to be protected from those same conditions.
Key Considerations
Local Codes
Always check your local building codes and amendments, as they may have stricter requirements than the NEC.
Design Intent
Consider the overall design intent of the emergency lighting system and the level of reliability required.
AHJ
When in doubt, consult with the Authority Having Jurisdiction (AHJ) for your project. They have the final say on what is acceptable.
In summary, while there isn't a general rule requiring separate conduits, it's vital to check for the exceptions above and to prioritize the reliability and integrity of the emergency lighting system. Think about potential failure scenarios and how separation might mitigate those risks. Flag for review