Question: If you have separate neutrals and using MC cable would you run separate MC cables like this or a multi circuit/neutral over to where there are a few devices with separate circuits.

Okay, let's break down the pros and cons of running separate MC cables versus a multi-circuit/neutral MC cable for a situation with a few devices on separate circuits.

Understanding the Options Separate MC Cables (Home Runs)

Each circuit has its own MC cable running directly from the panel to the device or junction box serving that device. Each cable contains a hot (ungrounded), a neutral (grounded), and a grounding conductor.


Multi-Circuit/Neutral MC Cable (Shared Neutral)

A single MC cable contains multiple hots (ungrounded), a shared neutral (grounded), and a grounding conductor. This allows for multiple circuits to be run within one physical cable assembly.

Factors to Consider
1. Code Compliance (NEC)

This is paramount. The NEC has very specific rules about multi-wire branch circuits (circuits that share a neutral).

Common Shutoff

NEC requires that all conductors of a multi-wire branch circuit (including the neutral) be disconnected simultaneously by the circuit breaker. This typically means using a 2-pole or 3-pole breaker for the circuit.


Neutral Continuity

The neutral conductor must remain intact and not be broken when devices are disconnected or removed. This is critical to prevent overvoltage on other circuits sharing the neutral.

Identification

The multi-wire branch circuit must be clearly identified at the panel and at any point where the wiring is accessible.2.

Load Balancing

Multi-wire branch circuits work best when the loads on each hot leg are relatively balanced. If one hot leg is significantly more heavily loaded than the others, the shared neutral can become overloaded.3.

Voltage Drop

Using a shared neutral can potentially reduce voltage drop compared to running separate cables, especially over longer distances, as the current in the neutral is the
difference between the currents in the hot legs.4.

Installation Complexity

Running separate MC cables is generally simpler to install and troubleshoot. Multi-wire circuits require careful wiring and attention to detail.5.

Cost

A multi-conductor MC cable will typically be more expensive than a comparable length of single-circuit MC cable (per conductor). However, you are using less cable overall.6.

Conduit Fill

If you are running the MC cable through conduit, a single multi-conductor cable will take up less space than multiple single-circuit cables.7.

Future Modifications

Separate home runs provide more flexibility for future modifications or additions to the electrical system.8.

Troubleshooting

Troubleshooting a multi-wire circuit can be more complex than troubleshooting separate circuits.9.

Safety

Improperly wired multi-wire circuits can be dangerous, leading to overloaded neutrals, voltage imbalances, and potential equipment damage or fire hazards.

Recommendation and Justification
Generally, for just a "few" devices, separate MC cables are often the simpler, safer, and more flexible option, especially if you're not extremely comfortable with the intricacies of multi-wire branch circuits.Why Separate MC Cables Are Often Preferred (in your scenario)



Simplicity

Easier installation, fewer points of failure, easier troubleshooting.


Safety

Less chance of wiring errors leading to overloaded neutrals or other problems.

Flexibility

Easier to modify or add circuits in the future without affecting other circuits.


Load Balancing is less critical

Since the devices are separate, it is less likely that an unbalance load on the neutral will occur

Less likely to violate NEC
: It is easier to make a mistake if you are not an experience electricianWhen a Multi-Circuit MC Cable Might Be Considered (less common in your scenario)



Significant Distance

If the devices are far from the panel, and voltage drop is a major concern, a well-designed and properly balanced multi-wire circuit might be considered.

Conduit Fill Issues

If space is extremely limited in conduits, a multi-conductor cable can save space.


Specifically Designed Multi-Wire Loads

If the devices are designed to operate on a balanced multi-wire circuit (e.g., some types of equipment with internal 120/240V transformers).

Cost savings.
If the cost savings of the multi-conductor MC cable is high enough it might be worth it if installed properly.

Important Considerations for Multi-Wire Circuits (If You Choose This Option)



Use a 2-pole or 3-pole breaker

Absolutely essential for a common disconnect.

Ensure Neutral Continuity

Wire the neutral in a way that it cannot be broken when devices are removed. Pigtail the neutral at each device location.


Labeling

Clearly label the circuit at the panel and at all junction boxes.*

Professional Installation

If you are not 100% confident in your ability to wire a multi-wire circuit correctly, hire a qualified electrician.

In summary:
Unless there are compelling reasons (long distances, conduit fill issues, specific equipment requirements), separate MC cables are generally the better choice for a small number of devices on separate circuits due to their simplicity, safety, and flexibility. Always prioritize safety and code compliance. If you do decide to use a multi-wire circuit, ensure you have a thorough understanding of the requirements and follow best practices for installation. If in doubt, consult a qualified electrician. Flag for review