Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Question: Externally Mounted EMT Under Commercial Hood?

User: OmniMan, Location: Bremerton, Washington

Asked on: Monday, September 30, 2024 at 8:47 pm EDT
Answered on: Thursday, March 6, 2025 at 3:12 am EST

Question: I’m having a very difficult time finding any specific info on externally mounted EMT under a commercial hood.We’re planning on installing two commercial stoves and a double oven. The 3/4 EMT, plugs and gas lines would be mounted externally on the wall behind the equipment.Could someone direct me to the code on that?

You're right to be diligent about code compliance for installations under a commercial hood. It's a critical area due to heat, grease, and potential fire hazards. While the NEC doesn't have a specific section dedicated solely to "EMT under a commercial hood," the requirements are scattered across several articles that apply based on the environment. Here's a breakdown of the relevant code sections and considerations, along with a clarification

Key Considerations and Relevant NEC Articles:

1. Operating Temperature



NEC 110.3(B) (Installation and Use)

This is foundational. Electrical equipment MUST be installed and used according to its listing and labeling. This means the EMT, fittings, wire, and any boxes need to be rated for the maximum anticipated ambient temperature under the hood. Commercial cooking equipment can produce extremely high temperatures.


Solution

Consult the hood manufacturer's specifications to determine the maximum ambient temperature the area behind the equipment will reach. Then, select EMT, wiring, and fittings with appropriate temperature ratings. This often necessitates using high-temperature-rated conductors (e.g., THHN/THWN-2, XHHW-2, or even more specialized high-temperature wire) and corresponding fittings.2.

Damp and/or Wet Locations



NEC Article 100 (Definitions)

Defines "Damp Location" and "Wet Location." A commercial kitchen
can be classified as a damp or wet location depending on cleaning practices.

NEC 314.15 (Damp, Wet, or Corrosive Locations)

Boxes in damp or wet locations must be listed for the purpose and be placed or equipped to prevent moisture from entering or accumulating within the box. This likely means using listed wet-location boxes with appropriate gaskets and fittings.

NEC 314.40(D) (Exposed Surface Extensions)

In damp or wet locations, boxes and fittings placed in walls or ceilings shall be so arranged or equipped as to prevent water from entering the raceways or equipment.


NEC 300.6 (Protection Against Corrosion)

Raceways, cable trays, cablebus, auxiliary gutters, cable armor, boxes, cable sheathing, cabinets, metal equipment, and supporting hardware in areas subject to severe corrosive influences shall be of material suitable for the conditions. Or, shall be protected by corrosion resistant coatings.

Solution

Even if not
directly hosed down, kitchens are often considered damp locations due to cleaning and condensation. Use EMT fittings listed for wet locations (e.g., compression connectors with sealing rings). Consider stainless steel EMT and fittings in particularly corrosive environments (e.g., near saltwater).3.

Mechanical Protection



NEC 300.4 (Protection Against Physical Damage)

Wiring methods must be protected from physical damage.

Solution

Ensure the EMT is securely supported to the wall with appropriate straps or clamps. Consider using rigid metal conduit (RMC) instead of EMT in areas particularly prone to impact.4.

Wiring Method



NEC Chapter 3 (Wiring Methods and Materials)

Covers the acceptable wiring methods (e.g., EMT, RMC, MC cable).

Solution

EMT is generally permitted in commercial settings, but ensure it's properly installed and supported.5.

Clearance and Access



NEC 110.26 (Spaces About Electrical Equipment)

Adequate working space must be maintained around electrical equipment for safe operation and maintenance. This applies to the outlets and disconnects.

Solution

Make sure the EMT and any boxes do not obstruct access to the cooking equipment or interfere with hood maintenance. Check local building codes regarding the positioning of utilities behind cooking equipment.6.

Grounding



NEC Article 250 (Grounding and Bonding)

Essential for safety. The EMT must be properly grounded.

Solution

Use listed EMT fittings and ensure proper bonding jumpers are installed.7.

Sealing



NEC 300.7 (Raceway Seal)

Where portions of a raceway are known to be subjected to different temperatures and where condensation is known to be a problem, the raceway shall be sealed.

Solution

If the temperature difference between the area inside and outside the hood is substantial, sealing the EMT may be necessary to prevent condensation.

Important Considerations/Clarifications



Local Codes and AHJ (Authority Having Jurisdiction)



This is CRITICAL.
Local codes may have stricter requirements than the NEC. Always consult with your local building department or electrical inspector BEFORE starting the work. They have the final say. Your inspector may require specific types of fittings, conduit materials, or installation methods based on local experience and interpretations of the code. Grease Accumulation

Consider how grease accumulation will be managed. Will the EMT and boxes be regularly cleaned? If so, this affects the selection of materials and enclosure types.


Stove and Oven Connections

Pay close attention to the manufacturer's instructions for the stoves and ovens regarding electrical connections. They may have specific requirements for the type of conduit, wire size, and overcurrent protection.

Disconnect Switches

You will almost certainly need readily accessible disconnect switches for each piece of cooking equipment, located within sight of the equipment (or capable of being locked open). The placement of these disconnects needs to be considered in relation to the EMT runs.

Example of How to Apply the Code

Let's say the hood manufacturer states the maximum ambient temperature behind the equipment is 150°F (65.5°C).
1. You need wire rated for at least 75°C (THHN/THWN-2 is a common choice).2. The EMT fittings must also be rated for that temperature.
3. Because it's a commercial kitchen, you'll likely use wet-location-rated boxes and fittings.4. The EMT will be securely supported to the wall.
5. You'll ensure the EMT is properly grounded.


In summary:
There's no single "EMT under a hood" section in the NEC. Instead, you must apply various articles related to temperature ratings, damp/wet locations, mechanical protection, grounding, and working space. Always consult with your local electrical inspector before* beginning the installation. They will provide guidance specific to your location and ensure the installation meets all applicable requirements. Your inspector's interpretation of the code is what matters most. Flag for review

Previous Question Next Question