Topic: Corrosion issues after mold remidiation

User: BECo, Location: Indiana

Asked on: Monday, September 30, 2024 at 10:29 pm EDT
Answered on: Thursday, March 6, 2025 at 3:13 am EST

Question: Called out to replace a pull chain fixture in an unfinished basement, which turned out to be a fixture that caught fire and burned up some wiring. After corrosion concerns and further troubleshooting, I was informed that mold remediation had been performed and everything had been severely coated with a corrosive spray. All steel and copper is severely corroded. Has anyone seen long term issues from remediation work? Worried about possible future issues due to severity of corrosion on bare copper and loose/ sloppy device terminations.

You've hit on a very real and legitimate concern. It sounds like the mold remediation was done aggressively and without proper consideration for the long-term effects on electrical systems. Corrosive sprays, particularly those containing bleach or other strong chemicals, can wreak havoc on electrical components. Here's a breakdown of potential issues and what you should consider

Immediate Concerns:
Weakened Conductors

The corrosion on the bare copper reduces the cross-sectional area of the conductors, increasing resistance. This can lead to:


Overheating

Higher resistance generates more heat under load, potentially causing insulation breakdown, fire hazards, and premature component failure.

Voltage Drop

Increased resistance causes voltage drop, leading to dimming lights, malfunctioning equipment, and overall poor electrical performance.


Compromised Connections

Corrosion at terminals (screws, wire nuts, push-in connectors) creates loose, high-resistance connections. These are prime locations for overheating and arcing. The sloppy terminations are a separate but compounding issue.

Insulation Degradation

The corrosive spray can attack the insulation on wires, making it brittle and prone to cracking. This increases the risk of short circuits and ground faults.


Equipment Failure

Corrosion can affect the internal components of devices like ballasts, transformers, and even circuit breakers, leading to premature failure.

Safety Hazards

Ultimately, all of these issues increase the risk of electrical shock and fire.

Long-Term Issues



Progressive Corrosion

The corrosive residue can continue to react over time, even if it appears dry. This means the problems will only get worse.

Hidden Corrosion

Corrosion can occur inside electrical boxes, conduit, and equipment housings, where it's not readily visible. This makes it difficult to assess the full extent of the damage.


Reduced Lifespan of Electrical System

The overall lifespan of the electrical system in the affected area will be significantly reduced.

Recurring Problems

You may see recurring issues with lights flickering, breakers tripping, or equipment malfunctioning.

What to Do (Safety First!)


Document Everything

Take detailed photos and videos of the corrosion, sloppy terminations, and any other problems you find. This is crucial for liability protection and for communicating the issues to the customer.2.

Inform the Customer Immediately

Explain the severity of the corrosion and the potential long-term risks.

Do not minimize the problem.
It's better to be upfront and honest.3. Recommend a Comprehensive Evaluation

Suggest that a qualified electrician perform a thorough inspection of the entire electrical system in the affected area. This should include:


Visual inspection

Looking for corrosion, damaged insulation, and loose connections.

Megger testing (insulation resistance testing)

To assess the integrity of the insulation on wires.


Voltage drop testing

To identify areas with excessive voltage drop.

Thermal imaging

To identify hot spots caused by loose connections or overloaded circuits.4.

Offer a Repair Plan

Based on the inspection, develop a plan to address the corrosion issues. This might include:


Replacing corroded wiring

This is often the best solution, as it eliminates the source of the problem.

Replacing corroded devices

Outlets, switches, light fixtures, circuit breakers, etc.


Cleaning corroded connections

Use a wire brush and electrical contact cleaner to remove corrosion from terminals. Then, tighten connections securely.

This is usually a temporary fix at best.
Applying corrosion inhibitors

Use a product specifically designed to protect electrical components from corrosion.


Properly sealing electrical boxes and conduit

To prevent moisture and further corrosion.5.

Consider a Licensed Mold Inspector

Suggest the customer consult with a licensed mold inspector to understand which chemicals were used and if there are any specific recommendations for remediation.6.

Be Wary of Band-Aid Solutions

Simply replacing the burned fixture is not enough. The underlying corrosion problem needs to be addressed.7.

Get it in Writing

Provide the customer with a written estimate for the inspection and repair work. Clearly state the scope of the work, the potential risks, and any limitations. Also, document the customer's decision (whether they choose to proceed with the recommended repairs or not).8.

Know When to Walk Away

If the customer is unwilling to address the corrosion issues, you may want to decline the job. You don't want to be liable for future problems caused by the corrosion.

Important Considerations



Building Codes

Ensure that all work is done in accordance with local building codes and the National Electrical Code (NEC).


Liability

You are responsible for the work you perform. If you simply replace the burned fixture without addressing the underlying corrosion problem, you could be held liable if a fire or other incident occurs in the future.*

Insurance

Check with your insurance carrier to ensure that you are covered for potential claims related to corrosion issues.

In summary, you are right to be concerned. The corrosive spray from the mold remediation has likely created a significant hazard. Document everything, inform the customer, and recommend a comprehensive evaluation and repair plan.