Question: Can RMC run exposed along fence line and be supported by fence posts at intervals 10 feet or less? Will this be code compliance?
Let's break down whether running Rigid Metal Conduit (RMC) exposed along a fence line and supported by fence posts is code-compliant. We'll focus on the National Electrical Code (NEC), as it's the standard in the US. Keep in mind that local jurisdictions can amend the NEC, so you must check with your local electrical inspector for definitive approval.
Factors to Consider & Code References
1.
Support Requirements for RMC (NEC Article 344)
NEC 344.30(B)(1)
RMC must be supported at intervals not exceeding 10 feet (3 m). Your proposed support at fence posts 10 feet or less apart meets this distance requirement. However, the manner of support is also crucial.2.
Method of Support
NEC 344.30(A)
"RMC shall be installed as a complete system in accordance with 300.18 and shall be securely fastened in place and supported in accordance with 344.30(B) and (C)." Critically, the conduit must be securely fastened. This is the most problematic area for your fence post idea. Simply strapping RMC to a fence post is unlikely to be considered "securely fastened" without the correct hardware.
What constitutes a "secure fastener" for RMC to a fence post? Think about: The type of fence post
Wood, metal, concrete? This affects what type of fastener you can use.
The environment
Is it subject to vibration, wind, or other stresses? The fastener needs to withstand these forces.
Material Compatibility
Avoid dissimilar metals that could corrode. Use galvanized or stainless steel hardware.
Specific UL-Listed Conduit Clamps/Straps
The best approach is to use UL-listed conduit clamps or straps specifically designed for securing RMC. These are designed to meet specific pull-out and shear strength requirements. Examples include: One-hole straps Two-hole straps RMC clamps with backplates that can be attached to the fence post.3.
Protection from Physical Damage (NEC 300.4)
NEC 300.4(D)
"Where subject to physical damage, raceways, cable armor, and cable sheaths shall be protected." A fence line could be considered an area subject to physical damage. Consider: Is it in an area where vehicles could hit it? Is it exposed to people or animals that might tamper with it? If deemed subject to physical damage, you might need additional protection like: Guarding the conduit with a physical barrier. Using a larger conduit size for increased strength.4.
Environmental Considerations (NEC 300.6)
NEC 300.6
"Metal raceways, cable trays, cablebus, cable armor, boxes, cable sheathing, cabinets, metal enclosures, fittings, supports, and support hardware shall be of materials suitable for the environment in which they are to be installed." Consider: Is the area wet, corrosive, or exposed to chemicals? Use appropriately coated or corrosion-resistant RMC and fittings. Is the area subject to extreme temperature fluctuations? Use expansion couplings if needed (see below).5.
Expansion and Contraction (NEC 300.7(B))
NEC 300.7(B)
"Raceways shall be provided with expansion fittings where necessary to compensate for thermal expansion and contraction." Long runs of RMC exposed to temperature changes can expand and contract significantly. If the temperature variation is large enough, you'll need expansion couplings to prevent stress on the conduit and supports. Consult NEC Chapter 9, Table 10 for expansion characteristics of RMC.6.
Accessibility (NEC 314.29)
Ensure that any junction boxes or pull points are accessible. You can't bury them behind the fence or make them inaccessible without tools.7.
Proper Grounding (NEC Article 250)
The RMC must be properly grounded to provide a safe path for fault current. This typically involves bonding the conduit to the grounding electrode system.
Summary and Steps to Take
Distance is OK
Your proposed spacing of 10 feet or less between supports meets the distance requirement in the NEC.
Secure Fastening is Key
The biggest challenge is how you attach the RMC to the fence posts. Simply strapping it on with generic straps is likely insufficient. You need UL-listed conduit clamps/straps suitable for the environment and securely fastened to the fence posts.
Physical Damage
Evaluate the risk of physical damage. If there's a risk, provide additional protection.
Environmental Considerations
Select RMC and fittings suitable for the environment.
Expansion/Contraction
Determine if expansion couplings are needed.
Grounding
Ensure proper grounding of the RMC.
Consult Local Inspector
Crucially, contact your local electrical inspector before starting the work. Show them your plan and ask for their specific requirements. They have the final say in whether your installation is code-compliant. Provide them with details on the type of straps you intend to use and how they will be attached to the posts.
In short, running RMC along a fence line can* be code-compliant, but it depends heavily on using the correct hardware, securely attaching it to the fence posts, and addressing potential physical damage and environmental factors. Always consult with your local electrical inspector. Flag for review