User: Treyhagg, Location: Durant, Oklahoma
Asked on: Tuesday, October 1, 2024 at 6:49 pm EDT
Answered on: Thursday, March 6, 2025 at 3:16 am EST
Question: So I’ve got one I’m kind of at a loss for. Our local co-op has started using a meter base with 200A breakers built in to the base itself. My question is, would that be considered the first means of disconnect for the sake of bonding? Also, for context, we did a 320 can with parallel lugs for both legs of the hots and neutrals, but it only had a singular grounding lug so it made me question where the right place to bond would be and if I’m required to pull a ground to the meter in that instance.
Okay, this is a good question, and the answer has some nuances dependent on your local interpretation of the NEC and any local amendments. Let's break it down.
Is the 200A Breaker in the Meter Base the First Means of Disconnect? Yes, most likely. If the 200A breakers built into the meter base are the first overcurrent protection device (OCPD) after the service point, and they are readily accessible to the homeowner or fire department, then they generally meet the definition of the first means of disconnect. The NEC requires a readily accessible disconnect means for each service entering a building (230.70). Importance of Local Interpretation
Check with your local inspector. Some jurisdictions might have specific interpretations or amendments. For example, some might consider the meter itself to be the service point, and then the disconnect after the meter is the first means.
Bonding Location with 320A Can and Parallel Lugs
This is where things get a little trickier. Here's a breakdown:1.
Single Grounding Lug Issue
Having a 320A meter can with parallel lugs for hot and neutral conductors, but only one grounding lug is problematic. A 320A service requires a substantial grounding electrode conductor.2.
Required Grounding Electrode Conductor (GEC)
You are absolutely required to have a grounding electrode conductor connecting the grounded (neutral) conductor at the service to the grounding electrode system (ground rod(s), water pipe, etc.). This is non-negotiable for safety and fault current path.3.
Where to Connect the GEC
Because you only have one lug, there are two possible options that comply with the NEC. You can run a supply side bonding jumper from the neutral bar to the meter enclosure, and then bond your GEC to the meter enclosure. The second option is to replace the buss bar that is in the 320 meter can.
Here's how to approach it
Confirm with Your Inspector
Before proceeding with anything, discuss this specific setup with your local electrical inspector. Get their explicit approval on the bonding method. Document their response.
Ground Rod Location
You will have to determine where your ground rods are in relation to your meter location. If your ground rods are located somewhere else on the property, the supply side bonding jumper you install should also run to the ground rods.
Pulling a Ground to the Meter (Supply-Side Bonding Jumper)
Yes. You need to pull the grounding electrode conductor to the can in order to provide ground fault current path and make the 200amp breakers effective.
Important Considerations and Best Practices
Material of Grounding Electrode Conductor
Use the correct size copper or aluminum conductor (or copper-clad aluminum) based on NEC Table 250.66, which is determined by the size of your ungrounded service conductors. In a 320A service, this will likely be a substantial conductor.
Enclosure Bonding
Ensure the meter enclosure itself is properly bonded.
Tightening
Use a torque wrench to tighten all lugs to the manufacturer's specifications. Overtightening or undertightening can lead to connection failures and dangerous arcing.
Inspection
Be present during the electrical inspection to explain your grounding and bonding method.
In Summary:
The meter base with the integrated 200A breakers is likely the first means of disconnect. The core issue is the single grounding lug in the 320A can with parallel lugs. You MUST have a grounding electrode conductor connected to a proper grounding electrode system, and because of the single lug, it is recommended to bond the GEC to the meter enclosure itself. Get this approach approved in writing by your inspector before proceeding. Do not proceed until you have this approval. This ensures safety and compliance with the NEC. Flag for review