Topic: Demand Loads for Single Family Dwelling per NFPA 70A

User: bearthebuilder3000, Location: Tampa, FL

Asked on: Wednesday, October 2, 2024 at 3:43 pm EDT
Answered on: Thursday, March 6, 2025 at 3:18 am EST

Question: Hi Everyone,I'm an architect / builder working on a new spec house prototype and I was hoping to get some guidance on how to determine the overall demand load for the electrical panel. I'm pretty well versed in FBC and navigating code in general, but I'm new to electrical design and NFPA 70A has been a bit challenging.I've put together my panel schedule and figured out all of my connected loads , but I cant seem to figure out which demand factors to apply to which connected loads in order to determine the total demand load for the panel. I've linked a working copy of the plans and schedules. Any insight would be appreciated.Linked Plan & Schedules - Please disregarding circuit callouts on plans. That was a first pass and has not been updated to match the linked panel scheduleConnected LoadsLighting: 1.25 KVAReceptacles: 9.42 KVAOnly includes 110V receptaclesMotors: 0.90 KVA(2) 50W exhaust fans (Not sure if this is miscategorized. I've sometimes seen it listed under lighting)(1) 800W Garage Door Opener.AC: 1.3 KVAAHU onlyHeating: 5.0 KVASupplemental heat kit only. Condensing unit omitted as non-coincidental.Kitchen: 16.05 KVAIncludes small appliance circuits plus all kitchen appliances.Should kitchen appliances be included here or should they be included under receptacles?Other: 12.25 KVAIncludes water heater, dryer, washer, and smoke detectorsTotal Connected Load = 46,170 VA / 240V = 192.38 AThis is where I'm stuck. I've been reviewing NFPA 70A for the last two days but don't understand how to get from the total connected load to the demand load.

Okay, I understand your challenge. Applying demand factors correctly can be tricky. Let's break down how to estimate your demand load based on your connected load and the NEC (NFPA 70A). I'll focus on the areas that are likely to have demand factors applied. This is NOT a substitute for a licensed electrical engineer's design and review. This provides general guidance based on common interpretations of the NEC, but local codes may vary, and a qualified professional should always be consulted.

IMPORTANT NOTES BEFORE WE START



This analysis is for determining the service load and main panel size.
It's not necessarily what you'd use for branch circuit sizing (e.g., you still need to size a 20A circuit for those kitchen receptacles, even if the overall demand factor suggests a lower contribution to the total load). Safety Factor

It's good practice to add a safety factor to your final calculated demand load. Many engineers add 15-25% as a cushion for future expansion or unforeseen loads.

Local Codes Prevail

Always check for local amendments to the NEC. Some jurisdictions have more stringent requirements.


Licensed Professional

This is a guide, not a substitute for a licensed electrical engineer. You need an electrical engineer to sign off on the final electrical design.Here's a breakdown, focusing on the relevant NEC articles and how to apply them to your loads:

1. General Lighting Load



NEC 220.12

For dwelling units, the general lighting load is calculated at

3 VA per square foot
. You didn't provide the square footage of the house, but let's assume, for example, the house is 2000 sq ft. General Lighting Load = 2000 sq ft 3 VA/sq ft = 6000 VA = 6.0 KVA NEC 220.42

Demand factors apply to general lighting as follows: First 3000 VA: 100% demand factor (3000 VA) From 3001 VA to 120,000 VA: 35% demand factor ((6000 VA - 3000 VA) 0.35 = 1050 VA) Total Lighting Demand = 3000 VA + 1050 VA =

4050 VA = 4.05 KVA
2. Receptacle Load (General Use)



NEC 220.14(H)

Similar to lighting, general-use receptacles are calculated at

180 VA per outlet
. You've already provided this, which is great. 9.42 KVA. NEC 220.44

Applies the same demand factors as lighting: First 3000 VA: 100% demand factor (3000 VA) From 3001 VA to 120,000 VA: 35% demand factor ((9420 VA - 3000 VA) 0.35 = 2247 VA) Total Receptacle Demand = 3000 VA + 2247 VA =

5247 VA = 5.25 KVA
3. Small Appliance Branch Circuits (Kitchen)



NEC 220.52(A)

Requires a minimum of
two 20-ampere small appliance branch circuits for the kitchen countertop. These circuits must be calculated at

1500 VA each
(3000 VA total). NEC 220.52(B)

Requires a minimum of one 20-ampere laundry branch circuit, calculated at

1500 VA
. NEC 220.52(C)

Requires a minimum of
one 20-ampere bathroom branch circuit, calculated at

1500 VA
. NEC 220.53

Provides a demand factor of

75%
that can be applied to the total of these circuits. Total Kitchen & Laundry & Bathroom Appliance Load = 3000VA + 1500 VA + 1500 VA = 6000 VA Demand Factor for Kitchen & Laundry & Bathroom = 6000 VA .75 = 4500 VA = 4.5 KVA Since this section specifically deals with small appliance branch circuits, you should only include the counter top circuits. Other appliances should be calculated with other general use receptacles. The NEC has special sections for things like ranges, dryers, and AC units that must be used.4. Electric Range/Oven (Part of Kitchen Load)



NEC 220.55

This is
critical. Ranges are calculated differently. You'll use Table 220.55. You need to know the rated power (in kVA) of the range/oven. Let's assume you have a range rated at 12 kW (12 kVA).

Table 220.55, Column C

For a 12 kW range, the demand is

8 kVA
. If your range is between 8.75 kW and 12 kW, use 8 kVA. If it's lower wattage, follow the notes under the table. If it's higher wattage, you can use the notes to adjust the demand. If you have a separate cooktop and oven

Follow the Notes
under Table 220.55. Each is considered separately, but the total demand cannot be less than 8 kVA. This is a tricky area; an engineer will know the nuances.

5. Dryer



NEC 220.54

Dryers are calculated at

5 kVA
(minimum). This demand load should be easy. Demand = 5.0 KVA6. Motors (Fans, Garage Door Opener)



NEC 430.24

Conductors supplying several motors are calculated at 125% of the full-load current rating of the highest rated motor, plus the sum of the full-load current ratings of all other motors in the group.

NEC 430.53(B)

The same principle of 125% of the highest rated motor is applied to the motors.


Since all of your motors are relatively low wattage
, applying this section strictly could be too conservative. Many inspectors will allow you to sum all motor loads and apply a demand factor if there is reason to believe the motors are non-coincidental. We will assume that none of the listed motors are expected to operate simultaneously. Exhaust Fans

You're right, these are often categorized under lighting, but since you've already separated them, let's keep them here.


Total Motor Load = 0.90 KVA
7. Water Heater

This is a continuous load so its load can be calculated directly. Total Water Heater Load =

12.25 KVA
8. Air Conditioning and Heating

You stated the units are non-coincidental, so you only need to account for the larger of the two loads.

NEC 220.60

Provides calculations for non-coincidental loads. Since AC unit (1.3 KVA) < Heating Unit (5.0 KVA), we'll only calculate the heating load. Heating Load =

5.0 KVA
Putting It All Together

Now, let's sum up the demand loads:
Lighting: 4.05 kVA Receptacles: 5.25 kVA Small Appliance Circuits (Kitchen, Laundry, Bath): 4.5 kVA Range: 8.0 kVA (Assumed) Dryer: 5.0 kVA Motors: 0.9 kVA Water Heater: 12.25 kVA Heating: 5.0 kVA

Total Demand Load = 44.95 kVA
Calculating Amperage

Amps = kVA 1000 / Voltage Amps = 44.95 kVA 1000 / 240V Amps = 187.29 Amps

Safety Factor

Add a 20% safety factor: 187.29 Amps 1.2 = 224.75 Amps

Panel Size

You would likely choose a

225 Amp or 250 Amp main panel.
This is subject to engineering judgment and local codes.Important Considerations & Next Steps



Largest Motor

Double-check if any of your motors require special consideration due to size (NEC 430).

Future Expansion

Consider leaving additional capacity in the panel for future additions.


Coordination with Utilities

The power company may have specific requirements for service entrance size and load calculations. Coordinate with them early in the design process.

Engineering Review

This is not a substitute for a licensed electrical engineer's design.* They will perform a detailed load calculation, consider all applicable codes and standards, and provide a stamped and sealed design.

In summary, focus on applying the correct demand factors from NEC 220, especially for lighting, receptacles, small appliance circuits, ranges/ovens, and dryers. Remember to include a safety factor and coordinate with a licensed electrical engineer.