Question: If I connect an old CSED to a new sub panel with a metal raceway (less than 24") and I run feeders to my sub panel and then the branch circuits back from the sub panel in the same raceway is there a need to run my grounded conductors along with my feeder and branch ungrounded conductors, I know 300.3(B) but this scenario is similar to a switch loop whereas the problem of heating through induction should not be an issue, am I correct? Thank you all
You're asking about a scenario where you're using a metal raceway (less than 24 inches) between an old combination service entrance device (CSED) and a new subpanel. You're proposing running both feeders to the subpanel and branch circuits back from the subpanel in the same raceway, and questioning if you must run the grounded (neutral) conductors for both the feeders and branch circuits in that raceway.Here's a breakdown of why you must run the grounded conductors in the raceway, despite the short length and your analogy to a switch loop: 300.3(B): Always Together for Inductive Heating and Impedance This section of the NEC is extremely clear: "All conductors of the same circuit...shall be installed in the same raceway..." The purpose is to minimize inductive reactance and ensure proper impedance. While a short raceway reduces the impact, it doesn't eliminate it. Why it matters: When current flows in a conductor, it creates a magnetic field. In a metallic raceway, this magnetic field can induce currents in the metal, leading to heating, increased impedance, and potential voltage drop, even over short distances. Having the grounded conductor present cancels out much of that magnetic field, minimizing these issues. Circuit Completeness
Every circuit requires a complete path for current to flow. That path includes not only the ungrounded conductors but also the grounded (neutral) conductor to return the current to the source. The subpanel is essentially acting as a new source for the branch circuits.
Ground Fault Current Path
The grounded conductor provides a low-impedance path for fault current to return to the source in the event of a ground fault. This is critical for the proper operation of overcurrent protection devices (breakers or fuses). If the grounded conductor isn't present, the fault current path will be significantly higher impedance, potentially preventing the overcurrent device from tripping quickly enough, creating a serious shock and fire hazard.
Switch Loop Analogy Doesn't Apply
A switch loop is fundamentally different. In a switch loop, you're interrupting the ungrounded conductor to control a load. There is no grounded (neutral) conductor as part of the switch loop itself. The grounded conductor for the light fixture or device controlled by the switch is run directly to the load, not through the switch. In your proposed scenario, you have complete circuits running to and from the subpanel, each of which must have a grounded conductor.
Code is Specific, Not Subjective
The NEC rules regarding conductors in raceways are prescriptive. While you might try to argue that the inductive heating is minimal in your specific case, the Code doesn't allow for that interpretation. The rule is intended to ensure safety and proper operation in all installations, regardless of perceived minimal risk.
In summary: You absolutely must* run the grounded (neutral) conductors for both the feeders and the branch circuits in the same raceway with the ungrounded conductors, even with a short metal raceway. Failing to do so violates 300.3(B) of the NEC and creates a dangerous and non-compliant installation. Flag for review