User: isaldana, Location: Ennis
Asked on: Wednesday, October 2, 2024 at 8:04 pm EDT
Answered on: Thursday, March 6, 2025 at 3:19 am EST
Question: I’m meeting some clarification on article 250.92B… I have 3” parallel raceways leaving a disconnect and feeding a 800 amp panel 200 feet away, Both the disconnect and service panel holes for the raceways were punched out. Is a lockring and plastic bushing enough to meet the bonding requirement of the raceways or is a bonding bushing also needed?
Let's break down 250.92(B) and apply it to your scenario to determine if a bonding bushing is required in addition to the lockring and plastic bushing.
Understanding 250.92(B) - Method of Bonding at Service Equipment
This section of the NEC outlines acceptable methods for ensuring the electrical continuity and effective grounding path of metallic raceways and enclosures used to house service conductors. It focuses on the connection between these components and the grounding electrode conductor (GEC) or the neutral conductor (if used as the grounding electrode). Key requirements include: (1) Bonding Jumpers
Where necessary to ensure the electrical continuity of metal raceways and metal enclosures, bonding jumpers must be used. These jumpers are typically sized according to Table 250.102(C)(1).
(2) Other Methods
Other listed devices, such as bonding bushings, wedges, or hubs, designed for grounding purposes, can be used to achieve electrical continuity and effective grounding.
Analysis of Your Scenario
Here's a breakdown of your specific situation and what 250.92(B) implies:
3" Parallel Raceways
You have multiple large-diameter metallic raceways. This increases the likelihood that simple locknuts and bushings may not provide adequate bonding, especially over a 200-foot distance.
Punched Out Holes
While not explicitly forbidden, punched-out holes are a crucial point. Punched-out holes often create rough edges and inconsistent contact between the raceway and the enclosure. This makes it harder to rely solely on the locknut for a reliable bond.
800 Amp Service
An 800A service implies a potentially high fault current. A robust bonding system is critical for safely handling fault currents.
200-Foot Run
The long distance significantly impacts the impedance of the raceway. A longer raceway run means a higher impedance, reducing the effectiveness of the raceway as a fault current path if not properly bonded. Inductance comes into play at longer distances.
Lockring and Plastic Bushing
A standard locknut and plastic bushing are generally considered not sufficient for bonding, especially in this scenario. A plastic bushing provides insulation and protects the conductors from abrasion, but contributes nothing to the electrical bond. The locknut alone is relied upon for bonding and with punched holes it's typically considered inadequate.
The Verdict: Bonding Bushings (and likely Bonding Jumpers) are Required
In your situation, yes, you most likely need bonding bushings in addition to locknuts and bushings. Here's why: Inadequate Contact
The punched-out holes and the large raceway size make it very difficult to ensure that the standard locknut alone will provide a sufficiently low-impedance path for fault current.
Long Distance/Parallel Raceways
The 200-foot run introduces significant impedance in the fault current path. The longer the path, the more critical it becomes to have low-impedance connections at the entry and exit points.
High Ampacity
The high service current (800 amps) further emphasizes the need for a robust and reliable bonding system.
Specific Requirements for Services
Service raceways are held to a higher standard in the NEC due to the increased potential hazard.
NEC 250.92(B)(4)
Bonding Methods. Bonding shall be accomplished by one of the following:(1) Listed for grounding and bonding(2) Equipped with fittings listed for grounding and bonding(3) Connected with clamps or other fittings identified for grounding and bonding.
Recommendations
Use Bonding Bushings
Install bonding bushings at both ends (the disconnect enclosure and the service panel) of each of the 3" raceways. These provide a dedicated connection point for bonding jumpers. Choose bushings listed for grounding and bonding.2.
Install Bonding Jumpers
Connect a bonding jumper from each bonding bushing to the enclosure's grounding busbar or a suitable grounding point. Size the bonding jumpers according to Table 250.102(C)(1). These jumpers ensure a low-impedance path.
3.
Consider Grounding Locknuts
While bonding bushings are the primary solution, using grounding locknuts (locknuts with a lay-in lug for a bonding conductor) in addition to the bonding bushings can provide an extra measure of safety. However, the bonding bushings are the more important element.4.
Inspect and Clean
Make sure the surfaces where the bonding bushings and locknuts make contact with the enclosures are clean and free of paint or corrosion. This is essential for a good electrical connection.
Important Considerations
Local Amendments
Always check for any local amendments to the NEC that may have stricter requirements for bonding service raceways.
Inspector's Interpretation
The final decision rests with the electrical inspector. Discuss your bonding plan with the inspector beforehand to ensure compliance.
Engineering Analysis: For very large services or complex installations, a professional engineer may be needed to perform a short-circuit analysis and specify the appropriate bonding methods.In summary, in your specific situation with large raceways, punched holes, a long run, and a high-amp service, a lockring and plastic bushing alone* are almost certainly insufficient for proper bonding. You need bonding bushings and bonding jumpers to comply with 250.92(B) and ensure a safe and effective grounding system. Always consult the latest edition of the NEC and local amendments for the most accurate and up-to-date requirements. Flag for review