Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 6 foot limit of liquid tight for hot tub

User: Stevenfyeager, Location: United States, Indiana

Asked on: Wednesday, October 2, 2024 at 8:22 pm EDT
Answered on: Thursday, March 6, 2025 at 3:19 am EST

Question: One electrical inspector some years ago told me that I used more than 6 foot of liquidtight to a hot tub and that is not allowed. He didn't make me change it but, was he right ?

It's tricky, because the NEC (National Electrical Code) has changed over the years, and interpretations can vary. Here's a breakdown of why the inspector might have said that and what the current situation is

Why the inspector MIGHT have been concerned:
Past Code Restrictions

In older versions of the NEC, there were more restrictive rules about the use of flexible conduits, including liquidtight flexible metal conduit (LFMC) and liquidtight flexible nonmetallic conduit (LFNC) for hot tubs. The concern was often related to grounding/bonding and potential for water ingress over longer runs. There may have been a 6-foot limit on flexible conduit runs to limit these issues.


Grounding/Bonding Concerns

Properly grounding and bonding a hot tub is absolutely critical for safety. Longer runs of flexible conduit can potentially introduce higher impedance in the grounding path, which could be a problem.

Suitability for the Environment

While liquidtight conduit is designed to be water-resistant, extremely long runs might be seen as more susceptible to water entering over time, especially if not properly installed with watertight fittings.

What the Current Situation is Likely to Be



Current NEC Requirements

The 2023 NEC (which is the most up-to-date as of October 2024) generally allows more than 6 feet of liquidtight conduit to a hot tub, as long as

all
of the following conditions are met: Proper Grounding/Bonding

The grounding and bonding must be done according to NEC Article 680 (Swimming Pools, Fountains, and Similar Installations). This includes using the correct size grounding conductors and ensuring a low-impedance ground path.


Listed Fittings

Use only liquidtight fittings that are properly listed and rated for the type of conduit you are using (LFMC or LFNC).

Approved Conduit Type

Make sure the conduit type itself is approved for the application (outdoor, wet locations).


Support

The conduit needs to be supported properly at intervals specified by the NEC (typically every 3 feet).

Grounding/Bonding Conductor

The most important part is that the equipment grounding conductor be run
inside the liquidtight conduit. This ensures a reliable ground path regardless of the length.

In other words, the NEC allows for more than 6 feet of liquidtight conduit, but requires a separate insulated or bare equipment grounding conductor inside the conduit.
Important Considerations & Recommendations


Local Codes Override

Always remember that local codes and amendments can be stricter than the NEC. You should always check with
your local electrical inspector or building department to confirm their specific requirements for hot tub wiring.2.

Inspector's Rationale

If the inspector didn't cite a specific code section, it's possible they had a concern about the installation quality or grounding. Ask them specifically what their concern is so you can address it.3.

Documentation

Keep records of your work, including the types of conduit, fittings, and grounding conductors used. This can be helpful for future inspections.4.

Best Practices

Even if the code
allows longer runs, shorter runs are generally better from a practical standpoint (easier to install, fewer potential points of failure). However, sometimes longer runs are necessary for routing.5.

LFMC vs. LFNC

LFMC (liquidtight flexible metal conduit) is generally considered more robust and offers better grounding characteristics than LFNC (liquidtight flexible nonmetallic conduit). If you are using LFNC, ensure it is listed for grounding purposes.6.

Get it in writing from your inspector
Ultimately the best advice I can give you is to speak to your local inspector. They make the final call in your area.

In Conclusion

While the inspector's comment might have reflected older code requirements or a general concern about grounding and water ingress, the current NEC
generally* allows for more than 6 feet of liquidtight conduit to a hot tub if proper grounding and bonding techniques are followed, with the equipment ground inside the conduit. However,

always prioritize local codes and the specific requirements of your local electrical inspector.
If you are unsure, consult a qualified electrician. Flag for review

Previous Question Next Question