User: Deke1069, Location: SC
Asked on: Thursday, October 3, 2024 at 8:03 am EDT
Answered on: Thursday, March 6, 2025 at 3:21 am EST
Question: The area that I work in has numerous houses with sub-panels that are fed with a 3 wire SE cable, two hots and a bare neutral/ground and all the grounds and neutrals are on the same bus bar. The obvious fix is to re-pull a 4 wire SER cable and separate the grounds and neutrals but this is a hard sell. Is it code compliant to just pull an appropriate sized separate ground from the same source as the original SE cable? Or should I pull a separate insulated neutral and use the bare uninsulated conductor in the SE cable as the ground? Also when was the first year that neutrals and grounds needed to be separated added to the code book? Must have been 50's or earlier?
You've hit on a common situation and a tricky one. Let's break it down.
Understanding the Problem 3-Wire SE Cable Issue
The core problem is that in subpanels, the neutral and ground paths must be separate. When they are bonded together at the subpanel, you create a parallel neutral path through the grounding system. This can lead to: Stray current on the grounding system. Nuisance tripping of GFCI breakers. Increased risk of electric shock.
Why It Was Done
Back in the day, it was common (and sometimes acceptable by older codes) to use the neutral as the grounding path in subpanels. This is no longer allowed.
Code Compliance & Solutions1. Best Solution: 4-Wire SER Cable Replacement
This is the only way to be fully compliant with current electrical codes. Pulling a 4-wire (two hots, neutral, and ground) SER cable allows for a properly isolated neutral and ground system at the subpanel. It can be a hard sell because of cost and labor.2.
Alternative 1: Adding a Separate Ground Wire (The Technically Feasible but Potentially Problematic Approach)
Concept
You propose running a separate grounding conductor from the main panel's ground bus to the subpanel's ground bus, while still using the existing bare conductor in the SE cable as the neutral.
Code Considerations
NEC 250.130(C)
Permits the use of the grounding electrode conductor as a grounding conductor for existing branch circuits.
This section is complex and often misinterpreted. It's usually intended for adding a ground to a branch circuit, not for fixing a fundamentally incorrect subpanel wiring configuration. Consult your local electrical inspector for their interpretation.
NEC 250.6(A)
Discusses Objectionable Current. Adding a supplemental ground might reduce objectionable current flowing on the neutral by providing an additional path back to the service equipment. However, it's more likely to increase the current on the grounding system, making the situation worse.
Problems
It does not fully isolate the neutral and ground paths. The neutral in the SE cable still carries current and is bonded to the enclosure. Any current imbalances will flow on the grounding system. Increased risk of objectionable current flowing on the grounding system, creating safety and performance issues. May not be acceptable to an electrical inspector.
Warning
This approach is often not a good solution, and its code compliance is highly debatable. Always consult with your local electrical inspector before attempting this.
If Allowed
If the inspector agrees to this approach, the grounding conductor must be sized according to NEC Table 250.122 based on the overcurrent protective device (breaker) protecting the feeder to the subpanel.
3.
Alternative 2: Using the Bare Conductor as Ground, Adding an Insulated Neutral (Also Problematic)
Concept
You propose using the existing bare conductor in the SE cable solely as the ground and pulling a separate insulated neutral to the subpanel.
Code Compliance
NEC 338.30(B)(2)
Permits using the bare conductor in SE cable for equipment grounding purposes under specific conditions (e.g., where there are no continuous metallic paths between the main panel and the subpanel). This is rarely the case in residential wiring.
Problems
Same issue with objectionable current. Using the bare conductor as the ground might not provide adequate fault current return path, especially for smaller gauge SE cable. Generally a confusing and non-standard approach.
Warning
This is usually not a good solution and is often disallowed by electrical inspectors. Always consult with your local electrical inspector before attempting this.
Important Considerations
Local Electrical Inspector is Key
The most crucial step is to discuss the situation with your local electrical inspector. They have the final say on what is acceptable in your jurisdiction. They may have specific interpretations or local amendments to the NEC.
Documentation
Document your discussions with the inspector, and get written approval if possible.
Safety First
Electrical work is dangerous. If you're not fully qualified and experienced, hire a licensed electrician.
Sell the Correct Solution
Emphasize the safety benefits of proper separation of grounds and neutrals to your customers. Explain the potential problems with the "band-aid" approaches.
When Did Ground/Neutral Separation Become Code?The requirement to separate neutral and ground conductors at subpanels was phased in over time. It became more firmly established in the NEC in the late 1960s and early 1970s with revisions to Article 250. However, the full implementation and widespread understanding of the importance of this separation took time. Prior to that, it was common to bond neutrals and grounds at subpanels, especially in older installations. There was not a single year it switched, but a gradual increase in the emphasis on separation as the codes went through revisions.
In SummaryThe best and safest solution is to replace the 3-wire SE cable with a 4-wire SER cable. While the alternative of adding a separate ground might* be considered by some inspectors under specific circumstances, it's often a problematic and potentially unsafe shortcut. Consult your local electrical inspector before proceeding with any work. Flag for review