Topic: Reuse existing MCC bucket to feed panel

User: bcm, Location: Atlanta, Georgia

Asked on: Thursday, October 3, 2024 at 12:33 pm EDT
Answered on: Thursday, March 6, 2025 at 3:22 am EST

Question: Happy Thursday, my sparky friends!I have been asked to reuse a spare bucket in a 600A, 480V, 3 ph MCC to feed a 200A, 120/240V, 1 ph panelboard. I've never seen an MCC used for anything but serving motors in the past, but I haven't found anything in the NEC that prohibits serving a panelboard. It feels like a gray area code-wise.As far as the design, the MCC is 600A, 480V 3 ph fed by 2 sets of (3) 350 MCM & 1#2 ground. The bucket is a spare from a removed 15 HP AC motor. Can I replace the "guts" (HOA, transformer, etc.) from the bucket with a 100A, 480V fuse or CB? I would then put a step-down transformer downstream which would bring voltage to 120/240 for the loadcenter, and wouldn't it also provide the required neutral?Thanks so much for your input!

Okay, let's break this down. You're right, this is a bit outside the typical MCC application, but that doesn't necessarily make it wrong.

NEC Considerations & Feasibility



Legality

You are correct. The NEC
doesn't explicitly prohibit using an MCC to feed a panelboard. MCCs are essentially enclosed circuit breakers or fused disconnects with additional motor control capabilities. Think of it as a really robust panelboard feeding another panelboard.

Article 408 (Panelboards)

You'll want to ensure your final setup adheres to all applicable requirements of Article 408, especially regarding overcurrent protection and interrupting rating.

Article 430 (Motors, Motor Circuits, and Controllers)

Make sure that you are removing ALL of the motor-related parts of the bucket; the HOA, OL's, everything, and that the bucket is no longer set up as motor control.


Article 240 (Overcurrent Protection)

The overcurrent protection (fuse or breaker) you install in the MCC bucket must be appropriately sized and rated for the downstream transformer and panelboard.

Available Fault Current

This is critical. You
must determine the available fault current at the MCC bus. Then, verify that the interrupting rating of the new overcurrent device (fuse or breaker) and the panelboard are adequate. You might need to consider using current-limiting fuses or a circuit breaker with a high interrupting rating.

Transformer Considerations

You are correct that you will need to supply a neutral for the new loadcenter. A step-down transformer would be a simple way to provide this. Ensure the transformer you choose is sized appropriately for the expected load on the 120/240V panelboard. Also, remember that you need to properly bond the transformer's secondary neutral to ground, per NEC 250.30. Pay attention to the X0 (neutral) connection of the transformer.

Physical Space

Double-check you have enough physical space inside the MCC bucket to accommodate the new overcurrent protection (fuse or CB) and all necessary wiring.

Design Considerations & Suggestions


Overcurrent Protection

A 100A breaker or fuse in the bucket seems reasonable
as a starting point. This size would need to be verified based on the size of the transformer's primary current requirements (calculated based on the panelboard's anticipated load and transformer kVA rating).2.

Transformer Selection



kVA Rating

Accurately estimate the total load the 120/240V panelboard will serve. Add a safety factor (125% is common). This will determine the required kVA rating of the step-down transformer.

Wiring

Size the conductors from the MCC bucket to the transformer and from the transformer to the panelboard per NEC tables, based on the amperage and voltage.


Overcurrent Protection (Transformer)

You'll need to provide overcurrent protection on both the primary and secondary sides of the transformer, according to NEC 450.3. This is crucial for safety and code compliance.
3.


Grounding

As mentioned before, proper grounding of the transformer secondary is critical. This involves creating a neutral-to-ground bond at the transformer and running an equipment grounding conductor (EGC) from the transformer back to the MCC.4.

Coordination

Ensure that the OCPD for the transformer and panelboard are coordinated.

Step-by-Step Process


Load Calculation

Perform a thorough load calculation for the 120/240V panelboard to determine its maximum demand.2.

Transformer Selection

Select a suitable transformer based on the load calculation.3.

Available Fault Current Calculation

Determine the available fault current at the MCC bus.4.

Component Selection

Choose an overcurrent device (fuse or breaker) for the MCC bucket with an adequate interrupting rating. Select overcurrent devices for the transformer primary and secondary sides.5.

Wiring Design

Size all conductors based on the calculated currents and NEC tables.6.

Grounding Design

Plan and implement the grounding system, including the neutral-to-ground bond at the transformer and the equipment grounding conductor.7.

Physical Installation

Install all components in the MCC bucket and make all necessary wiring connections.8.

Testing and Verification

Thoroughly test the entire system to ensure it is functioning correctly and safely.

Important Considerations



MCC Condition

Inspect the spare MCC bucket carefully. Ensure it's in good working order (no corrosion, damaged components, etc.).


Labeling

Clearly label all components and wiring in the MCC bucket and the panelboard.

Documentation

Keep detailed records of all calculations, component specifications, and wiring diagrams.


Engineering Review

If possible, have a qualified electrical engineer review your design to ensure it meets all applicable codes and standards.

In summary, yes, it is possible to use an MCC to feed a panelboard. However, it requires careful planning, design, and execution to ensure safety and code compliance.