Question: Can I bond neutral and ground on the gateway after transformer, the transformer is coming from main switch board where neutral and ground is bonded? Thank you!

No, you absolutely should not bond neutral and ground at the gateway after the transformer if the neutral and ground are already bonded at the main switchboard feeding the transformer.This is a violation of electrical codes (like the NEC in the US) and creates a dangerous situation known as a parallel neutral path. Here's why: Parallel Neutral Path

When you bond neutral and ground in multiple locations, you create alternative paths for neutral current to flow back to the source (the transformer). Some of this current will now flow through the grounding conductor (the safety ground wire), which it is

not designed to carry continuously
.
Overheating and Fire Hazard

The grounding conductor is typically smaller than the neutral conductor. Having neutral current flowing through the grounding conductor can cause it to overheat, potentially melting the insulation and creating a fire hazard.

Shock Hazard

If the grounding conductor becomes energized due to the neutral current flow, any metal enclosure or equipment connected to the ground can become a shock hazard. People touching these grounded parts could receive an electrical shock.


Ground Fault Protection Problems

Ground fault circuit interrupters (GFCIs) and arc fault circuit interrupters (AFCIs) rely on detecting an imbalance between the current flowing through the hot and neutral wires. When neutral current is flowing through the ground wire, it can interfere with the operation of these protective devices, rendering them less effective or even causing nuisance tripping.

The Correct Configuration (assuming US NEC practices)



Single Point Bond

The neutral and grounding conductor should be bonded together

only at one point
in the system – typically at the main service entrance (which in your case seems to be happening at the main switchboard). In your described scenario, this bond is at the main switch board. Separate Conductors

From the main switchboard to the transformer, and then from the transformer to the gateway, the neutral and ground conductors should be kept separate. The transformer itself may have a grounding electrode conductor (ground rod) connected to the transformer case, but the neutral from the transformer should only be bonded to ground at the main switchboard.

In summary

Do not bond neutral and ground at the gateway. Having the bonding done at the main switchboard supplying the transformer is the proper setup.

Important Safety Note:
Electrical work can be dangerous and requires knowledge of electrical codes and safe practices. If you are not a qualified electrician, it is highly recommended to consult with a licensed electrician for any electrical work. They can properly assess the situation and ensure that the installation is safe and compliant with local codes. Flag for review