Topic: System Bonding Jumper table 250.102(C)(1) question

User: reko19, Location: New Jersey

Asked on: Friday, October 4, 2024 at 10:13 am EDT
Answered on: Thursday, March 6, 2025 at 3:24 am EST

Question: Hi everyone. Dealing with 4000kVA transformer and 5000A substation. Transformer is closed coupled to the substation. Looking at table 250.102(C)(1), note 4, " If there are no service-entrance conductors, the supply conductor size shall be determined by the equivalent size of the largest service-entrance conductor required for the load to be served". The substation tie (it is main-tie-rie-main arrangement) is 11 sets of 750KCMIL. Note 1 states" if the ungrounded supply conductors are larger than 1100kcmil copper or 1750 kcmil aluminum, the grounded conductor or bonding jumper shall have an area not less than 12.5% percent of the area of the largest ungrounded supply conductor or equivalent area for parallel supply conductors." Note 3 states "If multiple sets of service-entrance conductors are used as permittedin 230.40, Exception No. 2, or if multiple sets of ungrounded supply conductors are installed for a separately derived system, the equivalent size of the largest ungrounded supply conductor(s) shall be determined by the largest sum of the areas of the corresponding conductors of each set."So do I size my SBJ based on 12.5% of 11x750KCMILORSince each set is 750KCMIL, use cooper 2/O?Thank you.

Okay, let's break down the sizing of your System Bonding Jumper (SBJ) for your 4000kVA transformer and 5000A substation, keeping in mind the closed-coupled arrangement and the NEC references you've cited.

Understanding the Scenario 4000kVA Transformer

Supplying power to a substation.


5000A Substation

You mention a main-tie-main arrangement, indicating redundancy and load sharing capabilities. The "tie" likely refers to the bus tie breaker

Closed-Coupled

This means the transformer is directly connected to the substation's main bus, minimizing conductor length between the transformer and the substation gear.


11 sets of 750 kcmil

This is a significant amount of conductor capacity for the substation ties.

NEC Analysis and Calculation
1. Applying Table 250.102(C)(1) and Notes

You correctly identify Note 4: This applies because you essentially don't have service-entrance conductors in the traditional sense. The transformer is supplying the substation, making it the source for the downstream load.

Equivalent Size

Note 3 becomes crucial. Because you have multiple sets of ungrounded supply conductors (the 11 sets of 750 kcmil), you must consider the total area of the conductors.

Total Area Calculation

11 sets
750 kcmil/set = 8250 kcmil. This is the equivalent size of your largest ungrounded supply conductor(s).

Applying Note 1 (The 12.5% Rule)

Because 8250 kcmil
exceeds 1100 kcmil for copper, you must apply the 12.5% rule.
2.


Calculating the SBJ Size

SBJ Area = 0.125 8250 kcmil = 1031.25 kcmil Since you are working with copper, you will need to select the next higher standard size. Consulting conductor ampacity tables in Chapter 9 of the NEC, we find that a copper conductor with an area greater than 1031.25 kcmil is likely to be

1250kcmil
3. Why the 2/0 is Incorrect

Using 2/0 copper would only be applicable if you were looking at a single 750 kcmil conductor. Because you have 11 sets in parallel, you must account for the total combined capacity.

Therefore, the correct size for your copper System Bonding Jumper (SBJ) is 1250kcmil.
Important Considerations and Best Practices



Material

Ensure the SBJ is copper (as we assumed above). If you are using aluminum, adjust the calculation based on the 1750 kcmil aluminum threshold in Note 1 and use appropriate ampacity tables for aluminum conductors.


Termination

Ensure proper termination of the large SBJ. Use listed and labeled connectors suitable for the conductor size and material. Torque connections to the manufacturer's specifications.

Accessibility

The SBJ must be accessible for inspection and maintenance.


Local Amendments

Always check with your local electrical inspector for any local amendments to the NEC that might affect sizing requirements. Some jurisdictions may have stricter rules.

Engineering Review

Given the size and complexity of this installation, I
strongly recommend having a qualified electrical engineer review these calculations and the overall grounding and bonding design. This helps ensure compliance and safety.

NEC 250.30
Also see 250.30 for SDS bonding jumpers.* Clarify "Closed Coupled" For clarity, when you say closed couple do you mean that the transformer is directly connected to the switchgear busbars?In summary: The size of your SBJ is primarily driven by the total equivalent area of all parallel ungrounded supply conductors. Don't underestimate this calculation, as proper grounding and bonding are essential for safety and equipment protection. Flag for review