Topic: Innerduct - separation of wire classes

User: W@ttson, Location: USA

Asked on: Friday, October 4, 2024 at 10:50 am EDT
Answered on: Thursday, March 6, 2025 at 3:25 am EST

Question: I understand solid ENT can be used to separate wire classes and be deemed a permanent barrier.What about split inner duct? Would you consider that a permanent barrier to separate wire classes inside and enclosure?

Split inner duct is generally not considered a permanent barrier suitable for separating wire classes in an enclosure according to electrical codes and best practices. Here's why: Not Listed or Rated for Separation

Split inner duct is primarily designed for ease of wire pulling and organization within conduit or enclosures. It is not typically listed or rated as a barrier specifically designed to maintain separation of different voltage classes.


Material and Construction

The material of split inner duct (usually plastic) and its split design are not intended to provide the necessary physical barrier and insulation characteristics required to prevent arcing, voltage breakdown, or other hazards associated with mixing different voltage classes.

Enclosure Ratings and Requirements

Electrical enclosures are often rated for specific uses and have requirements regarding internal barriers. Simply placing split inner duct inside an enclosure does not automatically meet those requirements.


Code Compliance

Electrical codes (like the NEC in the US) have very specific rules about separating different voltage classes. Relying on split inner duct for this purpose would likely not meet code.

Permanent Barriers for Wire Class Separation

To achieve a permanent barrier between wire classes, you would typically need to use:

Listed Barriers

Manufacturers make barriers specifically designed for enclosures to separate different voltage sections.


Physical Separation

Physically separate compartments within the enclosure.*

Grounded Metal Barriers

Properly grounded metal partitions within the enclosure can serve as a barrier.

In summary

While split inner duct can help organize wires and make pulling easier, it should

not
be used as a substitute for a properly rated and code-compliant barrier between different voltage classes of wiring in an enclosure. It's important to consult the electrical code, enclosure documentation, and qualified electrician to ensure your wiring installation meets all safety requirements. Flag for review