Topic: Infinite Bus Calculation

User: Brian LeBlanc 913, Location: St Pete Beach, FL

Asked on: Friday, October 4, 2024 at 11:27 am EDT
Answered on: Thursday, March 6, 2025 at 3:25 am EST

Question: Need help with an infinite bus calculation for PEPCO networked utility transformers. We have (2)1000KVA transformers (208V, 3phase secondary) connected to a common bus. I need the fault current at the bus.

Okay, let's break down the infinite bus fault current calculation for your scenario with the PEPCO networked utility transformers. Since you're dealing with utility transformers, the key is getting the right transformer impedance information from PEPCO.

Understanding the Infinite Bus Concept

An "infinite bus" assumes that the source (PEPCO's grid in this case) has virtually zero impedance. This simplifies the fault current calculation because the only impedance limiting the fault current is the transformer impedance.

Steps to Calculate the Fault Current


Obtain Transformer Impedance Data (%Z)



Crucially, contact PEPCO.
They are the only reliable source for the specific impedance data of their transformers and network. Do not guess or assume! Ask for the transformer impedance in percentage impedance (%Z) or per-unit impedance (pu). Specifically request the positive sequence impedance. This is the most important step. Without accurate impedance values, the calculation will be meaningless. Ask for worst-case (highest) impedance. Utilities typically provide the worst-case (highest) impedance to ensure that calculations are conservative and protective devices are properly coordinated. Networked Systems

Networked transformers often have lower impedance than standard transformers. PEPCO might provide a specific network impedance value rather than individual transformer impedances. In many network systems, the transformers are impedance-matched to work in parallel. PEPCO must provide these specifics.2.

Calculate Transformer Impedance in Ohms

If you receive %Z, convert it to ohms using the following formula:
`Z_transformer (ohms) = (%Z / 100) (kV_base^2 / MVA_base)`Where: `%Z` is the percentage impedance (from PEPCO). `kV_base` is the base voltage in kV (0.208 kV in your case). `MVA_base` is the base MVA (1 MVA for a 1000 kVA transformer).

Example (if %Z = 5% - this is an assumption for illustration only)

Z_transformer = (5 / 100)  (0.208^2 / 1) = 0.00216 ohms
This is the impedance per phase. This is very important for 3-phase calculations.3.

Adjust for paralleled Transformers

Since you have two identical transformers in parallel, you need to consider the equivalent impedance.`Z_equivalent = Z_transformer / number of transformers.`In your case, `Z_equivalent = Z_transformer / 2.` Using the prior example with a 5% impedance, `Z_equivalent = 0.00216 ohms / 2 = 0.00108 ohms.`4.

Calculate the Fault Current

`Fault Current (Amps) = V_LL / (√3 Z_equivalent)`Where: `V_LL` is the line-to-line voltage (208V). `Z_equivalent` is the equivalent impedance in ohms (calculated above, adjusted for paralleling). It is very important to include the square root of 3 to get the fault current in amps.

Example (continuing with the assumed 5% impedance)

Fault Current = 208 / (√3  0.00108) = 111,163 Amps
This is the symmetrical fault current.


Therefore, the symmetrical fault current is approximately 111,163 amps.
Important Considerations and Caveats



X/R Ratio

While this calculation gives you the symmetrical fault current, the actual
peak fault current will be higher due to the X/R ratio of the transformer impedance. A higher X/R ratio means a greater DC offset in the fault current waveform, and a higher peak current. PEPCO might provide the X/R ratio along with the impedance. If they don't, a typical assumption for distribution transformers is an X/R ratio of around 5 to 10. You'll need to use a multiplier based on the X/R ratio to estimate the peak fault current. This is often done using software like SKM Power Tools, ETAP, or EasyPower.

Momentary and Interrupting Duty

Protective devices (circuit breakers, fuses) are rated for both momentary and interrupting duty. The momentary duty is the fault current the device must withstand for a short time (usually a few cycles) before clearing the fault. The interrupting duty is the current the device must be able to interrupt. The calculated fault current needs to be compared to both of these ratings.

Network Protectors

Network Protectors are special devices designed to handle fault currents in network systems. PEPCO will have these located in the network transformers to clear faults in the network grid.


Upstream Impedance

In reality, even a utility grid has some impedance, though it's usually very low. The "infinite bus" assumption simplifies the calculation, but it's not perfectly accurate. For more precise calculations, you'd need to know the utility's source impedance at the point of connection, but PEPCO is unlikely to provide it. The fault current at your service will be limited by their source impedance.

Software Tools

Power system analysis software (SKM, ETAP, EasyPower) can perform these calculations much more accurately and can also handle things like the X/R ratio, motor contributions (if any), and protective device coordination.


Coordination Study

The calculated fault current is a key input to a protective device coordination study. This study ensures that your protective devices (circuit breakers, fuses) are properly sized and coordinated to clear faults quickly and selectively, minimizing the impact of faults on your system and the utility grid.

In Summary:


The most important step is getting the transformer impedance data from PEPCO. This calculation is based on that data. Be sure to understand that the 'infinite bus' assumption is the starting point, and other factors can increase or decrease the actual fault current. Flag for review