User: JimmysLimeade, Location: Utah
Asked on: Friday, October 4, 2024 at 4:10 pm EDT
Answered on: Thursday, March 6, 2025 at 3:26 am EST
Question: Hi, I am working on a DC side only design where they want to utilize the CE+T Stability 30C3. They are using 2 of those converters with 120 480W modules. My plan right now is to do 4 strings of 15 modules in series (totals to 804V) and then connect those in parallel (I dont really know the best way to do this so suggestions would be helpful) to hit 45A. Each converter has a maximum input of 1000V and 60A on the DC port which is why I decided to do it that way, but I need to know if I was correct in my reasoning here or if I need to fix it.Another issue I am having is the grounding for this system. I am at a complete loss with this whole grounding document I attached below, it seems like none of the scenarios really fit what I need and I dont know how to properly adapt my system to be grounded correctly. Ive been looking into the negative ground referenced monopole option which would make the most sense to me, but I dont know how to best show that in my diagram.I have been using a document from CE+T to base my initial design on but its somewhat lacking in detail of how to ground.Sorry for all the questions, I just want to make sure I get everything here right.
Okay, let's break down your design and address your concerns, particularly around the DC side configuration and grounding.
DC Side Configuration Analysis
Your initial approach seems reasonable, but let's analyze it in detail: Module Configuration
You're aiming for 4 strings of 15 modules in series. Assuming your modules have a Vmp (Voltage at Maximum Power) around 33.6V (480W / 14.28A), 15 modules in series would give you: 15 33.6V = 504V Vmp per string. Four parallel strings would then theoretically give you 4 \ 14.28A = 57.12A Imp (Current at Maximum Power).
Converter Compatibility
CE+T Stability 30C3: Max input 1000V, 60A. Two Converters: This means your entire array needs to operate within 1000V and the total current needs to be split to be under 60A per converter.
Issues and Adjustments Needed
Voltage
15 modules in series looks good voltage wise; 504Vmp is well below the 1000V limit of the converters.
Current
This is where you have a problem. 4 Strings of 15 Modules would deliver an estimated 57.12A Imp. It is important to verify Voc and Isc on the modules being used because these values will be used for sizing of overcurrent protection devices. The converter has a max input current of 60A which will be exceeded by the two arrays. I would suggest redesigning for 2 strings of 15 modules per converter.
Module Specifications are Crucial
I am estimating the module specs, but this design will live and die based on those specific values.
Parallel Connection and String Combiner Boxes
You're right to consider the best way to connect the parallel strings. Here's the best way to do this and why: String Combiner Box
This is the standard practice for parallel string connections in PV systems. A combiner box performs several critical functions:
Overcurrent Protection
Each string must have a dedicated fuse or circuit breaker within the combiner box. This prevents a fault in one string from causing damage to other strings and the rest of the system. You must use fuses or breakers that are specifically rated for DC PV applications.
Wire Management
Provides a central location to bring all the string wires together neatly.
Disconnect Switch (Optional but Recommended)
Some combiner boxes include a DC-rated disconnect switch, which allows you to safely isolate the PV array for maintenance or in an emergency.
Surge Protection (Optional but Recommended)
A surge protection device (SPD) protects the system from voltage surges caused by lightning or other events.
Monitoring (Optional)
Some combiner boxes have the ability to be monitored to ensure that each string is performing as expected.
Revised Recommendation for DC Configuration
Considering the limits of the CE+T converters, especially the current limit, here's a revised recommendation for a safer design: Two Strings of 15 Modules per Converter
Connect 2 strings of 15 modules in series. Voltage: 504Vmp per string (2 15 33.6V), which is well within the 1000V limit. Current: 28.56A per string (2 14.28A), which is within the 60A limit.
Grounding Considerations (The Tricky Part!)
Grounding is critical for safety and performance. You need to follow the guidance of the CE+T document, and the applicable electrical codes (NEC in the US, or equivalent in your location). Here's how to approach it:1. Understand the CE+T Document
Let's assume the document provides these options (I'm summarizing based on common PV grounding practices):
Ungrounded
Neither the positive nor negative conductor is intentionally connected to ground. Requires insulation monitoring. Generally NOT recommended for residential or commercial grid-tie PV systems.
Negative-Grounded
The negative (-) conductor of the PV array is intentionally connected to ground.
Positive-Grounded
The positive (+) conductor of the PV array is intentionally connected to ground. Less common.
Functional Grounding/Equipment Grounding
Grounding the metal frames of the modules, the racking system, and the enclosure of the inverter/converter to earth ground. This is ALWAYS required, regardless of the array's grounding scheme.2.
Choosing the Right Grounding Scheme
Negative Ground Referenced Monopole
This option (Negative-Grounded) is most commonly used in residential and commercial grid-tie PV systems. Some transformerless inverters REQUIRE negative grounding. If the CE+T documentation and the converters themselves allow or recommend it, this is a good choice.3.
Implementing Negative Grounding
Grounding Electrode Conductor (GEC)
Run a Grounding Electrode Conductor (GEC) from the negative terminal of the array to the main grounding electrode system (earth ground). The size of this conductor is determined by the electrical code (NEC in the US).
Equipment Grounding Conductor (EGC)
Connect all the metal frames of the PV modules, the racking system, and the metal enclosure of the string combiner box and the CE+T converters to earth ground. This is typically done with a green or bare copper wire. Again, size is determined by the electrical code.
Grounding Busbar in Combiner Box
The combiner box will have a grounding busbar where you connect all the equipment grounding conductors and the GEC.
Grounding at the Converter
The CE+T converter will have a designated grounding terminal. Connect the EGC from the converter enclosure to the main grounding system.4.
Documenting Your Grounding
One-Line Diagram
Your one-line diagram must clearly show the grounding connections. Here's how to represent it for a Negative-Grounded system: Draw the PV array as a voltage source. Add a ground symbol to the negative terminal of the voltage source. This indicates that the negative conductor is intentionally connected to ground. Draw equipment grounding conductors connecting the module frames, racking, combiner box enclosure, and converter enclosure to earth ground. Label all grounding conductors with their size and type (e.g., "8 AWG Cu GEC").5.
Important Cautions
Consult a Qualified Electrician
Grounding is a critical safety aspect. If you're not a qualified electrician with experience in PV systems, do not attempt to do this yourself. Hire a professional.
Follow Electrical Codes
The NEC (National Electrical Code) in the US, or the applicable electrical code in your region, has specific requirements for PV system grounding. Adhere to these codes strictly.
Inverter Compatibility
Double-check the CE+T converter documentation to ensure that negative grounding is permitted or recommended. Some inverters are not compatible with certain grounding schemes.
Ground Fault Protection
Ensure that the CE+T converters have built-in ground fault protection (GFP). If not, you may need to add an external GFP device.
Next Steps
Confirm Module Specifications
Get the exact Vmp, Imp, Voc, and Isc of the PV modules you plan to use. This is critical for accurate calculations.2.
Finalize DC Configuration
Based on the module specifications, finalize your DC configuration to ensure you stay within the voltage and current limits of the converters.3.
Choose a Grounding Scheme
Review the CE+T documentation and the electrical code, and decide on the appropriate grounding scheme for your system. Negative grounding is often the preferred choice for many transformerless grid-tie inverters.4.
Design the Grounding System
Lay out the grounding connections in detail, including the size and type of grounding conductors.5.
Consult a Qualified Electrician
Have a qualified electrician review your design and perform the actual installation of the PV system.6.
One-Line Diagram: Create a detailed one-line diagram that clearly shows all DC and AC connections, overcurrent protection devices, and grounding connections.This is a complex topic, and it's important to get it right. Take your time, do your research, and consult with qualified professionals. Good luck! Flag for review