Question: 2020 NEC. If you have a meter on the outside of the dwelling with an EM disconnect (Not Service Equipment) and a panel (service disconnect) on the inside where must the IBT be located? The FiOS ONT which needs to be connected to the IBT is located next to the panel. I say either location inside or outside is compliant. A fellow electrician told me that the inspector says it needs to be outside next to the meter even if the equipment connecting to it is inside.250.94(A) The Intersystem Bonding Termination Device.An intersystem bonding termination (IBT) for connecting intersystem bonding conductors shall be provided external to enclosures at the service equipment or metering equipment enclosure and at the disconnecting means for any additional buildings or structures. If an IBT is used, it shall comply with the following:
You've hit on a common point of confusion with the 2020 NEC regarding Intersystem Bonding Terminations (IBTs). Let's break it down
Understanding the Code Language:
250.94(A)
This section mandates an IBT external to enclosures at the service equipment or metering equipment enclosure
AND at the disconnecting means for additional buildings/structures. The key phrase is "service equipment or metering equipment enclosure." Your Situation
Meter on the outside with an EM disconnect (not service equipment). Panel inside with a service disconnect. FiOS ONT is located next to the panel
Analysis
Meter Location (Outside)
While you have a meter enclosure outside, the code explicitly states that the IBT must be at the service equipment enclosure or the metering enclosure. The outside disconnect is EM disconnect, which may not be considered a disconnect as the code defines it.2.
Service Disconnect Panel (Inside)
This is the location of your service equipment. Since the service disconnect is inside, that is where the IBT should be located.
Conclusion
Your initial assessment is correct: either location would be compliant
as long as there is an IBT at the service equipmentWhy the Inspector Might be Requiring Outside (and why that might be incorrect)
Misinterpretation
The inspector may be overly focused on the meter being the primary point of connection and assuming the EM disconnect meets the requirement of the IBT being located there.
Local Amendments
It's possible that your jurisdiction has a local amendment to the NEC that specifically requires the IBT to be located at the meter, regardless of the location of the service disconnect. This would override the standard NEC.
How to Resolve the Issue
Politely Refer to the Code
Discuss 250.94(A) with the inspector, emphasizing that the service equipment is the key.
2.
Ask for Clarification
Inquire if there's a local amendment to the NEC in your jurisdiction. Request a copy of the amendment if it exists.3.
Appeal the Decision (If Necessary)
If the inspector insists based on a misinterpretation and there's no local amendment, you may need to go through the formal appeals process for your jurisdiction.
Important Considerations
Accessibility
The IBT must be accessible.
Bonding Conductor Size
Ensure the bonding conductor connecting the IBT to the communications system is sized according to 250.94(B).
Manufacturer Instructions
Always follow the manufacturer's instructions for the IBT and the equipment you're bonding to it.
In summary, based on the 2020 NEC as written, the IBT should be located inside at the service equipment. However, always confirm whether there are local amendments that supersede the standard NEC requirements. Flag for review