User: Stevenfyeager, Location: United States, Indiana
Asked on: Saturday, October 5, 2024 at 4:36 pm EDT
Answered on: Thursday, March 6, 2025 at 3:28 am EST
Question: I only see USE in the ampacity table. Is SER rated the same ampacity rating as USE ? Mnf says I have to install a 70 amp sub panel for 2 infratech heaters rated 25 amps each. NEC has #4 USE aluminum for 75 amps. Is SER the same rating? I realize it will not be used for service entrance, that makes it rate less? Is the NEC #4 rated for 75 amps only if used for service entrance? Thank you!
Okay, let's break down the ampacity ratings for USE and SER cable, and address your specific situation with the Infratech heaters.1. USE vs. SER Ampacity and NEC 310.15 USE (Underground Service Entrance Cable)
USE cable is designed for direct burial or installation in wet locations. It's typically insulated with a moisture-resistant material like cross-linked polyethylene (XLPE).
SER (Service Entrance Cable, Type R)
SER cable is primarily used for above-ground service entrance wiring. It has a flame-retardant covering.
Ampacity Ratings are NOT Identical
While both are service entrance cables, their ampacity ratings can differ slightly.
Crucially, you cannot assume they have the same ampacity. The specific insulation type and construction of the cable determine its ampacity. NEC 310.15 and Ampacity Tables
The NEC (National Electrical Code) provides ampacity tables (specifically Table 310.15(B)(16)) that list the allowable ampacities of various conductors based on their insulation type, ambient temperature, and installation method.
You MUST consult this table to determine the correct ampacity for the specific type and size of conductor you are using. 75°C vs. 60°C and Termination Temperature Limits
This is a critical point. Most breakers, switches, and equipment are only rated for 75°C termination temperatures. You can use a conductor with a 90°C insulation, but you must use the 75°C column from the ampacity table. If the equipment is rated 60°C, you use the 60°C column in the table.
2. Your Specific Infratech Heater Situation Heater Load Calculation
You have two Infratech heaters, each drawing 25 amps. Total load = 2 heaters 25 amps/heater = 50 amps.
Continuous Load
Electric heaters are considered a continuous load if they operate for 3 hours or more. The NEC requires you to size the conductor and overcurrent protection (circuit breaker) at 125% of the continuous load. 50 amps 1.25 = 62.5 amps (minimum conductor ampacity and breaker size).
Manufacturer's Recommendation
The manufacturer recommends a 70-amp subpanel. This recommendation is likely based on: Allowing for future expansion of the heating system. Ensuring adequate headroom for voltage drop. Their own safety margin considerations.
Aluminum vs. Copper
Aluminum conductors have a lower ampacity than copper conductors for the same size.
3. Analyzing Your Cable Choice and NEC Requirements #4 Aluminum USE
You mention #4 aluminum USE with a 75-amp rating from NEC 310.15(B)(16).
HOWEVER, this is likely only accurate if the terminations are rated to handle 75°C. If you are using the 60°C column the #4 is only good for 60 amps. SER Ampacity
You need to consult the ampacity table (NEC 310.15(B)(16)) for the specific insulation type of your SER cable. SER cable insulation types can vary. Look on the cable jacket. It will say something like "Type XHHW-2" or "Type THHN." Then, find that insulation type in the table.
Service Entrance vs. Feeder
You are correct that the ampacity of a cable can be different depending on if it is a service entrance. NEC Article 310.15(B)(7) is where this allowance is found, but it only applies to service conductors (the wires from the utility company to your main panel) and it is only applied to the entire load. It does not apply to feeders to a subpanel.
Non-Service Entrance
Since your cable is going to a subpanel (not the main service entrance), you cannot use the ampacity rules specifically for service entrance conductors in 310.15(B)(7) (the one that often allows you to use a smaller conductor). You MUST use the standard ampacity tables based on the conductor's insulation type and temperature rating, along with the terminal ratings of all the devices.
4. Recommended Steps1. Identify the Insulation Type of Your SER Cable
Look carefully at the markings printed on the cable jacket. Find the insulation type (e.g., THHN, XHHW-2).2.
Consult NEC Table 310.15(B)(16)
Find the ampacity for that insulation type, conductor size (#4 aluminum), and temperature rating (60°C, 75°C, or 90°C).
Use the 60°C or 75°C ampacity columns, depending on the temperature rating of your breaker and subpanel terminals.3. Verify Termination Temperature Limits
Make absolutely sure your breakers, subpanel, and heaters are rated for at least 75°C. If they are only rated for 60°C, you MUST use the 60°C ampacity from the table.4.
Calculate the Load Properly
Account for the continuous load and size the conductor and overcurrent protection at 125% of the continuous load.5.
Consider Voltage Drop
Long runs of cable can experience significant voltage drop, which can affect the performance and lifespan of your heaters. Use a voltage drop calculator to ensure the voltage at the heaters remains within acceptable limits. (This is likely why the manufacturer recommended 70 amp).6.
When in doubt, follow the manufacturer's recommendations
The Infratech manufacturer's recommendation for a 70-amp subpanel is based on their understanding of the heaters' electrical requirements, safety considerations, and likely includes a safety margin.7.
Get it inspected
Permits and inspection can save lives!
Example Scenario
Let's say your SER cable is marked "Type XHHW-2 Aluminum." You consult NEC Table 310.15(B)(16). If your terminations are rated 75°C: A #4 Aluminum XHHW-2 conductor may have an ampacity of 75 amps.* If your terminations are rated 60°C: A #4 Aluminum XHHW-2 conductor would only be rated for 60 amps.Since you need at least 62.5 amps (for the continuous load), if your terminations are 60°C you would need to go to a #2, which is good for 75 amps.
In conclusion: It's crucial to base your conductor size and overcurrent protection on the specific insulation type of your cable, the termination temperature limits of your equipment, and the continuous load calculation. When in doubt, consult with a qualified electrician to ensure your installation meets all NEC requirements and is safe. Flag for review