User: TwistLock, Location: California
Asked on: Sunday, October 6, 2024 at 10:49 am EDT
Answered on: Thursday, March 6, 2025 at 3:29 am EST
Question: I typically see SER with bare ground. In photo below the ground is insulated. Since this place was built in the ’70’s I’m just curious if there was NM available in #2 AL and or a distinction between SER back then - and if it even matters for the 83% rule, formerly 310.15(b), for a feeder from a meter-main.I.e. if this were #2 AL NM (not listed as SER) would I still be allowed to protect it with a 100a breaker at meter-main or is it just a stepchild at 60C ? *(can't see any markings on jacket with what is visible at either end).
Okay, let's break down this situation and address your questions about the wire in the photo.
Assumptions Based on the Photo and Description You're looking at a multi-conductor cable, likely aluminum, that you believe is feeding from a meter-main to a subpanel or other load. The cable is installed in an insulated wall cavity. The installation is in a structure built in the 1970s. You can't see any markings on the jacket of the cable.
Answering Your Questions1. NM Cable in #2 Aluminum in the 1970s
Availability
While copper was the dominant material for NM cable, aluminum NM cable was available in the 1970s. It wasn't as common as copper, and it had its challenges (which led to some changes in later code cycles).
Jacket
Back in the 70s, it was not at all uncommon to not list temp ratings on NM and SE type cable.
Reliability
This wire would most likely be considered problematic these days because of the propensity for the connections to go bad and cause fires.2.
Distinction between SER in the 1970s
SER Definition
The definition of Service Entrance Cable, Type R (SER) has been fairly consistent over the years. It's always been intended for use as service entrance conductors or as feeders. SER typically does have a bare ground conductor, but that is not what defines it. SER typically had a white or grey jacket and was more rugged than NM.
Bare Ground
SER typically has a bare ground conductor.3.
The 83% Rule and the 60°C Column The 83% Rule (formerly 310.15(B)(7) - Now 310.12)
The residential 83% rule applies to the entire feeder
ampacity, which in turn allows the use of a smaller service entrance conductors than the total calculated load. This rule only applies to feeders or services for dwelling units. It is a limited exception to the typical load calculations and conductor sizing. Ampacity of Aluminum NM
The big issue is determining the ampacity of this #2 aluminum cable. If it were determined to be NM, it would likely be rated for 60°C (133F). However, the cable may be able to be up-rated if the terminations are rated for 75 degrees C.
Protecting with a 100A Breaker
A #2 aluminum conductor, if rated at 60°C, typically has an ampacity of around 75 amps (check the NEC table for the exact ampacity based on the insulation type). Therefore, protecting it with a 100 amp breaker would
violate the code (overcurrent protection exceeding conductor ampacity).4. "Stepchild" Status: NM Cable and Overcurrent Protection "Stepchild" Status
This refers to the fact that NM cable, due to its construction and typical 60°C rating, is often the weak link in an electrical system. It is limited by its temperature rating and the smaller ampacity that results.
Overcurrent Protection is Paramount
Regardless of whether it's NM or SER, the overcurrent protection must never exceed the ampacity of the conductor.
What To Do Next1. Identify the Cable
Very Important
Try your best to identify any markings. You may need to carefully pull the cable further out at either end (service/subpanel) to expose more of the jacket. Use a flashlight and magnifying glass. The markings are essential for determining the cable type and temperature rating.
Consider an Electrical Inspection
If you are unable to identify the cable and ampacity on your own, a qualified electrician should inspect it. They can use their experience and tools to make a determination.2.
Determine Ampacity
Once you know the cable type (NM, SER, etc.) and insulation type, consult the NEC ampacity tables (specifically those for the cable's temperature rating) to determine the appropriate ampacity for #2 aluminum.
Termination Ratings
Confirm the temperature rating of the terminals at both ends of the cable. If the terminals are rated for 75°C or higher, you might be able to use the 75°C ampacity, only if the cable insulation is also rated for 75°C or higher.3.
Verify Overcurrent Protection
Ensure that the breaker protecting the cable is sized appropriately, not exceeding the ampacity of the cable. If the breaker is too large, it
must be replaced with a smaller one to protect the cable from overheating and potential fire hazards.
In Summary While aluminum NM cable existed in the 1970s, its temperature rating limits its ampacity. Overcurrent protection must always be sized based on the conductor's ampacity, as per the NEC. Protecting that cable with a 100A breaker would be wrong. Without knowing the cable's markings, temperature rating, and confirming the termination temperature ratings, it's impossible to provide a definitive answer. A proper inspection by a qualified electrician is highly recommended for safety.* In general it is very rare to see NM feeding from the main panel to a sub-panel. It is typically SER or feeder cable.
Disclaimer: I am an AI chatbot and cannot provide electrical advice. This information is for general knowledge and educational purposes only. Always consult with a qualified and licensed electrician for any electrical work. Incorrect electrical work can be dangerous and potentially deadly. Flag for review