Topic: Aluminum branch circuit conductors for EVSE

User: nizak, Location: Henrico County, VA

Asked on: Monday, October 7, 2024 at 2:26 pm EDT
Answered on: Thursday, March 6, 2025 at 3:31 am EST

Question: Would like opinions on the following proposed install.Planning on installing 60’ #1 SE aluminum cable. It will run from the load center to a j box and then transition to #3 copper and run 35’ to a disconnect mounted at the equipment.This circuit will feed a 80 amp level 2 and will be protected with a 100A breaker.Thanks

Okay, let's break down this proposed EV charger installation and get some opinions and recommendations. I'll focus on code compliance (primarily NEC), best practices, and overall safety and efficiency.

Here's a breakdown of the key elements and my thoughts



60' #1 SE Aluminum Cable (from Load Center to J-Box)



Adequacy

#1 Aluminum SE cable is rated for approximately 100A at 75°C ampacity (check your specific cable for the correct rating). This is marginal for a 100A breaker, but it's technically allowable.

NEC Considerations



310.15(B)(16)

This table is the core of ampacity ratings. Confirm the exact cable type and temperature rating. Crucially, the termination points (breaker, J-Box, etc.) must be rated for the temperature rating you are using (usually 75°C). If the terminations are only rated for 60°C, you must use the 60°C column. This could require increasing the cable size.

220.100/220.100(B)

The feeder is sized to have sufficient capacity to carry the load. The charger load is considered continuous, thus requiring 125% of the continuous load. 80A x 1.25 = 100A, further reinforcing this is marginal at best.


310.15(B)(3)(a)

If this run of cable is subject to bundling or being run in conduit with other conductors, derating for conduit fill and ambient temperature must be considered. This could further lower your usable ampacity.

J-Box Transition



Required

A J-box is necessary for transitioning from Aluminum to Copper conductors.

Connectors

Crucially, you must use connectors specifically rated for Aluminum to Copper connections and rated for the size of conductors. These are often marked with "AL-CU" or similar. Oxidation is a major issue when connecting aluminum and copper. Using the correct connectors prevents corrosion and connection failure.

Box Size

Ensure the J-box is sized correctly to handle the number and size of conductors entering and exiting. See NEC Article 314.

35' #3 Copper Cable (J-Box to Disconnect)



Adequacy

#3 Copper is typically rated for 100A at 75°C.

NEC Considerations

Same as above for terminations and derating.


Flexibility

Consider using THHN/THWN conductors run in conduit. This allows future upgrades.

Disconnect at Equipment



Required

A disconnect is almost always required near the EV charger for service and safety. Local codes may dictate the type of disconnect required (e.g., readily accessible, lockable).

Rating

The disconnect must be rated for at least 100A and suitable for the voltage.


100A Breaker Protection



Size

Since the charger is 80 amps this is correct, as 80 amps x 125% = 100 amps.


Type

Use the breaker type recommended by the panel manufacturer.

GFCI/AFCI

Check local codes and the EV charger manufacturer's requirements regarding GFCI (Ground Fault Circuit Interrupter) and AFCI (Arc Fault Circuit Interrupter) protection. Some jurisdictions
require GFCI protection, and some EV chargers may have built-in GFCI that may require a different type of breaker.

Concerns and Recommendations


Marginal Ampacity

The #1 Aluminum SE cable's ampacity is
very close to the required 100A. Any derating due to conduit fill, bundling, or high ambient temperatures could push it below the required level.

I strongly recommend upgrading the #1 Aluminum to #1/0 Aluminum SE cable.
This gives you a comfortable safety margin and allows for future upgrades.2. Aluminum-Copper Connection

Critical. Use

only
connectors specifically rated for Aluminum to Copper connections and are sized correctly for your conductors. Apply anti-oxidant compound ("Noalox" or similar) to the aluminum conductors before connecting them. Torque the connection to the manufacturer's specifications.3. Temperature Rating of Terminations

Double-check the temperature rating of
all termination points (breaker, J-box terminals, disconnect terminals, charger terminals). If any are only rated for 60°C, you must use the 60°C ampacity column, which will almost certainly require larger conductors.4.

Voltage Drop

Calculate the voltage drop for the entire run (aluminum + copper). Excessive voltage drop can damage the EV charger and increase charging time. Keep voltage drop below 3%. Online voltage drop calculators are readily available. The longer runs of wire are often the main issue with voltage drop, so if voltage drop is a problem, consider shortening the runs of wire.5.

Conduit vs. SE Cable

While SE cable is cheaper, consider using individual THHN/THWN conductors in conduit for the entire run. This offers better protection, easier future upgrades, and easier pulling.6.

Local Codes and Permits

Absolutely essential. Check with your local building department and electrical inspector. They may have specific requirements beyond the NEC, and you will need a permit for this type of work.7.

Professional Installation

Unless you are a qualified electrician, I strongly recommend hiring a licensed electrician to perform this installation. Electrical work can be dangerous, and improper installation can lead to fire hazards and other serious problems.

In summary



Upgrade the #1 Aluminum SE cable to #1/0 Aluminum SE cable.
Use only AL-CU connectors in the J-box and torque them properly. Verify the temperature rating of all terminations. Calculate voltage drop and ensure it's within acceptable limits. Check local codes and obtain a permit.* Consider hiring a qualified electrician.

By addressing these points, you'll ensure a safe, reliable, and code-compliant EV charger installation. Flag for review