Topic: PV AC COMBINER WITH LOAD

User: Zyb, Location: Maine

Asked on: Monday, October 7, 2024 at 7:36 pm EDT
Answered on: Thursday, March 6, 2025 at 3:33 am EST

Question: Hi,just want to ask if the 200A MLO load center is code compliant? does anyone knows if the pv load center is exclusively for pv breaker only? and what chapter/section does the label "solar source only" refer to NEC? Thank you!

Okay, let's break down your questions regarding a 200A MLO (Main Lug Only) load center in the context of solar PV systems and NEC compliance.1. Is a 200A MLO Load Center Code Compliant? Yes, generally, a 200A MLO load center can be code compliant. However, it's not a simple yes/no answer. Compliance depends heavily on how it's being used, the specific installation details, and compliance with relevant NEC articles, particularly Article 705 (Interconnected Electric Power Production Sources). MLO vs. Main Breaker

The key difference between an MLO panel and a main breaker panel is that an MLO panel does not have a main overcurrent protection device (circuit breaker) built into the panel itself. It relies on an upstream breaker (usually in another panel) for overcurrent protection.

Overcurrent Protection

The upstream breaker protecting the MLO load center must be sized appropriately for the panel's ampacity and the loads connected to it.

2. Is a "PV Load Center" Exclusively for PV Breakers?
No, not necessarily. A load center marketed as a "PV load center" is typically designed with features suited for solar PV installations, but it's not restricted to only PV breakers. Common features of PV Load Centers



More Space

Often have more physical space inside the enclosure for managing the numerous conductors involved in PV systems.

Busbar Configuration

May be designed to more easily accommodate backfeeding breakers (solar inverters feed power back into the panel).


Dedicated Bonding

Often have robust grounding and bonding provisions required for PV systems.

Neutral

Ensure you have a robust neutral connection.


Flexibility

You can use a PV load center for general-purpose circuits in addition to the solar PV breakers, provided you follow all applicable NEC requirements for conductor sizing, overcurrent protection, labeling, etc. The panel's rating must be sufficient for all loads connected.

3. "Solar Source Only" Label and NEC Reference
NEC Article 690 (Solar Photovoltaic (PV) Systems)



690.56(B)
is the main section that discusses warning labels for PV systems. It requires labels at various locations, including: PV System Disconnects

Required to clearly indicate the disconnect is for the PV system.


Point of Connection to the Utility Grid

To warn personnel that the system is interconnected with the utility.

Equipment Containing PV System Components

To warn about the presence of PV power sources.


Purpose of the Label

The "Solar Source Only" label indicates that all of the circuits within that specific load center originate from the solar PV system. This is a critical safety warning for anyone working on the electrical system. They need to be aware that even when the main grid power is disconnected, there may still be voltage present from the PV array.

NEC Implications for MLO and PV Interconnection


The NEC places restrictions on how much power you can backfeed into a load center from sources like solar PV. The key concepts are: 120% Rule (NEC 705.12(B)(2)(3)(b))

This is the most important rule in this case. It dictates how much backfeed current is allowed into a load center based on the busbar ampacity.
The sum of the overcurrent devices supplying power to a busbar section shall not exceed 120 percent of the rating of the busbar.

Example

With a 200A MLO panel, assuming it is connected to a 200A breaker in the main service panel. The total of all breakers feeding this panel, including the upstream breaker AND the PV breaker(s), must not exceed 240A (200A x 1.2 = 240A). If the upstream breaker is 200A, then the PV breaker(s) can not exceed 40A(240A-200A=40A).


100% Rule (NEC 705.12(B)(2)(3)(a))

The sum of the overcurrent devices supplying power to a busbar section shall not exceed the rating of the busbar.

Example

With a 200A MLO panel, the total of all breakers feeding this panel, including the upstream breaker, must not exceed 200A. If the upstream breaker is 200A, then the PV breaker(s) can not exceed 0A.

This can be permitted only under engineering supervision by a qualified person
Important Considerations and Best Practices1. AHJ (Authority Having Jurisdiction)

Always consult with your local electrical inspector (AHJ)
before starting any solar PV installation. They have the final say on what is compliant in your specific area, and they may have local amendments to the NEC.2.

Qualified Installer

Use a licensed and experienced electrical contractor with specific expertise in solar PV systems. They will be familiar with the NEC requirements and best practices.3.

Proper Labeling

Ensure that all required labels are installed correctly and are clearly visible.4.

Documentation

Keep detailed records of the system design, component specifications, and all inspections.5.

Single Line Diagram
It is crucial to have a single line diagram as required for the permit.6. Load Calculation: A full load calculation is always recommended before interconnection7. Series Rating: Ensure all breakers have a series rating which can handle the available fault current.

In summary:

A 200A MLO load center
can* be used in a solar PV system, but the installation must be carefully planned and executed to comply with the NEC, especially Article 705, as well as all relevant equipment listing and labeling requirements. The "Solar Source Only" label is a safety warning indicating that all circuits in that panel are powered by the PV system. Proper sizing of breakers, understanding the 120% rule, and consulting with your local AHJ are crucial for a safe and code-compliant installation. Flag for review