Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: High leg delta and corner grounded delta

User: The electron man, Location: Nyc

Asked on: Monday, October 7, 2024 at 8:54 pm EDT
Answered on: Thursday, March 6, 2025 at 3:33 am EST

Question: When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??

No, there isn't a single, specialized transformer wired internally specifically for high-leg delta or corner-grounded delta systems in the sense that you order a transformer pre-configured for only that. You use standard distribution transformers, but how they are connected on the outside determines whether you get a high-leg delta or a corner-grounded delta.Here's the breakdown: Standard Distribution Transformers

The heart of the system is usually a standard three-phase transformer, often with a delta primary (for connection to the distribution system) and a delta or wye secondary. Sometimes it's three single-phase transformers connected externally. The secondary is what we manipulate to create the desired system.


High-Leg Delta (aka Wild-Leg Delta, Red-Leg Delta)



How it's created

One phase winding of the delta secondary is center-tapped. This center tap is then grounded.


The Result

This grounding creates two 120V legs (relative to ground) and one "high leg" (usually around 208V) relative to ground. The voltage phase-to-phase remains balanced.

Transformer Wiring

The transformer itself isn't special inside. It's the external connection of the center tap to ground that makes it a high-leg delta. Any three-phase transformer with a delta secondary (or three single-phase transformers configured as a delta)
can be connected as a high-leg delta by grounding the midpoint of one of the windings.

Corner-Grounded Delta



How it's created

One of the
corners (phase conductors) of the delta secondary is grounded.

The Result

One phase is directly at ground potential (0V). The other two phases are at the full phase-to-phase voltage (e.g., 240V or 480V) relative to ground.

Transformer Wiring

Again, the transformer
inside is a standard three-phase delta secondary transformer (or three single-phase transformers configured as a delta). It's the external connection of one of the corners to ground that defines it as corner-grounded.

Key Takeaways



External Connections Matter

The type of delta system (high-leg or corner-grounded) is determined by the external connections and grounding scheme, not by special internal transformer wiring.

Standard Transformers

Use standard three-phase transformers (or three single-phase transformers).


Understanding Connections

The crucial part is understanding where and how to ground the secondary delta winding.

Why not pre-wired?
Flexibility

Pre-wiring for a specific grounding scheme would greatly limit the transformer's application. Using standard transformers and then connecting them externally allows for much greater flexibility in system design.


Inventory

It would be a logistical nightmare to stock specialized transformers for every possible grounding configuration.

Cost:
Specialized manufacturing would likely increase the cost.In summary, you don't buy a "high-leg delta transformer" or a "corner-grounded delta transformer." You buy a standard three-phase transformer with a delta secondary (or three single-phase transformers), and then you connect it externally* according to the desired grounding configuration. Flag for review

Previous Question Next Question