Topic: BDA bonding?

User: JJWalecka, Location: New England

Asked on: Tuesday, October 8, 2024 at 6:28 am EDT
Answered on: Thursday, March 6, 2025 at 3:34 am EST

Question: Good morning. I have to run a number 6 insulated ground thhn from the BDA to main building ground...Does the conductor need to be in a raceway? Can I run it free air supporting it with 3/8 mc straps and tie wrapping it to EMT pipes? Or does it require a raceway?Appreciate your time

Good morning! Let's break down the requirements for running a #6 insulated ground (likely a Grounding Electrode Conductor or a Bonding Jumper) between your BDA (Bi-Directional Amplifier) and the main building ground.

Here's the general approach, with references to the NEC (National Electrical Code), which is the standard in the US


Identification of the Conductor Purpose

First determine the exact purpose of the conductor. Common purposes include:

Grounding Electrode Conductor (GEC)

Connects the grounding electrode (e.g., ground rod, water pipe) to the building's main grounding busbar or neutral bus. This establishes the connection to earth.


Bonding Jumper

Connects different metallic parts together to ensure electrical continuity and a low-impedance path for fault currents. This might be used to bond the BDA's metal enclosure to the building's grounding system.2.

Protection Requirements for Grounding Electrode Conductors (GECs)
NEC Article 250.64(B) addresses the protection requirements of grounding electrode conductors 250.64(B)(1) states that "Grounding electrode conductors shall be installed in one of the following: (1) Rigid metal conduit. (2) Intermediate metal conduit. (3) Rigid nonmetallic conduit. (4) Electrical metallic tubing. (5) Cable tray, where identified for the purpose. (6) Cable armor. (7) Cable interlock armor. (8) Cable sheath of mineral-insulated metal-sheathed cable. (9) Busways. (10) Other raceways specifically listed for the purpose. Exception to 250.64(B)

A #6 or larger grounding electrode conductor isn't required to be in a raceway if it's "securely fastened to the surface on which it is carried." The NEC doesn't define "securely fastened" very precisely, but it generally implies that the conductor is well-supported and protected from physical damage. This exception is often interpreted to mean that you can run it exposed, properly supported, and protected from physical damage

For a #6 GEC that is exposed to physical damage, it


MUST be protected by being installed in RMC, IMC, EMT, or RTRC.3.

Protection Requirements for Bonding Jumpers
Bonding jumpers generally have similar protection requirements. The primary goal is to ensure they maintain their electrical continuity and aren't easily damaged. The rules are usually found in the specific article of the NEC that governs the type of bonding being performed (e.g., bonding metal water piping, bonding metal raceways). Generally, bonding jumpers can be run exposed if they're sized properly and adequately secured. If they're subject to physical damage, they need to be protected in a raceway.

So, Back to Your Specific Situation


Confirm the Conductor's Purpose

Is this a
Grounding Electrode Conductor connecting to a grounding electrode, or is it a Bonding Jumper connecting the BDA enclosure to the building's grounding system? The answer determines the specific applicable code sections.2.

If it is a GEC



Raceway Generally Required

The default is that the #6 GEC needs to be in a raceway (RMC, IMC, EMT, PVC, etc.) per 250.64(B).

Exception (Exposed, Secured)

If you can demonstrate that the #6 conductor is "securely fastened to the surface" and not subject to physical damage, you might be able to run it exposed, without a raceway. This is where local interpretation matters. MC straps and tie-wrapping to EMT pipes might be considered sufficient in some jurisdictions, but you'd need to verify with the AHJ (Authority Having Jurisdiction).3.

If it is a Bonding Jumper

The rules will depend on the specific type of bonding. However, the same general principle applies: if the conductor is properly sized, well-secured, and not subject to physical damage, it can often be run exposed. If there's a risk of damage, a raceway is required.

Recommendations



Consult Your Local AHJ

This is the most important step. Your local electrical inspector has the final say. Describe your proposed installation and ask if running the #6 conductor exposed, using MC straps and tie wraps to EMT, is acceptable. Get their answer in writing if possible. AHJs often have differing interpretations of "securely fastened" and "subject to physical damage."

Err on the Side of Safety (and Compliance)

If there's any doubt, just run the conductor in EMT. It's a relatively inexpensive and straightforward way to ensure compliance and avoid potential issues during inspection. It also provides excellent physical protection.

Proper Support

Regardless of whether you use a raceway or run the conductor exposed, ensure it's properly supported at regular intervals (as required by the NEC for the specific wiring method). This prevents stress on the conductor and ensures it stays in place.

In summary, while it
might be possible to run the #6 ground conductor exposed in your situation (especially if it's a bonding jumper), it's essential to understand the specific purpose of the conductor, the relevant NEC requirements, and, most importantly, to get approval from your local electrical inspector before proceeding.* Flag for review