User: SparkinTexas2001, Location: Texas
Asked on: Tuesday, October 8, 2024 at 8:20 am EDT
Answered on: Thursday, March 6, 2025 at 3:34 am EST
Question: Since the IQ series comes with overload protection what is the consensus on breaker and fuse sizing? FLA vs LRA
You're right, the IQ series (typically referring to Enphase IQ microinverters) has built-in overload protection, making breaker and fuse sizing a bit different than traditional AC circuits. Here's the consensus, broken down by FLA vs. LRA and important considerations
Key Distinction: FLA vs. LRA is NOT the primary consideration for IQ Microinverter Circuits
Why? The IQ microinverters are electronic devices, not motors. Motors are where LRA (Locked Rotor Amps) is crucial for inrush current at startup. Microinverters don't have that kind of inrush current. Their inrush current is managed by their internal circuitry.
The Consensus for IQ Microinverter Breaker/Fuse Sizing
The primary consideration for IQ series microinverters is the maximum continuous output current of the microinverter, combined with the number of microinverters on the circuit. You'll need to follow these steps:1.
Identify the Microinverter Model and its Max Continuous Output Current
This is CRITICAL. Refer to the data sheet for the specific model of IQ microinverter you're using (e.g., IQ7, IQ8, IQ8M, etc.). The datasheet will list the maximum continuous output current (sometimes called "maximum output AC current"). This is usually measured in amps (A).2.
Determine the Maximum Number of Microinverters per Branch Circuit
This is usually on the label on the Microinverter itself.3.
Calculate the Maximum Continuous Current per Circuit
Multiply the individual microinverter's maximum continuous output current (from step 1) by the number of microinverters you'll have on that branch circuit (from step 2).4.
Apply the 125% Rule (NEC 690.8(B))
Because the output current is considered "continuous" (operating for 3 hours or more), the National Electrical Code (NEC) requires you to increase the calculated current by 25%. This is to prevent nuisance tripping of the breaker. `Calculated Current (Step 3) 1.25 = Required Ampacity`5.
Select the Breaker/Fuse
Choose the next highest standard breaker or fuse rating above the required ampacity calculated in step 4.
Example
If your required ampacity is 17.5A, you would use a 20A breaker.
Example Scenario
Let's say you're using Enphase IQ8M microinverters. Looking at the datasheet, you see: Maximum Continuous Output Current (IQ8M)
1.21A
Max Microinverters Per Branch Circuit
131.
Total Current per Circuit
1.21A/inverter 13 inverters = 15.73 A2.
Apply 125% Rule
15.73A 1.25 = 19.66A3.
Choose Breaker
You would choose a
20A breaker.
Important Considerations and Best Practices
Always consult the microinverter's datasheet
This is the single most important resource. The datasheet provides the exact specifications for your specific microinverter model.
Follow the NEC and Local Codes
This is paramount. Electrical codes are designed to ensure safety. Your local electrical inspector has the final say.
Wire Sizing
Don't forget to size the wiring appropriately for the selected breaker/fuse. Use the NEC ampacity tables for the conductor type you're using (e.g., THHN, THWN). Wire gauge should be adequate for the breaker size and length of the run to avoid voltage drop.
Oversizing is generally not recommended
Using a breaker that's much larger than required provides less protection. The breaker's job is to trip in the event of an overcurrent or short circuit.
Professional Installation
Solar PV system installations can be complex. It's highly recommended to use a qualified and licensed solar installer. They will be familiar with the applicable codes and best practices.
Voltage Drop
Consider voltage drop, especially for longer branch circuit runs. You may need to increase the wire gauge to minimize voltage drop.
Enphase Documentation
Enphase provides detailed documentation, including installation guides and design tools, that specifically address breaker and fuse sizing. Take advantage of these resources.
In summary, forget about LRA/FLA when sizing the breaker for Enphase IQ microinverters. Focus on the maximum continuous output current of the specific* microinverter model, the number of microinverters on the branch circuit, and the 125% rule. Always consult the datasheet and follow NEC and local codes. Flag for review