Question: Since the IQ series comes with overload protection what is the consensus on breaker and fuse sizing? FLA vs LRA

You're right, the IQ series (typically referring to Enphase IQ microinverters) has built-in overload protection, making breaker and fuse sizing a bit different than traditional AC circuits. Here's the consensus, broken down by FLA vs. LRA and important considerations

Key Distinction: FLA vs. LRA is NOT the primary consideration for IQ Microinverter Circuits
Why? The IQ microinverters are electronic devices, not motors. Motors are where LRA (Locked Rotor Amps) is crucial for inrush current at startup. Microinverters don't have that kind of inrush current. Their inrush current is managed by their internal circuitry.

The Consensus for IQ Microinverter Breaker/Fuse Sizing

The primary consideration for IQ series microinverters is the maximum continuous output current of the microinverter, combined with the number of microinverters on the circuit. You'll need to follow these steps:1.

Identify the Microinverter Model and its Max Continuous Output Current

This is CRITICAL. Refer to the
data sheet for the specific model of IQ microinverter you're using (e.g., IQ7, IQ8, IQ8M, etc.). The datasheet will list the maximum continuous output current (sometimes called "maximum output AC current"). This is usually measured in amps (A).2.

Determine the Maximum Number of Microinverters per Branch Circuit

This is usually on the label on the Microinverter itself.3.

Calculate the Maximum Continuous Current per Circuit

Multiply the individual microinverter's maximum continuous output current (from step 1) by the number of microinverters you'll have on that branch circuit (from step 2).4.

Apply the 125% Rule (NEC 690.8(B))

Because the output current is considered "continuous" (operating for 3 hours or more), the National Electrical Code (NEC) requires you to increase the calculated current by 25%. This is to prevent nuisance tripping of the breaker.
`Calculated Current (Step 3) 1.25 = Required Ampacity`5.

Select the Breaker/Fuse

Choose the
next highest standard breaker or fuse rating above the required ampacity calculated in step 4.

Example

If your required ampacity is 17.5A, you would use a 20A breaker.

Example Scenario


Let's say you're using Enphase IQ8M microinverters. Looking at the datasheet, you see: Maximum Continuous Output Current (IQ8M)

1.21A


Max Microinverters Per Branch Circuit

131.

Total Current per Circuit

1.21A/inverter 13 inverters = 15.73 A2.

Apply 125% Rule

15.73A
1.25 = 19.66A3.

Choose Breaker

You would choose a

20A
breaker.

Important Considerations and Best Practices



Always consult the microinverter's datasheet

This is the single most important resource. The datasheet provides the
exact specifications for your specific microinverter model.

Follow the NEC and Local Codes

This is paramount. Electrical codes are designed to ensure safety. Your local electrical inspector has the final say.

Wire Sizing

Don't forget to size the wiring appropriately for the selected breaker/fuse. Use the NEC ampacity tables for the conductor type you're using (e.g., THHN, THWN). Wire gauge should be adequate for the breaker size and length of the run to avoid voltage drop.


Oversizing is generally not recommended

Using a breaker that's much larger than required provides less protection. The breaker's job is to trip in the event of an overcurrent or short circuit.

Professional Installation

Solar PV system installations can be complex. It's highly recommended to use a qualified and licensed solar installer. They will be familiar with the applicable codes and best practices.


Voltage Drop

Consider voltage drop, especially for longer branch circuit runs. You may need to increase the wire gauge to minimize voltage drop.

Enphase Documentation

Enphase provides detailed documentation, including installation guides and design tools, that specifically address breaker and fuse sizing. Take advantage of these resources.

In summary, forget about LRA/FLA when sizing the breaker for Enphase IQ microinverters. Focus on the maximum continuous output current of the