Question: It seems odd to me that this would feasible — but it’s on the drawing; then I thought -How many amps can a 14 AWG carry for the length of an average lightning strike?
Okay, let's break down why this is a fascinating and complex question, and what we can reasonably estimate. You're right to be skeptical; it's not a typical scenario to consider.
Why the Question is Tricky Lightning is NOT a Standard Circuit
Lightning is a massive, incredibly brief discharge of static electricity. It doesn't behave like the power flowing through your house wiring.
Time Duration is Key
Standard wire ampacity (the current it can safely carry) ratings are based on continuous current flow that would heat the wire to a potentially unsafe level over time. Lightning strikes last milliseconds or even microseconds. Heat buildup is drastically different in that time frame.
Insulation Breakdown
The sheer voltage of lightning will likely overcome the insulation on standard 14 AWG wiring immediately, causing flashover and arcing. The copper conductor itself is not the only factor in how it behaves.
Frequency/Skin Effect
Lightning is a very high-frequency event. At high frequencies, current tends to flow more on the surface of the conductor (the "skin effect"). This reduces the effective cross-sectional area and potentially increases heating, but this is probably less of a factor than the sheer energy involved and duration.
Impossible to predict
Lightning is impossible to predict
Estimating and Considerations1. Lightning Current Values
Lightning strikes can range from a few thousand amps to hundreds of thousands of amps. A typical strike is often estimated around 30,000 amps. However, these are averages. A particularly strong strike could be significantly higher.2.
Time Duration
Lightning stroke durations are typically in the range of 30 microseconds.3.
Wire Heating
In a standard circuit, the ampacity of a wire is determined by how much it heats up due to the resistance of the wire carrying current. The heat generated is given by I^2R, where I is the current and R is the resistance.4.
Fusing Current
We need to consider the wire's fusing current. Fusing current is the amount of current a conductor can withstand before it melts.5.
Lightning Protection Systems
Lightning protection systems don't use standard 14 AWG wire. They use much heavier conductors (often copper or aluminum tape, or heavy gauge wire, specifically designed to handle the high current and heat). These are bonded to a grounding system to safely dissipate the energy into the earth.
Very Rough Calculation (and Big Assumptions)
Let's make some extreme assumptions to get a very rough idea. We'll assume the lightning current flows uniformly through the wire (which it won't due to the skin effect), we ignore insulation breakdown, and we assume that the wire is exposed to the air. We'll use 30,000A as the current and 30 microseconds as the duration. Resistance of 14 AWG
Roughly 8.28 ohms per 1000 feet at 20°C. For the length of an average lightning strike path (let's say 100ft), the resistance would be ~0.828 ohms.
Heat Generated
I^2Rt = (30000^2 0.828 0.00003) = ~22356 joules.
Volume of wire heated: Let's make a guess at the average path length. Given a typical strike distance of 3 miles (15840 ft) with 200ft between ground strike zones, we will estimate the length of wire at 100ft. Volume = length pi r^2. r of 14AWG = 0.00814 inches or 0.000678 ft. Volume = 0.00001146 ft^3 Heat Capacity
Copper's specific heat capacity is about 385 J/(kgK), and its density is about 8960 kg/m^3. So the heat capacity of that 100ft of 14AWG wire is the volume the density the specific heat = 39.33 J/K.
Temperature Rise
Temperature rise is the heat/heat capacity or ~568K. This means a temperature rise of 568 degrees Kelvin or Celcius.
Caveats and Conclusion This calculation is massively simplified. It ignores all the high-frequency effects, doesn't account for non-uniform current distribution, radiation of heat, insulation failure, etc. Insulation is the Weak Point
The insulation will almost certainly fail immediately.
The Wire Probably Vaporizes
Even a short burst of that much energy is likely to cause the wire to melt, vaporize, and potentially explode.
The takeaway:
While 14 AWG might momentarily conduct a portion of a lightning strike, it is absolutely not* suitable for lightning protection. The wire will be severely damaged, the insulation will fail, and it's a serious fire hazard.Lightning protection systems are engineered with much heavier conductors and grounding specifically to handle the enormous energy of a lightning strike. Never attempt to use standard wiring as a substitute. Flag for review